Question: Hi all,I'm a home owner in the process of changing a circuit in my garage from a 240v to 120v. The wire is a 10/3 plus ground, so I'll cap and tape the red wire in the load center and box and install a single pole breaker using black wire. Two questions:1. Any issues with the above plan?2. My load center is a TL812SL and it says I can use "type THQP, TQP, TQL-AC, TQAL-AC, THQL-AC, THQAL-AC or TXQL" breakers. I've located a GE THQP120 breaker that will fit, but I've read there are issues with these starting fires when when used with aluminum bus bars, which my load center appears to have. I also have a GE THQL1120 breaker that appears to fit, but isn't listed on the load center. Is this THQL breaker ok to use?Thanks in advance!
Let's break down your plan and the breaker situation
1. Your 240v to 120v Conversion Plan:
Generally Sound
Your plan to cap and tape the red wire at both ends (load center and box) is the correct approach for repurposing the 10/3 wire. Using the black wire as your hot and the white as your neutral is standard practice. Connect the bare copper (or green) to ground at both ends.
Important Consideration
Make absolutely sure you've properly identified the wires with a voltmeter before you disconnect anything. Double and triple-check your connections. Electrical work is dangerous, and mistakes can be fatal.
Recommendation
Label the capped red wire at both ends (Load Center and Box) with something like "UNUSED 240V WIRE" so that future electricians (or yourself) understand what it is. A simple piece of electrical tape with a permanent marker is sufficient.
2. Breaker Selection: The Critical Part
This is where things get tricky and you need to be extra cautious. Using the wrong breaker can create a dangerous situation. GE TL812SL Load Center Compatibility
You correctly identified the list of approved breakers. This list is not a suggestion; it is a
requirement. Using a breaker not on the list can void the UL listing of the panel and, more importantly, creates a significant safety hazard. THQP120 and Aluminum Bus Bars
The issue you raised regarding THQP breakers and aluminum bus bars is valid and very important. There have been concerns about poor contact and potential overheating with THQP breakers on some aluminum bus bar panels. If you suspect your bus bars are aluminum,
DO NOT USE a THQP breaker without specific confirmation from GE (or a qualified electrician) that it is safe to use in your panel with your bus bar material. While some people have used them without immediate issues, the potential for problems over time is a real risk. THQL1120 and the Approved List
The fact that the THQL1120 is not on the approved list for your TL812SL load center is a
critical issue. Even if it appears to fit physically, do not use it. The manufacturer has specified the breakers that have been tested and approved for safe operation with that panel. Using a non-approved breaker could result in: Poor Electrical Contact
Leading to arcing, overheating, and fire.
Inadequate Overcurrent Protection
The breaker might not trip when it's supposed to, leading to damage to your wiring and potential fires.
Voided Warranty
If something goes wrong, your insurance company might deny a claim if you've used unapproved equipment.
Recommendations
Identify Bus Bar Material
Carefully examine your load center's bus bars. They are usually silver color if aluminum, but can be confused with tin-plated copper bus bars. Look for markings or labels on the load center that might indicate the bus bar material. If unsure,
consult a qualified electrician.2. Contact GE Directly
The best course of action is to contact GE's technical support directly. Provide them with the model number of your load center (TL812SL) and ask them about the suitability of the THQP120 and THQL1120 breakers, specifically addressing the aluminum bus bar concern if you have aluminum bus bars. You might need to send them photos of your panel and bus bars. They will provide the definitive answer.3.
Find an Approved Breaker
The safest approach is to stick to a breaker that is explicitly listed as compatible with your load center. Search for a THQP, TQP, TQL-AC, TQAL-AC, THQL-AC, THQAL-AC or TXQL breaker, taking the busbar material into account.4.
Consult a Qualified Electrician
If you are at all unsure about any of this, especially the breaker selection and bus bar material identification,
hire a licensed electrician. They can properly evaluate your panel, determine the correct breaker, and safely perform the wiring. Electrical work is not a place to cut corners.5. Double-Check Your Wiring
After installing the correct breaker, double-check your wiring with a multimeter before energizing the circuit.
In Summary:
While your wiring plan is generally correct, the breaker selection is the critical point. Never* use a breaker that is not specifically approved for your load center. If you suspect you have aluminum bus bars, be extra cautious with THQP breakers and consult GE or a qualified electrician. Safety first! Flag for review