Topic: generator, 480 v, 200 amp

User: shalomfred, Location: Dillon Montana

Asked on: Tuesday, November 5, 2024 at 11:51 pm EST
Answered on: Thursday, March 6, 2025 at 4:52 am EST

Question: I was asked to hard wire a three-phase generator for a city septic system. It is currently hooked up with a so cord. The generator has three phase wires with a chassis ground, in the service the ground is connected ground with a neutral being derived there. Do, I need to try and pull a neutral from the generator? Am I calculating the wire size correct at 250kcmils.you all are great helping with our issues, thank you

Okay, let's break down the issues with hardwiring a three-phase generator to a city septic system, focusing on the grounding, neutral, and conductor sizing. Given the information provided, it's highly likely the generator should NOT have a neutral connected.Crucial Considerations & Disclaimers



Safety First

Working with electrical systems, especially three-phase and generators, can be extremely dangerous. Improper wiring can lead to electrocution, fires, equipment damage, and system malfunctions.

If you are not a qualified and licensed electrician, you should not be doing this work.
Local Codes are Paramount

The National Electrical Code (NEC) provides a baseline, but local electrical codes always take precedence. These codes can be stricter or have specific requirements for generator installations. You must comply with all applicable codes. You need to contact your local permitting office and have the installation inspected.

Generator and Transfer Switch Specifications are Essential

We need the
exact generator model and the exact type of transfer switch (if any) being used. Different generators and transfer switches have different requirements.

System Configuration

Understanding how the overall system is intended to function during a power outage is essential. What loads are being powered? Is there a transfer switch involved? Is this generator intended to run in parallel with the utility at any time?

Analyzing the Situation Based on the Provided Information


Existing SO Cord

The fact that it's currently connected with an SO cord suggests it's intended to be a portable generator, but that does not give you the authority to install as a permanent generator. This is not allowed by code.2.

Generator Wiring (3-Phase + Chassis Ground)

This is key. The generator having three phase wires and a chassis ground strongly indicates a separately derived system configuration where

the generator is NOT intended to have its neutral bonded to ground at the generator.
The chassis ground provides safety grounding for the generator frame.3. Service Grounding (Grounded Conductor)

The fact that the service has a ground connected with a neutral being derived there is common.4.

Do NOT Connect a Neutral from the Generator



Connecting a neutral from the generator to the grounded neutral at the service will likely create a ground loop. This is dangerous and violates code.
The generator is likely designed to operate as a floating neutral system.

Why No Neutral Connection at the Generator is Likely Correct



Separately Derived System

When a generator is wired as a separately derived system (which is very common for standby generators), the neutral is
not bonded to ground at the generator itself. The neutral is derived at the transfer switch or the service entrance equipment, and the grounding is handled through a separate grounding electrode conductor connecting to a grounding electrode system (ground rods, water pipe, etc.). The generator's frame is connected to the grounding electrode system via an equipment grounding conductor.

Ground Loops

Connecting a neutral at both the generator and the service creates a parallel path for current to flow through the grounding system. This can cause circulating currents, overheating, nuisance tripping of breakers, and potentially dangerous voltages on metal parts.

Grounding Considerations



Grounding Electrode System

The generator's frame (chassis)
must be connected to the building's grounding electrode system (ground rods, water pipe, etc.) via an equipment grounding conductor. This ensures that the generator frame is at the same potential as the earth and other grounded equipment.

Equipment Grounding Conductor

You'll need to run an equipment grounding conductor (typically green or bare copper) along with the phase conductors from the generator to the connection point at the service. This conductor is sized according to the overcurrent protection device protecting the circuit.

Wire Sizing



250 kcmil Calculation

You need to base the conductor ampacity on the generator's output current. This will require the generator's rated output current, taking into account the voltage and power factor. Once you have the current, you need to look up the appropriate wire size in NEC Table 310.16 (or the equivalent table in your local code), considering the conductor's insulation type and the ambient temperature.

250 kcmil might be correct, but without knowing the generator's output current, I cannot verify that.
Voltage Drop

Don't forget to calculate voltage drop, especially if the distance between the generator and the service is significant. Excessive voltage drop can cause equipment malfunction.


Overcurrent Protection

The conductors must be protected by an appropriately sized overcurrent protection device (circuit breaker or fuses) at the generator or at the service entrance, depending on the installation.

Steps to Take


Identify Generator Model and Type

Get the make and model number of the generator. Look up the manufacturer's specifications, wiring diagrams, and installation instructions.2.

Determine Load Requirements

Understand what loads the generator will be powering during an outage.3.

Consult with a Qualified Electrician

This is absolutely essential. Have a licensed electrician review the entire installation plan, verify the wiring, and ensure compliance with all applicable codes.4.

Permitting and Inspection

Obtain the necessary permits from your local building department before starting any work. Have the installation inspected by a qualified inspector after it's complete.

In summary, based on the limited information, you should NOT connect a neutral from the generator. You need to connect the generator frame to the building's grounding electrode system. Verify the generator's output current, calculate the correct conductor size, and have the entire installation reviewed and inspected by a qualified electrician.