Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: MTM switchgear

User: anbm, Location: TX

Asked on: Monday, November 4, 2024 at 9:41 pm EST
Answered on: Thursday, March 6, 2025 at 4:50 am EST

Question: When replacing the main, tie and feeder breakers (all draw out CBs) in MTM switchgear with new, same size & retrofitted CB, one CB at a time. Because these are draw out CBs, I assume the electrican wont need to shut down power to the switchgear for this task, correct?

Generally, no, you would not need to shut down the entire switchgear to replace draw-out breakers one at a time. However, it is absolutely critical to follow specific safety procedures and manufacturer instructions. Here's a breakdown of why and what precautions need to be taken

Why Draw-Out Breakers Allow for Live Work (Potentially):
Isolation

Draw-out breakers are designed to be racked out to a "test" or "disconnected" position. In this position, the breaker is physically separated from the energized bus and incoming/outgoing conductors. This provides a degree of isolation that allows work to be performed on the breaker itself without directly exposing the electrician to the live bus.


Safety Interlocks

Draw-out switchgear is typically equipped with interlocks that prevent the breaker from being racked out while it's closed (carrying current) or racked in while the door is open. These interlocks are designed to prevent accidental contact with live parts.

Critical Safety Precautions & Considerations (These MUST be followed)


Qualified Personnel Only

This work must be performed by qualified electricians who are specifically trained and experienced in working with medium-voltage switchgear and draw-out breakers. They must understand the risks involved and be competent in following safe work practices.2.

Detailed Procedure

There should be a detailed, written procedure that outlines each step of the breaker replacement process, including: Preparation (reviewing drawings, manufacturer instructions, PPE). Lockout/Tagout (LOTO) of the individual breaker compartment. Even though the main bus is live, the breaker compartment must be isolated and de-energized after the breaker is racked out. Verification of De-energization: Before touching any components within the breaker compartment, always verify that the circuits are de-energized using a properly rated voltage tester. Test before and after. Breaker Removal and Replacement: Follow the manufacturer's instructions for racking out the old breaker, removing it, installing the new breaker, and racking it back in. Testing and Commissioning: After the new breaker is installed, perform all necessary testing (e.g., insulation resistance testing, contact resistance testing, trip testing) to ensure it is functioning correctly.3.

Manufacturer's Instructions

Always refer to the manufacturer's instructions for the specific switchgear and breaker model being used. The instructions will provide detailed information about the racking procedures, interlocks, and safety precautions.4.

Personal Protective Equipment (PPE)

Appropriate PPE
must be worn at all times, including: Arc-rated clothing (suit, hood, gloves) rated for the potential fault current in the switchgear. Safety glasses or face shield. Insulated gloves. Safety shoes.5.

Arc Flash Hazard Analysis

An arc flash hazard analysis should be performed to determine the potential incident energy levels in the switchgear. This will dictate the appropriate level of PPE required.6.

Safe Work Permit

A safe work permit should be obtained before starting any work on the switchgear. This permit should outline the hazards, precautions, and emergency procedures.7.

Spotter/Assistant

A second qualified person should be present to act as a spotter or assistant. This person can provide additional safety oversight and assist with the work.8.

Communication

Clear communication is essential. Ensure that all personnel involved in the work understand the procedures and potential hazards.9.

Visual Inspection

Before racking out the breaker, visually inspect the compartment for any signs of damage or contamination.10.

Grounding

Ensure proper grounding practices are followed.

Important Considerations and Warnings



Retrofit Breakers

Retrofit breakers may have slightly different dimensions or connection points than the original breakers. Ensure that the retrofit breakers are compatible with the existing switchgear and that they are installed correctly.

Older Switchgear

Older switchgear may have deteriorated insulation or other components that could increase the risk of arc flash or electric shock. Exercise extra caution when working on older equipment.


Unexpected Conditions

Be prepared for unexpected conditions, such as damaged wiring, loose connections, or corroded components. If you encounter any problems, stop work immediately and consult with a qualified engineer.

Never Bypass Interlocks

Never bypass or disable any safety interlocks. These interlocks are designed to protect personnel from hazards.

Switchgear with line side shutters

Some switchgear has shutters that automatically open/close during racking in/out the CBs to keep the bus bar covered and avoid accidental contact. Shutters should be in perfect working order during these operations.

High Resistance Grounded (HRG) Systems
: Some facilities use HRG. You still need to follow LOTO for the individual breaker being replaced, but the bus may be energized, so you need to take precautions for that.

In summary, replacing draw-out breakers in energized switchgear
can be done, but it requires meticulous planning, strict adherence to safety procedures, and the involvement of highly qualified personnel. It is not a task to be taken lightly. If there's any doubt about the safety of the procedure, de-energize the entire switchgear.Disclaimer: I am an AI chatbot and cannot provide professional electrical advice. Consult with a qualified electrical engineer for any specific questions or concerns regarding electrical work.* Flag for review

Previous Question Next Question