Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: TECO Westing House 12 Lead MAX-E1 Motor

User: Saturn_Europa, Location: Fishing Industry

Asked on: Thursday, November 7, 2024 at 6:56 pm EST
Answered on: Thursday, March 6, 2025 at 4:58 am EST

Question: The plant I work at has WYE 480V 3 phase.Just got in a rebuilt motor back. Its a 12 lead motor.I didnt unwire it.From what I am reading online it should be 4&7, 5&8, 6&9, 10&12&11 wired together. Then my line voltage to T1, T2 and T3.It will be running on a VFD.Let me know if this looks good.

Yes, based on the information you provided, your understanding of wiring a 12-lead motor for 480V WYE configuration for VFD operation is correct. Here's a breakdown and why it works: Understanding the Goal

You want to connect the motor windings in a WYE (also known as a Star) configuration suitable for 480V. A 12-lead motor offers flexibility to be wired for different voltage levels, either in WYE or Delta.


Your Configuration



4 & 7 Connected

This connects the start and end of one winding phase.


5 & 8 Connected

This connects the start and end of another winding phase.

6 & 9 Connected

This connects the start and end of the third winding phase.


10, 11, & 12 Connected

This connects the other end of each winding phase together. This creates the neutral point of the WYE connection.

Line Voltage to T1, T2, & T3

This connects the three phases of your 480V supply to the three remaining winding terminals.


Why It Works

This arrangement places the motor windings in series to handle the 480V input. The VFD then controls the frequency and voltage applied to the motor, allowing you to vary its speed.

Important Considerations & Best Practices



Motor Nameplate



VERIFY!
Always double-check the motor nameplate. It should explicitly state the wiring diagram for 460V/480V WYE. While your description is the common configuration, you absolutely need to confirm with the specific motor's diagram. Differences, though rare, can exist. Megger Test (Insulation Resistance Test)

Before applying power, perform a megger test on the motor windings to ensure there are no shorts or insulation breakdown. This is especially crucial for a rebuilt motor. A low megger reading indicates a problem and needs to be addressed before energizing the motor. Consult your company's procedures for acceptable megger values.

Rotation Check (Jog)

After wiring,
briefly jog (momentarily apply power) the motor to confirm it rotates in the correct direction. If it rotates in the wrong direction, swap any two of the input power leads (T1, T2, or T3) to reverse the rotation.

VFD Programming

Ensure your VFD is properly programmed for the motor's voltage (480V), current, frequency, and number of poles. Incorrect VFD settings can damage the motor.

Overload Protection

Set the VFD's overload protection settings to match the motor's nameplate FLA (Full Load Amps).


Grounding

Ensure the motor frame and VFD are properly grounded according to applicable electrical codes.

Motor Lead Numbers

Ensure the Motor lead numbers have not been changed from factory


Document Everything

Keep a record of the motor wiring configuration, VFD settings, and test results for future reference.

In summary:
Your understanding is likely correct, but absolutely verify with the motor nameplate diagram before applying power. Always follow safe electrical practices and consult with a qualified electrician if you have any doubts. Flag for review

Previous Question Next Question