Topic: Stray voltage mystery question

User: e57, Location: San Francisco, CA

Asked on: Tuesday, November 5, 2024 at 10:23 pm EST
Answered on: Thursday, March 6, 2025 at 4:52 am EST

Question: Been a bazillion years since I’ve posted here. Miss you guys sometimes. (Not posted much since a dad)Nonetheless, got a little question - how much stray voltage is too much? And who you think is responsible for correcting it?Last week disconnected a 200A feeder that goes from a main house panel board to a pool house then to a distant shed each building with its own electrodes etc and no MBJ’s in them. No other conductors building to building. Soil conditions mostly fractured serpentine rock.During reconstruction of the equipment grounding conductor - the kid I had doing it got shocked. So he it it with proximity tester (because he questioned it) - nothing, but got shocked making the connection again and told me. So I had him pull out his meter and it was 63 volts. And I said well that’s interesting?!? I tapped them together and there was a little spark. Threw an ammeter on it - but got no current that registered after being connected… (figured enough to shock and enough to spark would at least register current?)We broke the ground again just to check. At the building in the middle and got the same conditions and measurements. When reconnected it’s completely gone… And with the feeder fully connected there’s barely a volt between EGC/with electrodes and the separate structures neutral. Condition vanishes seemingly.Nearest I can assume is a stray current in the earth from either or both the adjacent property and this and that property that is one which is in front of the property next door 500’ away. POCO Transformer unknown location but think it’s further away in the other direction (?)It feels/seems like neutral current levels of voltage (if one was dumb enough to disconnect one) But 63v seems excessive? And seems to vanish with no current on the grounding conductor after connected.Any thoughts?

Wow, welcome back to the land of electrons and code battles! Being a dad will change your posting frequency, guaranteed.Okay, let's unpack this stray voltage situation. You've got a head-scratcher on your hands, but a fascinating one.

How Much Stray Voltage is Too Much?

This is the million-dollar question. There's no single, universally agreed-upon answer. It depends on context and jurisdiction. Here's a breakdown: General Safety Concern

In general,
any voltage high enough to cause a shock is "too much." In the USA that is 30 volts to earth. 63V is absolutely concerning. The threshold for perceived shock varies from person to person and depends on skin resistance (wet vs. dry), path of current, and frequency. Anything above 30V (AC) should be investigated aggressively.

Poultry/Cattle

In agricultural settings (which, from your description of a "shed" could potentially apply), even low levels of stray voltage (below 1V) can impact animal behavior and productivity. This is especially true for dairy cows, who are very sensitive.

Code Considerations (USA)

The NEC doesn't specifically define a
threshold for "stray voltage" necessitating immediate action. However, it does require all electrical equipment and systems to be installed in a manner that is safe and free from hazards. A 63V potential between grounding conductors definitely suggests a hazard.

IEEE Standard 142 (Green Book)

This provides more in-depth information on grounding and bonding, including discussions about ground potential rise and circulating ground currents. While not code, it's a valuable resource for understanding the phenomena.

Who is Responsible for Correcting It?


This is another complex question and often depends on the source of the problem:1. On-Site Issues (Most Likely Culprit)



The Property Owner/Homeowner is ultimately responsible
for the safety of the electrical system on their property. You, as the electrical professional, have a moral and professional obligation to inform the homeowner of the hazard and advise on corrective action.2. POCO (Power Company) Contribution

If the stray voltage originates from the POCO's distribution system (e.g., a failing neutral conductor, improperly grounded transformer), they are responsible for fixing it. However, proving that the issue originates from their system can be challenging.

How to involve them

Call the POCO immediately and explain the situation very clearly. Emphasize the 63V potential difference and that someone received a shock. Use terms like "potential safety hazard" and "risk of electrocution." They are legally obligated to investigate potential safety concerns. Be prepared to demonstrate the voltage readings and explain the configuration.

Important

Don't assume they will immediately take responsibility. They will often want to blame on-site wiring first.3.

Neighboring Property

If the stray voltage is demonstrably originating from a neighboring property (e.g., a compromised neutral, faulty equipment grounding), the neighbor (or their electrician) is responsible.

How to address it

This is a delicate situation. Start with a polite conversation with the neighbor, explaining the issue and the potential hazard. If they are uncooperative or unresponsive, you may need to involve the local building department or electrical inspector.

Possible Explanations and Troubleshooting Steps

Your description points to a few possibilities:1.

Neutral Current in the Earth

The most likely scenario. You are probably seeing a voltage gradient caused by neutral current flowing through the earth back to the source (POCO transformer or possibly a miswired connection). This is common when there are inadequate grounding conductors or if neutral conductors are failing in the utility’s grid.2.

Fault Condition on a Nearby Property

Another property could have a ground fault that is injecting current into the earth. This is especially possible if that property is further away.3.

POCO Neutral Issues

Failing neutral conductors on the utility's primary or secondary side can cause significant ground potential rise issues.4.

Galvanic Corrosion

While less likely to produce 63V, dissimilar metals in the earth can create voltage potentials. The serpentine rock could potentially play a role here, as it can contain conductive minerals.5.

Equipment Grounding Conductor issue

An improperly installed EGC, damaged or missing, could be the cause, especially if the fault is coming from within the system.

Here's what I would do


Document Everything

Record voltage readings, current measurements, dates, times, weather conditions, photos, and everything else. Keep a detailed log.2.

Call the POCO immediately

Explain the situation and emphasize the safety hazard. Request that they investigate the neutral conductors and grounding of their distribution system in the area.3.

Insulation Resistance Testing

Perform megger tests on all circuit conductors (including neutral) to ground from the main panel. Look for low insulation resistance, which could indicate a fault.4.

Ground Resistance Testing

Use a ground resistance meter (fall-of-potential method) to measure the resistance to ground of each electrode at each building. Elevated ground resistance can exacerbate stray voltage issues.5.

Neutral-to-Ground Voltage Measurements

Measure the voltage between neutral and ground at the main panel and at each subpanel.
Significant voltage here suggests a neutral-ground bond issue or excessive neutral current.6.

Investigate Neighboring Properties

(Carefully!) Talk to the neighbors and see if they have experienced any electrical issues. Visually inspect their service entrance for any signs of corrosion or damage.7.

Investigate Sub Panels

Inspect and test the grounds, neutrals, and general state of your sub panels.8.

Check All Grounding Connections

Make sure all grounding connections are tight and free from corrosion.9.

Qualified Professional

Consult with a qualified electrical engineer experienced in grounding and power quality issues. They may have specialized equipment (e.g., earth resistivity testing) to diagnose the problem more accurately.10.

Check your Ground Grid

If you had a fault to ground on any of the systems on the property, the ground electrode system should have been able to sink the current and not cause a voltage differential, so check the grid.

Important Safety Considerations



Treat all electrical circuits as energized until proven otherwise.
Use appropriate PPE (Personal Protective Equipment), including insulated gloves and safety glasses. Work with a helper whenever possible.* If you are not comfortable working with energized circuits, call a qualified electrician.Why the Voltage Disappears When Connected

When you connect the grounding conductor, you create a low-impedance path for current to flow between the two buildings. The voltage potential drops because you are essentially short-circuiting the voltage source (the stray current in the earth). The fact that you don't register current with your ammeter suggests that the source impedance is high and/or the current is flowing via a different path.

In Conclusion:


You've uncovered a potentially dangerous situation. Take it seriously, document everything, and involve the POCO. A systematic approach to troubleshooting, as outlined above, should help you pinpoint the source of the stray voltage and get it corrected. Good luck, and let us know what you find! Flag for review