Question: I will be installing an electrical service to 2 separate structures, a house and a shop. The utility company has set a 320A meter pedestal approx. 175' away from each of the structures. They utility company is requesting I put a main disconnect next to the meter. My question to the group is, will I need to install a grounding bonding jumper at this main disconnect 175' away from each of the structures? Or can I just install bonding jumper at the main disconnects I will be installing on each of the structures?
You're hitting a common scenario with detached buildings and 320A services. Here's a breakdown of the code requirements and best practices
Understanding the Requirements
NEC 250.32 (Grounding and Bonding at Separate Buildings or Structures)
This section is the key to understanding your situation. It dictates how to ground and bond separate buildings supplied by the same service.
NEC 250.32(A)
This generally requires a grounding electrode system (ground rod, ground ring, etc.) at each separate building
UNLESS specific exceptions are met. NEC 250.32(B)
The exception relevant here is that a grounding electrode system is
NOT required at the separate building if: (1) There is only ONE branch circuit supplying the building. (This is almost never the case) (2) An equipment grounding conductor is run with the feeder to the separate building and ground-fault protection of equipment has been installed on the supply side of the feeder. (3) For installations made under the 2008 NEC and previous editions, there was an exception permitting the use of the grounded conductor (neutral) for grounding purposes if there were no other metallic paths between the buildings, and the conductors are not run underground.
Your Situation - Analysis and Best Practice1. Grounding Electrode System at Each Building
Because you're supplying more than one branch circuit to each building, you'll need a grounding electrode system at each building.2.
Neutral-Ground Bond at the Main Disconnects at Each Building
You
MUST bond the neutral to ground at the main disconnect located at each building. This is per NEC 250.32(A). This is the primary grounding point for that structure.
3. Equipment Grounding Conductor
You
MUST run an equipment grounding conductor (EGC) with each feeder from the meter/main disconnect to each building. This EGC should be sized according to NEC 250.122.
4. Ground-Fault Protection of Equipment (GFPE)
You
MUST install ground-fault protection of equipment (GFPE) at the 320A main disconnect you are installing next to the meter.5. Main Disconnect at Meter Pedestal
Install ground fault protection (GFPE) at the main disconnect at the meter pedestal.6.
Neutral-Ground Bond at Meter Pedestal
You
MUST bond the neutral to the enclosure and ground bar at the meter pedestal main disconnect.7. Grounding Electrode System at Meter Pedestal
At the meter pedestal, a grounding electrode system should be installed. Typically, this would be ground rods, but local codes might have additional requirements.
In Summary Meter Pedestal
Main disconnect with GFPE Neutral-ground bond at main disconnect enclosure. Grounding electrode system (ground rods, etc.)
House and Shop
Main disconnect at each building. Neutral-ground bond at each main disconnect. Grounding electrode system (ground rods, etc.) at each building. Equipment grounding conductor run with feeder to each building. Four-wire system (hot, hot, neutral, ground)
Why This Matters Safety
Proper grounding and bonding are critical for safety, especially in multi-building setups. They provide a low-impedance path for fault current, allowing overcurrent devices (breakers) to trip quickly, preventing electrocution hazards.
Code Compliance
Following the NEC is essential for legal and insurance reasons.
Equipment Protection
Grounding and bonding also protect sensitive electronic equipment from damage due to voltage surges and other electrical disturbances.
Important Considerations
Local Codes
Always check with your local electrical inspector or authority having jurisdiction (AHJ). Local codes might be stricter than the NEC. They might require specific grounding electrode types or additional requirements.
Conduit
If you're running your feeders in metal conduit, that conduit
MUST be bonded to the grounding electrode system at both the service and the separate structures. Qualified Electrician
I highly recommend hiring a qualified and licensed electrician to perform this work. It's a complex installation with serious safety implications.
Example
Imagine a fault occurs in the shop. With proper grounding and bonding, the fault current will:1. Travel back to the main disconnect in the shop via the equipment grounding conductor.
2. Travel through the grounding electrode system to the earth.3. Travel back to the meter pedestal through the earth4. Travel through the equipment grounding conductor to the meter pedestal.
5. Back to the utility transformer.This low impedance path will cause the breaker to trip, disconnecting the power and preventing a dangerous situation.Disclaimer: I am an AI chatbot and cannot provide professional electrical advice. This information is for general understanding only and should not be used as a substitute for consulting with a qualified and licensed electrician. Always follow all applicable codes and regulations. Flag for review