Question: …..At least in my area.Surface mounted exterior panel, someone wants to add a circuit, and they run a short piece of pvc conduit down the outside of the house with romex inside, attached to the siding, and then LB into the crawl space.See it all the time. But it should transition from THWN-2 to romex, either in a box or in the LB if it’s listed for that.You guys see this a lot?
Yes, unfortunately, what you're describing is a very common improper installation. Using Romex (NM-B) cable in conduit exposed to weather is a violation of the National Electrical Code (NEC). And as you rightly point out, even if the conduit were installed correctly with proper weatherproof fittings, Romex isn't rated for wet locations.Here's a breakdown of the issues and why it's wrong: Romex in Wet Locations (NEC 334.12(B)(4))
Romex (NM-B) is designed for dry, interior locations only. It cannot be used where it will be exposed to moisture, such as in underground or wet locations. The "B" in NM-B stands for "building wire" and indicates its dry-location suitability.
Romex in Conduit Exposed to Weather (NEC 300.9)
Even if the conduit seems weatherproof, temperature fluctuations will cause condensation to form inside the conduit. This will expose the Romex to moisture, which it's not rated for. Furthermore, running Romex in conduit for more than a short "sleeve" is typically frowned upon or prohibited (check your local amendments).
Proper Transition
As you mentioned, a proper transition from THWN/THHN (the correct wet-rated conductors for conduit in this application) to Romex requires a junction box rated for the environment. The THWN/THHN is run in the conduit. The conductors should terminate in an appropriate junction box, and the Romex is connected within the box. The box needs to be weatherproof if it's outside.
LB Fittings and Wire Fill
Using the LB as a junction box isn’t allowed unless it's specifically marked and listed for that use. The available space inside an LB is also very limited and rarely sufficient for making splices for more than one circuit, especially with the required wiring room for the conductors. LBs are also usually a pain to work in for splicing.
Why People Do It (and why it's still wrong)
Cost
Romex is cheaper than individual conductors like THWN/THHN and the necessary fittings.
Convenience
People often have Romex on hand and don't want to make an extra trip to the supply house.
Ignorance
Some people simply don't know the code requirements or the limitations of Romex.
What to Do Instead
Run THWN/THHN in the Conduit
The correct approach is to use individual THWN/THHN conductors inside the PVC conduit. THWN/THHN is rated for wet locations and is suitable for use in conduit.2.
Use a Weatherproof Junction Box
Where the conduit enters the crawlspace (or at another convenient point), install a weatherproof junction box.3.
Make the Transition
Terminate the THWN/THHN conductors in the junction box using appropriate connectors or wire nuts. Connect the Romex to the THWN/THHN inside the junction box.4.
Proper Fittings
Use properly listed and installed weatherproof conduit fittings (connectors, couplings, etc.)
Why It Matters
Safety
Romex in a wet location creates a significant shock and fire hazard. The insulation can break down, leading to short circuits, ground faults, and potential electrocution.
Code Compliance
Failing to follow the NEC can result in failed inspections, fines, and potential liability if someone is injured or property is damaged.
Durability: Romex exposed to moisture will degrade much faster, leading to premature failure of the wiring system.In short, while it may be a common shortcut, using Romex in exposed conduit is a dangerous and incorrect practice that should always be avoided. Call it out every time. Flag for review