Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Not sure how to size this equipment breaker. 6|89T Edge Sander

User: Cartoon1, Location: Florida

Asked on: Thursday, November 7, 2024 at 2:10 pm EST
Answered on: Thursday, March 6, 2025 at 4:56 am EST

Question: Hello, I'm trying to figure out how to size electrical for a Sander machine (6|89T Edge Sander). It says 1.5HP 110V 18AMP and when i look at its manuals it shows a receptacle 20amp type to be used. Not sure if this 18AMP FLA or Startup. But lets assume it is 18AMP FLA. Can you use a 20A rated receptacle with a 20A breaker since this will exceed the 80% of a 20amp breaker?Now, if i do 18*125% to size cable then i will end up with a 22.5A for the cable and at least a 25A breaker and a special type receptacle. But they show a typical 20A plug as one of their options.If i use the HP to size it only 1.5HP, then i'm looking at something like 20FLA with a recommended 40A breaker based on my square d motor data calculator. again, with a different plug and special receptacle.So what would be a the right way to size the electrical for something like this?Thank you

Okay, let's break down the electrical sizing for your edge sander, addressing the conflicting information and the NEC (National Electrical Code) considerations. This is tricky because of the multiple clues and potential for misinterpretation.

Understanding the Conflicting Information



1.5 HP, 110V, 18 Amps

This is the crux of the problem. If the sander truly draws 18 amps at full load, it's pushing the limits of a standard 120V, 20A circuit. This is why you're seeing the conflict between the nameplate and the manual suggesting a 20A receptacle.


Manual Suggesting a 20A Receptacle

The manual's suggestion of a 20A receptacle could be based on a few assumptions, none of which can be certain without further clarification. It might assume:

Short Duty Cycle

The sander is not used continuously at its maximum load.


Over-Amperage is Tolerable for Short Periods

The motor can handle slight overloads for short durations.

Misinformation

The manual is incorrect.


HP Calculation vs. Nameplate Amps

The HP calculation leading to a much higher FLA and breaker size could indicate the inrush current (starting current) is significantly higher than the running current. However, the nameplate is usually the key information.

The Correct Approach Based on the Information You Have
The most conservative and safest approach is to base the sizing on the nameplate amps (18A), and then see if the manual suggests another way.

This assumes that the nameplate information is accurate and the manufacturer has sized it to be at 18A at full load.

Here's a step-by-step process


Start with the Nameplate Amps (FLA)

Use the 18 amps as your starting point.2.

Overcurrent Protection (Breaker) Sizing



NEC 430.52 (Motor Overcurrent Protection)

The NEC allows you to size the overcurrent protection (circuit breaker) for a single motor based on a percentage of the motor's FLA. Typically, you can use an inverse time breaker up to 250% of the FLA.


Calculation

18 amps 250% = 45 amps.

Standard Breaker Size

You'd round down to the next lower standard breaker size, which would be a

40-amp breaker. The NEC specifically allows rounding down to the next lower standard size.

Alternative

While 250% is allowed, it is more to protect the cable, you may be able to do a lower percentage and start at 150% and see if the breaker trips during start up.3.

Conductor (Wire) Sizing



NEC 430.22 (Motor Circuit Conductors)

Conductors supplying a single motor must have an ampacity of at least 125% of the motor's FLA.

Calculation

18 amps
125% = 22.5 amps.

Wire Gauge Selection

Based on NEC Table 310.16 (ampacity of conductors), you'd need to choose a wire gauge that has an ampacity of at least 22.5 amps
after considering any derating factors (ambient temperature, number of conductors in a raceway, etc.). Typically for a circuit like this, you'll need at least a

12 AWG copper conductor. You MUST verify the ampacity of the conductor based on insulation type and installation conditions.

Grounding Conductor

Don't forget to size the equipment grounding conductor according to NEC Table 250.122.
4.


Receptacle and Plug



NEMA Configuration

Given the 110V voltage and likely a standard single-phase power supply, you're looking at NEMA 5 series receptacles and plugs.

Minimum Amperage

The receptacle's amperage rating must be equal to or
greater than the breaker's amperage rating. Since you are using a 40A breaker, you will need a NEMA 5-30 or 5-40 receptacle.

Locking Type

Because the sander is portable and subject to vibration, a locking-type receptacle and plug (e.g., NEMA L5-30) is highly recommended to prevent accidental disconnection.5.

Code Compliance and Inspections



Local Codes

Always check with your local electrical inspector or building department to ensure you are meeting local codes and regulations.


Inspection

Have your work inspected by a qualified electrical inspector.

Addressing the Original Questions



Can you use a 20A rated receptacle with a 20A breaker?

No, based on the nameplate information. The 18A load exceeds 80% of the 20A breaker, and more importantly, the NEC generally requires the receptacle amperage rating to be at least equal to the breaker rating in this situation, but NEC 210.21(B)(1) states that "Where a branch circuit supplies two or more receptacles or outlets, the receptacle rating shall not be less than the rating of the overcurrent device protecting the branch circuit."
18 125% leads to 22.5A cable and at least 25A breaker

Correct on the cable sizing. The overcurrent is actually sized up to 250%, leading to a 40A breaker.

Important Considerations



Motor Starting Characteristics

The 250% breaker sizing accounts for the motor's inrush current during starting. A 20A breaker would likely trip on startup. This is why the HP to Amps calculator can be misleading if you only use it to determine running amps.

Nameplate Accuracy

Double-check the nameplate information on the sander itself. Ensure it matches the information in the manual. If there are any discrepancies, contact the manufacturer for clarification.


Service Requirements

Check the service requirements of the machine; it may require a dedicated circuit and/or an isolation transformer depending on the manufacturer's guidelines.

In summary

You need to use a 40A breaker with a receptacle that is rated for 30/40A, with a 12 gauge cable.

Disclaimer: I am an AI chatbot and cannot provide professional electrical advice. This information is for general guidance only. Consult with a qualified electrician to ensure your installation meets all applicable codes and safety requirements. Flag for review

Previous Question Next Question