Topic: Metal Box Cover Plates

User: Little Bill, Location: Tennessee NEC:2017

Asked on: Wednesday, November 6, 2024 at 2:56 pm EST
Answered on: Thursday, March 6, 2025 at 4:54 am EST

Question: I can't seem to find where in the code it says that device metal cover plates with flat corners don't require a jumper to the device. Can someone find that article for me? I'm talking about a 4 square box with an industrial raised cover.

You're likely not finding a specific code article that explicitly states flat-cornered metal device cover plates on metal boxes don't require a bonding jumper to the device. The code doesn't typically list things that aren't required. Instead, the code focuses on what is required for effective grounding and bonding.Here's the reasoning and the relevant NEC sections that support why a bonding jumper is usually not required in this specific scenario: Effective Grounding Path

The key is that the metal box, the metal cover plate, and the equipment grounding conductor (EGC) system need to create a continuous, low-impedance path back to the source.


Code Sections to Consider



NEC 250.4(A)(5): Bonding of Electrically Conductive Materials and Other Equipment.
The metal box and metal cover are part of the "electrically conductive materials" that are likely to become energized. This section requires these to be bonded together to create a low-impedance path to ground. NEC 250.92(A): Bonding Jumpers and Connection Means. This section discusses how to create those bonds. However, the subsequent sections show how to create an effective ground without a jumper. NEC 250.146(B): Connection to Equipment Grounding Conductor. This section is crucial. It outlines how devices (like receptacles or switches) are grounded when installed in metal boxes. It allows for the box to act as the ground for the device under certain conditions. NEC 250.146(B)(1)

This exception states that if the device screws and box provide adequate bonding between the device and box, then no jumper is required. It goes on to say that this exception applies to receptacles installed in boxes that are flush with a surface. Because the box is flush with the surface and the screw makes contact with the box, this exception can be applied.

Why No Jumper is Usually Needed with a Metal Box and Flat-Cornered Metal Cover Plate


Metal Box Grounding

The metal box is connected to the equipment grounding conductor (EGC) through an approved method like a grounding screw, a grounding clip, or a listed connector.2.

Direct Metal-to-Metal Contact

When the metal cover plate is screwed tightly to the metal box, the flat corners provide direct and secure metal-to-metal contact. This contact establishes a low-impedance grounding path between the cover plate and the box.3.

Device Grounding

The device (e.g., receptacle, switch) is then grounded to the box either through mounting screws or through a listed self-grounding device that makes direct contact with the metal box.

In Summary

The flat corners of the metal cover plate, when securely fastened to the grounded metal box, create a sufficient grounding path, negating the need for a separate bonding jumper to the cover plate itself. The device is grounded via its connection to the metal box.

Important Considerations



Tight Connections

It is critical that all screws and connections are tight and secure. Loose connections create high impedance and compromise the grounding path.


Paint and Corrosion

Any paint or corrosion between the metal surfaces can impede the grounding path. Clean the surfaces if necessary.

Damaged Boxes

If the box is severely damaged or corroded, it might not provide an effective grounding path, and additional bonding might be necessary.


Listed Devices

Using self-grounding devices that are listed for the purpose is always recommended for a secure and reliable grounding connection.

AHJ (Authority Having Jurisdiction):
Always consult with the local electrical inspector or AHJ for specific interpretations and requirements in your area. They have the final say on code compliance.Therefore, you won't find a rule saying "no jumper required for flat corners." The code implies it by defining what's required* for proper grounding, and the combination of a properly grounded metal box, a metal cover plate with flat corners securely attached, and a grounding type receptacle connected via screws to the box meets those requirements in most situations. However, this situation depends on the screws providing the needed connection to provide the ground to the receptacle/switch. Flag for review