Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Service Disconnect for EV chargers

User: Grouch1980, Location: New York, NY

Asked on: Wednesday, November 6, 2024 at 10:43 pm EST
Answered on: Thursday, March 6, 2025 at 4:55 am EST

Question: I'm trying to follow this thread, but I am not able to.Electric Vehicle ChargingI see that branch circuits are required to be designed to 125% for EV chargers because they are considered continuous load. I assume a service that is designed solely for EV chargers would also need to be sized for 125%. But how does one get to that conclusion via the NEC? 220.40 says...

Okay, let's break down why the thread is likely talking about sizing branch circuits and services for EV chargers at 125% and how that relates to the National Electrical Code (NEC).

Understanding the Core Concept: Continuous Load

The key is the concept of a "continuous load" in electrical wiring. The NEC defines a continuous load (Article 100 - Definitions) as:> "A load where the maximum current is expected to continue for 3 hours or more."Why is this important?

Electrical conductors (wires) and overcurrent protection devices (like circuit breakers and fuses) generate heat as current flows through them. If a load runs continuously for 3 hours or more at its rated amperage, that heat can build up, potentially causing: Conductor Degradation

The insulation around the wires can deteriorate over time, leading to shorts and fire hazards.


Overcurrent Protection Device Nuisance Tripping

The breaker might trip even though the load isn't technically exceeding its rated amperage, simply because the breaker itself is getting too hot.To mitigate these risks, the NEC mandates that continuous loads be factored into the design calculations as if they were 125% of their actual current draw. This effectively derates the conductors and overcurrent protection devices, providing a safety margin for the sustained heat.

EV Chargers and Continuous Load


EV chargers are generally considered continuous loads. Charging an electric vehicle can easily take 3 hours or more. This is a key starting point.

How the NEC Addresses Continuous Loads (General Principles)

The NEC doesn't have a single section explicitly saying "All EV chargers must be sized at 125%." Instead, it works through a combination of general rules and specific equipment instructions. Here's how it typically plays out:1. General Rule: 210.19(A)(1) (Branch Circuits - Conductors): This section generally requires that branch-circuit conductors have an ampacity not less than 125 percent of the continuous load, plus the noncontinuous load.2. General Rule: 210.20(A) (Branch Circuits - Overcurrent Protection): This section requires that the overcurrent protection device be rated not less than 125 percent of the continuous load, plus the noncontinuous load.3. 220.40 (General)

This is where the thread probably leads off. This section is an intro to the general requirements for calculating feeder and service loads. It is telling you that Articles 220.42 through 220.56 provide requirements for calculating the "ampere load" used in load calculations.

Applying it to EV Chargers - A Simplified Example


Let's say you have an EV charger that draws 32 amps continuously. Conductor Sizing

You need to size the branch circuit conductors for 32 amps
1.25 = 40 amps. You would then select a conductor size from Table 310.16 (or other applicable table) that is rated for at least 40 amps under the appropriate temperature conditions. For example, using the 75°C column, you might need #8 AWG copper THHN wire.

Overcurrent Protection

You need to use a circuit breaker or fuse rated for at least 40 amps. However, standard breakers are typically available in increments of 15, 20, 25, 30, 35, 40, 45, 50, etc. You would use a 40 amp breaker.

Service Calculations


Now, let's address the service calculation question: If the service is
solely for EV chargers, then you absolutely must apply the 125% rule to the total calculated load. Aggregation of Chargers

If you have multiple EV chargers on the service, you need to total their continuous loads first. Then, multiply that total by 1.25 to determine the minimum service amperage.

220.82 or 220.84 (Optional Calculations)

For dwelling units, the NEC allows for optional calculations that might reduce the service size in certain situations. But these options depend on the specific details of the installation. The optional calculations still factor in continuous loads.


220.87 (Noncoincident Loads)

This section allows for reducing the calculated load by using the actual, measured maximum demand. It is usually applied in commercial settings, where measuring the actual load is realistic.

Why 220.40 is Important
220.40 is like a roadmap. It tells you that other sections in Article 220 provide the detailed rules for calculating the loads on feeders and services. You wouldn't expect 220.40 itself to say "EV chargers must be sized at 125%."In Conclusion EV chargers are generally considered continuous loads. NEC 210.19(A)(1) and 210.20(A) require branch circuits to be sized for at least 125% of the continuous load (including the conductors and the OCPD, like a breaker). If a service is dedicated solely to EV chargers, that also makes it a continuous load service. The total load calculation for the service needs to factor in the 125% requirement.

Important Disclaimer
These explanations are for educational purposes and should not be taken as complete and comprehensive electrical code interpretations. Always consult the latest edition of the NEC and consult with a qualified electrician for any electrical work. Local codes may also be more stringent than the NEC.* Flag for review

Previous Question Next Question