Topic: Can the same cable be class 1 for part of a circuit and class 2 for another at the same time?

User: Electrician123456789, Location: Florida

Asked on: Friday, November 8, 2024 at 7:00 am EST
Answered on: Thursday, March 6, 2025 at 4:59 am EST

Question: Is it okay to have cm cable cl2 in same conduit as line voltage to switch, but come out of a jbox and be in free air to fixtures at the same timeFrom what I've read, you can have the cable in the same conduit since the circuit is 120V and the cm cl2 cable is rated for 150V.The cable is re-classified as a class 1 and will have to be wired with chapter 3 wiring methods.But can the cable run down to the switch with 120V then come out of the box and jump to fixtures in free air or if it is in conduit to the switch, does it need to stay in conduit to the light? Can you have part of the 0-10V wiring be class 1 where it's in the conduit and call it class 2 when it's just in free air above the ceiling?I have read a lot of threads, but haven't seen this scenario.Thanks in advanceTom

Okay, Tom, let's break this down. You're asking about a mixed Class 1 (due to proximity to line voltage) and Class 2 (in free air) wiring situation for 0-10V dimming control. This is a common scenario, but there are specific rules you must follow.

Here's a summary of the key points and considerations


Sharing Conduit with Line Voltage



Yes, you
can share conduit with line voltage (120V in your case) if the CL2 cable is rated for at least the voltage of the power conductors and if you treat it as a Class 1 circuit within the conduit.
In your case, the CL2 cable is rated for 150V, exceeding the 120V requirement. Important: Insulation Rating is Key. The insulation rating of the CM/CL2 cable is paramount. It MUST be rated for at least the voltage of the power conductors in the raceway. Since the cable is rated for 150V, it should meet that threshold for a 120V circuit.2. Classification Change – The Big Consideration



Inside the Conduit: Class 1.
As you mentioned, when the CL2 cable shares the same conduit with line voltage, it becomes classified as a Class 1 circuit for the entire length of the cable within the conduit. This means you have to treat it as such and use Chapter 3 wiring methods inside the conduit. Class 1 Wiring Methods: This primarily means: Conductors

The CL2 cable
effectively becomes a bunch of individual conductors inside the conduit. Think of it as you are installing THHN conductors for low voltage.3.

Exiting the J-Box and Running in Free Air

This is where things get tricky:


The Problem

The critical question is whether you can transition back to Class 2 wiring after it exits the conduit. The NEC is not perfectly clear on this, and interpretations can vary.

The Generally Accepted (and safest) Interpretation



Once classified as Class 1 due to being in the same raceway as line voltage, the wiring REMAINS Class 1 for the entire run.
This means you cannot simply transition to "free air" Class 2 wiring after it exits the conduit. Reasoning

The concern is the potential for induced voltage/noise and the possibility of a fault transferring from the line voltage circuit to the low-voltage control circuit, even after it's out of the conduit. The NEC is very conservative regarding safety.

What This Means In Practice

If the 0-10V wiring shares a conduit with line voltage, then that 0-10V wiring is considered Class 1 wiring and is classified using chapter 3 wiring methods. So running 0-10V wire to a junction box in free air is not going to meet code requirements.4.

Alternatives and Solutions to Properly Meet Code Requirements



Option 1: Maintain Class 1 Wiring all the Way.
This is the safest and most straightforward approach. Continue to treat the cable as Class 1 wiring for the entire run to the light fixtures. This involves: Conduit/Raceway

Keep the wiring in conduit or a similar raceway system from the J-box to the fixtures.


Wiring Method

Use appropriate wiring methods for Class 1 circuits (e.g., THHN/THWN conductors in conduit).

Option 2: Separate Completely.
The best way to avoid the Class 1 classification is to completely separate the low-voltage wiring from the line-voltage wiring. This may involve: Separate Conduit

Run the 0-10V wiring in its own conduit, physically separated from the line-voltage conduit. Maintain sufficient separation as defined in the NEC.

Separate Boxes

Use separate junction boxes for line voltage and low voltage.


Physical Separation

Ensure the low-voltage cable doesn't come into direct contact with line-voltage wiring or equipment.

Option 3: Use a Barrier

You
might be able to use a physical barrier within the J-box to completely separate the line voltage and low voltage. This is highly dependent on the specific J-box, the type of barrier, and local inspector approval. This is often difficult to implement effectively.5.

Code References (Typical - Check Your Local Codes!)
NEC Article 725 (Class 1, Class 2, and Class 3 Remote Control, Signaling, and Power-Limited Circuits)

This article is essential. Read it carefully.

NEC Article 300 (Wiring Methods)

Covers general wiring methods and requirements.


NEC Article 310 (Conductors for General Wiring)

Covers conductor types and ratings.

NEC 725.55 (Separation from Electric Light, Power, Class 1, Nonpower-Limited Fire Alarm Circuit Conductors, and Medium-Power Network-Powered Broadband Communications Cables)

Addresses the separation requirements.


NEC 300.3(C) (Conductors of Different Systems)

Deals with conductors of different systems (line voltage and low voltage) in the same raceway.

In Summary

The safest, most reliable, and generally accepted approach is to treat the 0-10V wiring as Class 1 for its entire run if it shares conduit with line voltage. This means continuing the conduit/raceway system to the fixtures. Alternatively, completely separate the low-voltage and line-voltage wiring using separate conduits and boxes. Consult with your local electrical inspector for their interpretation of the code and the best solution for your specific situation. They have the final say.

Important Disclaimer:
I am an AI Chatbot and not a licensed electrician. This information is for educational purposes only and should not be considered a substitute for advice from a qualified and licensed electrician. Electrical work can be dangerous, and it is essential to follow all applicable codes and safety regulations. Always consult with a qualified electrician before performing any electrical work. Flag for review