Topic: 4/3 NM cable as dwelling feed

User: nizak, Location: New Jersey

Asked on: Thursday, November 7, 2024 at 4:51 pm EST
Answered on: Thursday, March 6, 2025 at 4:57 am EST

Question: Existing single family dwelling built in the mid 80’s.Load center is being fed with 4/3 NM cable from an exterior disconnect protected by a 100 amp breaker.Am I correct in saying that wasn’t even compliant when it was new?I’m looking to upgrade the service . Will have an 8 space 3R 200 amp main breaker panel adjacent to the meter.Will that now need to be reduced to a 70 amp breaker because the NM rating for the 4/3 is 60 degree and it’s not feeding the entire dwelling?I will be adding an EV charger and taking that load from the new panel outside.Thanks

You've got a few points to address here, and it's important to get them right for safety and code compliance. Let's break it down

1. Was 4/3 NM cable on a 100A breaker compliant in the mid-1980s?
Likely No. This wasn't likely compliant. The ampacity of 4/3 NM cable is dictated by the 60-degree Celsius column in the ampacity tables (NEC 310.16) unless specifically permitted otherwise. This is almost always the case in residential applications. In the 60-degree column, 4 AWG copper is rated for only 70 amps. Therefore, a 100 amp breaker would have been an overcurrent violation.2. New Service Upgrade & NM Cable



The Issue

You're absolutely right to focus on the 60-degree ampacity of the 4/3 NM cable. The problem with relying on the existing NM cable is that the new panel is NOT serving the entire dwelling unit load as it did originally, so you CANNOT use the exception in 334.80 which allows you to use the 75 degree column.

The correct size breaker in the new panel

Since the cable isn’t being used to feed the entire dwelling, the breaker in the new panel is required to be rated for the 60 degree ampacity of the cable, or 70 Amps.

3. EV Charger Load



Load Calculation

The EV charger introduces a significant continuous load (125% of the charger's output). You'll need to perform a full service load calculation based on the current NEC (or your local adopted code) to determine the total load on your home. This calculation will include general lighting, small appliance circuits, laundry circuits, fixed appliances (water heater, HVAC, etc.), and the EV charger load.

Adequacy of Existing Wiring

After calculating your total load, compare it to the existing 70 amp capacity of the current wiring.
It's highly unlikely that a house originally designed for 100 amps, plus the additional EV charger load, will be adequately served by a 70-amp supply.
4. Upgrading the Service - What to do?


Given the issues outlined above, here's the recommended approach:
Replace the NM Cable

The best approach is to replace the 4/3 NM cable with a cable rated for the new amperage. If this is too difficult or cost prohibitive, you would need to derate the new breaker to the 60 degree rating.

Load Calculation

Absolutely essential. Don't guess! Perform a detailed load calculation to determine the minimum service size required. This is the foundation for your entire upgrade.

Consider Future Needs

Think about future expansion. Do you anticipate adding more electric appliances, another EV charger, or other significant loads? Oversizing the service slightly now can save you money and hassle later.

Important Considerations & Advice



Local Codes and Inspections

Everything you do MUST comply with local building codes and be inspected by a qualified electrical inspector. Contact your local building department to clarify any specific requirements in your area.

Licensed Electrician

Hire a qualified, licensed electrician to perform the service upgrade. This is not a DIY project, due to the potential for serious injury or death from working with electricity.*

Documentation

Keep detailed records of all calculations, wiring diagrams, and inspection approvals for future reference.

In summary:
The existing wiring situation was likely incorrect from the beginning. The new setup requires careful consideration of ampacity, load calculations, and code compliance. Replace the undersized NM cable. Flag for review