User: Electrician123456789, Location: Florida
Asked on: Thursday, November 7, 2024 at 11:12 am EST
Answered on: Thursday, March 6, 2025 at 4:55 am EST
Question: Is it okay to have cm cable cl2 in same conduit as line voltage to switch, but come out of a jbox and be in free air to fixtures at the same timeFrom what I've read, you can have the cable in the same conduit since the circuit is 120V and the cm cl2 cable is rated for 150V.The cable is re-classified as a class 1 and will have to be wired with chapter 3 wiring methods.But can the cable run down to the switch with 120V then come out of the box and jump to fixtures in free air or if it is in conduit to the switch, does it need to stay in conduit to the light? Can you have part of the 0-10V wiring be class 1 where it's in the conduit and call it class 2 when it's just in free air above the ceiling?I have read a lot of threads, but haven't seen this scenario.Thanks in advanceTom
Okay, Tom, let's break down this scenario with a focus on the code and practical considerations. Your situation brings up some important nuances in how Class 1 and Class 2 circuits are handled.
Here's the core issue
You're mixing Class 1 and Class 2 wiring methods within the same circuit run, with a change in wiring method mid-run (conduit to free air).
Here's the breakdown and analysis
Sharing Conduit (Conduit Segment)
Yes, you are correct, under specific conditions, you can run Class 2 (CM, CL2) cables in the same conduit as 120V line voltage. Conditions
The Class 2 cable must be re-classified as a Class 1 circuit. This is the critical part.
Why
NEC 725.136(D) allows Class 2 and Class 3 circuit conductors to be installed in the same raceway, cable, or enclosure with conductors of electric light, power, Class 1, nonpower-limited fire alarm and medium-power network-powered broadband communications circuits, where they are introduced solely to connect to the equipment connected to those conductors, and where either of the following conditions are met: (1) The Class 2 or Class 3 conductors are separated by a barrier from all other conductors of the other circuits or systems. (2) All the conductors of electric light, power, Class 1, nonpower-limited fire alarm and medium-power network-powered broadband communications circuits are installed with a wiring method suitable for the voltage and power of the highest voltage and power conductors.
Crucial Point
When you reclassify the CL2 cable as Class 1 within the conduit, you must use Chapter 3 wiring methods for that entire section of the cable run. This means the CL2 cable inside the conduit needs to be treated as a Class 1 circuit conductor.
In your scenario since there's no barrier, all the conductors are installed with a wiring method suitable for the voltage and power of the highest voltage and power conductors.2. Free Air Section After Conduit
This is where it gets problematic. You cannot simply switch back to Class 2 wiring methods (i.e., free-air CL2 cable) after the conduit section, especially if it is in free air. Why
The NEC requires consistency in wiring methods for a circuit run, especially when you've intentionally reclassified it. You can't have a cable be Class 1 part of the way and then revert back to Class 2. Once you classify it as class 1, use the wiring methods of chapter 3.
Therefore, the section from the switch up to the fixtures also needs to be wired per Chapter 3. The switch and jboxes will need to be sized with wirefill for the 120V as well as the additional conductors from the CM CL2 cable, reclassified as class 1.3. Example ScenariosScenario A: To the switch via chapter 3 methods, then up to the fixtures via Chapter 3 as well.
Scenario B: Run the low voltage and line voltage to a powered relay and switch via chapter 3 methods. Then take CL2 to the fixtures.
Key Considerations and Recommendations
Physical Protection
Free-air CL2 cable above a suspended ceiling is typically acceptable as long as it's not subject to physical damage. However, if the cable is exposed to damage, it must be protected.
Workmanship
Regardless of the wiring method, neat and workmanlike installation is always required (NEC 110.12). Cable must be properly supported and secured.
In Summary
You can run CL2 cable in the same conduit as line voltage if you reclassify it as Class 1. But once you do that, the wiring methods for the entire* reclassified circuit run need to adhere to Chapter 3, including the section going to the lighting fixtures. You can't switch back to Class 2 wiring methods mid-run.The least amount of Class 1 wiring that needs to be done, the better.Consider alternate scenarios to minimize the area where Class 1 wiring needs to be used.
Disclaimer: I am an AI chatbot and cannot provide professional electrical advice. Always consult with a qualified and licensed electrician to ensure your installation complies with the NEC and local codes. They can assess your specific situation and ensure a safe and compliant installation. Flag for review