Topic: Working Clearance for 5kv Wireway

User: bevans34, Location: Houston, TX

Asked on: Friday, November 8, 2024 at 10:52 am EST
Answered on: Thursday, March 6, 2025 at 4:59 am EST

Question: What is the proper working clearance needed for a juction box that 5kv wire is being pulled through?Scenario: Pullbox in between floors, going up from level 1 to level 8 of a building, containing 5kv wire. Route going through electric rooms and 277/480v panels are in front of the pull box. There is 4' -7 1/2" of clearance between the front cover of the pullbox and the front cover of the panel.Per NEC, Table 110.34(A), the working clearance for Condition 2 (exposed live parts on one side and grounded parts on the other side) says there needs to be 5ft of clearance for voltages between 2501-9000.

You are correct to reference NEC Table 110.34(A). Let's break down the analysis and address the specific situation.

Understanding the Requirements NEC 110.34(A)

This section of the National Electrical Code (NEC) dictates the
minimum working space about electrical equipment operating at 600 volts, nominal, or less to ground. The voltage ranges from 2501-9000, applies in your case.

Working Space

This space is required to permit safe operation, inspection, maintenance, and repair of electrical equipment.

Condition 2

This condition, as you stated, applies when there are exposed live parts on one side and grounded parts on the other side, or exposed live parts on both sides.


5ft Clearance Requirement

For your voltage range (2501-9000V) and Condition 2, Table 110.34(A) requires a minimum working clearance of 5 feet.

Applying the Rules to Your Scenario
1. The Pull Box

You're pulling 5kV wire through the pull box. While the conductors themselves are insulated, the potential for arcing and the presence of 5kV wire means the working space rules apply, especially if the pull box cover needs to be removed during the pull or for maintenance in the future.2.

Obstruction

You have 4' - 7 1/2" of clearance between the front cover of the pull box and the front cover of the 277/480V panel. This is

less than
the required 5 feet.3. Violation

Because the available clearance (4' 7 1/2") is less than the required minimum (5 feet), the installation is a violation of NEC 110.34(A).

Important Considerations and Potential Solutions
Equipment Grounding

Double-check that the pull box and any other metallic enclosures are properly grounded according to NEC Article 250. This is crucial for safety.


Enclosure Rating

Verify that the pull box is rated for the voltage and environmental conditions (e.g., NEMA rating).

Alternate Solutions



Relocate Equipment

The ideal solution is to relocate either the pull box or the panel(s) in front of it to achieve the required 5-foot clearance. This might involve physically moving equipment or rerouting conduits.

Modify Equipment Location (Less Desirable)

Depending on the building structure and other constraints, you
might be able to recess the pull box or the 277/480V panel into the wall to gain some space. This is less desirable because it can make future access and maintenance more difficult and may not be structurally feasible.

Engineering Judgement

An exception may be applied in certain instances by a qualified electrical engineer who can demonstrate equivalent safety. This would involve a thorough risk assessment and documentation showing how safety is maintained despite the reduced clearance. This would not be a preferred approach and would need AHJ approval.

Lockout/Tagout

Emphasize the importance of following proper lockout/tagout procedures whenever working on or near the 5kV system or the 277/480V panels.


Personal Protective Equipment (PPE)

Always use appropriate PPE when working with electrical equipment, including arc flash protection.

Conclusion


Based on the information you provided, the existing clearance is insufficient and violates NEC 110.34(A). Corrective action is required to comply with the code and ensure worker safety. Relocating either the pull box or the obstruction panels is typically the most straightforward solution. Consulting with a qualified electrical contractor and engineer is essential to determine the best course of action. Flag for review