Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: SPD Required on RV Pedestal

User: B677, Location: Florida

Asked on: Tuesday, November 5, 2024 at 3:23 pm EST
Answered on: Thursday, March 6, 2025 at 4:51 am EST

Question: Running a new conduit and 1/0 feed to metered earth buried pedestal GE1LM532ESInspector dropped requirement for GFCI but wants SPD. This pedestal likely does not allow double tapping the lugs for a type 1 SPD. Looks like it only has one double pole breaker slot open.Looking for ideas to install a SPD.Thoughts:Remove single pole 20A and replace with double pole 20AOne leg of SPD to breakerOther leg pigtailed Breaker to Receptacle hot and other leg of SPDNever done this but technically both poles of the breaker are in use; is it code?Polaris with 3 portsnot sure there will be wire to use these on in the customer side of the RV panelAnyone have any good ideas?

Okay, let's break down the situation and explore some options for installing an SPD (Surge Protective Device) in your GE1LM532ES metered pedestal, considering the inspector's requirements and the limited space.

Understanding the Challenges No Double Tapping

Modern code generally prohibits double-tapping lugs, so you're right to be cautious.


Limited Space

Only one available double-pole breaker slot limits your options.

Existing Wiring

Working with existing wiring can be tricky, especially in a compact space like a pedestal.


SPD Type

You didn't specify the type of SPD, but I'm assuming based on the need for a double pole breaker slot that it is a Type 2 SPD and not a Type 1 which requires a disconnect and is installed at the service entrance.

Potential Solutions, Ranked and Explained
1. The Preferred Solution: Replace Single Pole with Double Pole, and Use a Double Pole Breaker



How it Works

This is the cleanest, safest, and most compliant approach. Remove the existing single-pole 20A breaker. Install a new double-pole breaker (the correct amperage for the existing circuit—likely 20A). One pole is for the existing circuit, the other for the SPD.


Wiring



Breaker to Existing Circuit

Run the existing circuit's hot wire to one pole of the new double-pole breaker.


SPD Connection

Connect the SPD's two hot legs to each of the two poles on the new double pole breaker

Neutral & Ground

Connect the SPD's neutral and ground wires to the neutral and ground bars within the pedestal.


Why it's Best



Dedicated Protection

The SPD gets a dedicated breaker, providing the best protection and isolation.


Code Compliance

Avoids any double-tapping or questionable wiring practices.

Future-Proofing

Allows for easier future maintenance or upgrades.


Safety

The SPD will have its own dedicated overcurrent protection.

Important Considerations



Amperage

Make absolutely sure the new double-pole breaker is the correct amperage for the circuit it's protecting (the one that was previously on the single-pole breaker).

Physical Fit

Double-check that the double-pole breaker you choose physically fits in the available slot in the pedestal's panel. Some panels have very specific breaker requirements.2.

Using Polaris Connectors (Consider with Caution)



How it Works

Polaris connectors (insulated multi-tap connectors) allow you to splice multiple wires together. You'd use them to create a "tap" point off the existing feed to connect the SPD.

Wiring

Locate where your 1/0 feed connects to the bus in the pedestal. Add a Polaris connector to each leg of the 1/0 to tap the wire. From each Polaris connector, run a wire to the SPD. The other wire remains feeding the panel. Connect the SPD's neutral and ground wires to the neutral and ground bars.

Concerns



Space

Polaris connectors can be bulky. You need enough room in the pedestal to accommodate them without creating excessive strain on the wires.


Accessibility

You'll need to be able to access and tighten the Polaris connectors properly.

Wire Bending Radius

Be careful not to exceed the minimum bending radius for the 1/0 wire.3.

Pigtailing with the Breaker and Receptacle (NOT Recommended)



Why it's a Bad Idea



Code Violations

This likely violates code regarding proper use of breakers and creating proper splices within an enclosure.


Overloading

While technically the breaker is physically connected, you're effectively overloading the circuit electrically if the SPD draws current simultaneously with the receptacle.

Safety

This is a risky and potentially dangerous setup.


Inspector Rejection

This is almost guaranteed to fail inspection.

Important Considerations for ALL Solutions



Consult the SPD Manufacturer's Instructions

Always follow the manufacturer's instructions for the specific SPD model you're using. They will have specific requirements for wiring, grounding, and overcurrent protection.


Grounding

Ensure a solid, reliable ground connection for the SPD. This is crucial for its effectiveness.

Neutral Connection

The neutral connection is also important. Make sure it's properly sized and connected.


Enclosure Rating

Since this is an outdoor pedestal, ensure that any new components (like Polaris connectors) are rated for outdoor use.

Professional Help

If you're not completely comfortable with electrical work,
hire a qualified electrician. Electrical work can be dangerous, and mistakes can have serious consequences.

Recommendation:


Start with Option 1: Replacing the single-pole breaker with a double-pole breaker and dedicating one pole to the SPD. This is the cleanest, safest, and most compliant solution. Carefully plan your wiring, check for physical fit, and consult the SPD manufacturer's instructions. If space or breaker availability is truly an issue,
then* explore Option 2 (Polaris connectors) with extreme caution and a thorough understanding of the risks. Avoid Option 3 entirely. Flag for review

Previous Question Next Question