Topic: Request guidance on Coke Breeze use for Grounding.

User: Installer, Location: DesMoines, Washington

Asked on: Thursday, November 7, 2024 at 10:43 am EST
Answered on: Thursday, March 6, 2025 at 4:55 am EST

Question: I'm doing a Project in Alaska in silty soil and I'm not expecting it to be amenable to grounding.I need to put in a Grounding Counterpoise with 4 10' ground rods cad welded to 40' of 4/0 AWGI'd like to use Coke Breeze and I believe that you place it around each ground rod?If that is the case , how much coke breeze should I place around each ground rod?Would a 50 pound pound bag work?Thank you in advance

You're on the right track thinking about counterpoise and coke breeze for grounding in challenging Alaskan silty soil. Here's a breakdown of the coke breeze considerations and quantity.

Regarding Coke Breeze and Grounding in Silty Soil



Why Coke Breeze?
Coke breeze is a low-resistance backfill material often used in grounding systems, especially where soil resistivity is high (like silty soil). It surrounds the ground rod, creating a larger, more conductive contact area with the earth. This helps reduce the overall ground resistance. Counterpoise is a Good Idea

Given the silty soil conditions, a counterpoise system is a smart approach to improve grounding.

Coke Breeze Placement and Quantity



Placement

You're correct. Coke breeze should be placed around the ground rods. Think of it as creating a "sleeve" or "donut" of coke breeze around each rod.


How Much Coke Breeze?
This is where things need some specific calculation. A 50-pound bag might be sufficient for each rod, but it depends on the desired diameter of the coke breeze column and the rod length. The goal is to fully encase the ground rod.

Here's how to estimate (and why a 50-pound bag might be marginal)


Desired Coke Breeze Column Diameter

A common recommendation is to have a coke breeze column that is 6-12 inches in diameter around the ground rod. Let's assume you're aiming for a 8 inch diameter column.2.

Calculate the Volume of the Coke Breeze Column



Radius of the Column

Diameter / 2 = 8 inches / 2 = 4 inches = 0.33 feet


Volume of the Column

π radius2 height = π (0.33 ft)2 10 ft = ~3.42 cubic feet3.

Coke Breeze Density

Coke breeze density varies but is typically in the range of 30-50 lbs per cubic foot. Let's use 40 lbs/cubic foot as an estimate.4.

Weight of Coke Breeze Needed per Rod

Volume Density = 3.42 cubic feet 40 lbs/cubic foot = ~137 lbs

Conclusion Regarding 50 lb Bags

Based on these calculations, a

50 lb bag per rod is very likely not enough.
You'd need closer to three 50 lb bags (or one larger bulk quantity) per ground rod to achieve a reasonable coke breeze column.

Important Considerations and Recommendations



Soil Resistivity Testing

Before you finalize your grounding system, conduct a soil resistivity test at your site. This is crucial. Soil resistivity varies dramatically, even within a relatively small area. A soil resistivity test will give you the actual resistance you're dealing with and allow you to design your grounding system more accurately. A low reading, may negate the need for Coke Breeze.

Ground Resistance Measurement

After installation, measure the ground resistance. The goal is to meet applicable codes and project requirements (typically 5 ohms or less, but check your specific requirements). If the resistance is too high, you may need to add more ground rods, extend the counterpoise, or use more coke breeze.

Coke Breeze Quality

Use a high-quality coke breeze specifically designed for grounding applications. This will ensure it has the proper resistivity and chemical properties. Ask your supplier for the specifications.


Installation

Dig a hole around each ground rod, larger than the desired coke breeze column diameter. Place the ground rod in the center. Carefully pour coke breeze around the rod, ensuring it's evenly distributed. Compact the coke breeze slightly. Don't over-compact. Backfill the remaining hole with the original soil.

Moisture

Coke breeze performance is enhanced by moisture. In very dry environments, consider a method to periodically add water to the grounding area.

Corrosion

Coke breeze can be corrosive. Be sure to use ground rods and conductors that are compatible with coke breeze. Copper-clad steel ground rods are common. Cad welding is essential to ensure good, long-lasting connections.


Local Codes and Standards

Always adhere to local electrical codes and any project-specific grounding requirements.

In summary:
Get a soil resistivity test. Calculate the necessary coke breeze volume based on your desired column diameter (6-12 inches is a good range). A 50-pound bag per rod is likely insufficient. Plan on needing significantly more. Measure the ground resistance after installation. Follow proper installation techniques. Comply with all applicable codes and standards.Doing these things will help you create an effective and reliable grounding system in challenging silty soil conditions. Flag for review