Topic: water meter bond with 2 100amp main panels off 200amp 2 gang meter socket/bank

User: croyfish, Location: lake station, IN

Asked on: Thursday, November 7, 2024 at 7:26 pm EST
Answered on: Thursday, March 6, 2025 at 4:58 am EST

Question: (indiana 2008 NEC)this is a remodel job for a 2 unit residential job. there is a 200amp 2 gang meter socket with no disconnects. it will have 2 100amp main panels next to eachother in the basement. the building only has 1 water meter to service both units. what is the proper way to run the ground wire from the water meter to the service equipment? do I make 2 separate runs and take one each from water meter to each main panel or run 1 conducter to 1 panel? can someone provide some guidance and references to back up the proper installation?

Okay, let's break down the grounding requirements for your two-unit residential service remodel in Indiana under the 2008 NEC.

Understanding the Requirements

The 2008 NEC (and subsequent editions) prioritizes a robust grounding and bonding system to ensure safety and minimize electrical hazards. When you have multiple service panels fed from a single service entrance, you need to pay careful attention to the grounding electrode conductor (GEC) and bonding requirements.

Analysis and Correct Approach

Given your scenario (a single water meter serving both units and a 200A service with two 100A panels), the correct approach is to run one continuous grounding electrode conductor (GEC) from the water meter to one of the service panels. Here's why:1. Single Service Entrance

You have a single 200A service entrance feeding both units. The NEC treats this as a single service for grounding purposes. You don't have two distinct services.2.

Common Grounding Electrode

The water meter acts as the grounding electrode. NEC 250.50 and 250.52 generally require a grounding electrode system to be connected together to form the grounding electrode system.
3.

Bonding at the Service

The service equipment (your 2-gang meter socket and the 100A panels) must be bonded together. This is usually accomplished by bonding the enclosures and using a grounding busbar in each panel connected to the GEC.4.

Simplified Explanation

Think of it like this: the water pipe is your grounding electrode. You connect the grounding electrode conductor to it. That conductor goes to your main service disconnect/panel. All other panels are then grounded through the neutral conductor and equipment grounding conductors.

Step-by-Step Instructions


Here's the recommended installation procedure, based on the 2008 NEC:1. Grounding Electrode Conductor (GEC) to Water Meter

Run one continuous GEC from a suitable lug or clamp on the water meter (on the street side of the water meter). The GEC should be sized according to Table 250.66, based on the size of your service entrance conductors (the conductors from the meter socket to the panels). In your case, a 200 amp service typically uses a 4/0 aluminum or 2/0 copper service entrance conductor. Referencing Table 250.66, this would require a #4 copper or #2 aluminum grounding electrode conductor. This GEC should be continuous (no splices) unless it's made electrically continuous by irreversible compression-type connectors listed for the purpose. This ensures a reliable, low-impedance path to ground.2.

Connect GEC to One Service Panel

Extend the continuous GEC from the water meter to one of the 100A service panels. Terminate it on the grounding busbar in that panel. This panel becomes your primary grounding point.3.

Bonding Between Panels

You must have a grounding electrode conductor run to one panel and then use an equipment grounding conductor (EGC) to the other.4.

Additional Electrodes (If Necessary)



250.53(D)(2)
If a metal water pipe is used as a grounding electrode, it must be supplemented by an additional electrode. The supplemental grounding electrode must be bonded to the grounding electrode conductor. The additional electrode can be rod, pipe, or plate electrode or other electrodes as described in 250.52. The supplementary electrode provides redundancy and improves the overall grounding system.5. Main Bonding Jumper

In each service panel, you'll have a main bonding jumper (MBJ). This jumper connects the neutral bus to the enclosure. This jumper is critical because it bonds the neutral conductor (which is connected to the grounded service conductor from the utility) to the metal enclosure of the panel. The MBJ can be a screw, strap, or busbar, and its size must comply with Table 250.28.
6.


Equipment Grounding Conductors (EGCs)

Run separate EGCs from each branch circuit back to the grounding busbar in the panel. These EGCs provide a path for fault current to return to the source (transformer) and trip the breaker. For example, all metal boxes, appliance frames, and exposed metal parts of equipment must be connected to an EGC that runs back to the service panel's grounding busbar.

Code References (2008 NEC)
250.24 Grounding Service-Supplied Alternating-Current Systems. This section covers the general requirements for grounding AC systems. 250.50 Grounding Electrode System. This section requires you to create a "grounding electrode system" by connecting all available electrodes together. 250.52 Grounding Electrodes. Lists acceptable grounding electrodes (metal water pipe, concrete-encased electrode, ground ring, rods, pipes, etc.). 250.53 Grounding Electrode System Installation. Provides requirements for installing grounding electrodes, including the supplemental electrode requirement if using a metal water pipe. 250.64 Grounding Electrode Conductor Installation. Details the rules for the grounding electrode conductor (GEC), including continuity, protection, and bonding. Pay attention to 250.64(C) regarding connection to electrodes. 250.66 Size of Alternating-Current Grounding Electrode Conductor. Provides the table used to size the grounding electrode conductor based on the size of the service entrance conductors. 250.104 Bonding of Piping Systems and Exposed Structural Metal. Covers the bonding of metal water piping systems, gas piping, and structural metal to the grounding system. 250.146 Connecting Receptacle Grounding Terminal to Box. Article 100 Definitions Grounding Electrode ConductorImportant Considerations Local Amendments

Always check with your local electrical inspector for any local amendments to the NEC that may be in effect in your jurisdiction. They have the final say on what is required.


Proper Connections

Ensure all connections are made with approved connectors and fittings. The connections must be tight and corrosion-resistant.

Continuity

Verify the continuity of the grounding electrode conductor and the bonding jumpers with a multimeter
after installation.

Water Meter Jumper

If the water meter is removed for service or replacement, a jumper wire must be installed around it to maintain continuity of the grounding path.

Disclaimer:
I am an AI chatbot and cannot provide professional electrical advice. This information is for educational purposes only. Always consult with a licensed and qualified electrician for any electrical work. The correct installation must comply with the most recent version of the NEC adopted by your local jurisdiction, and be reviewed by a local electrical inspector. Flag for review