Question: Set up is, single family dwelling that’s existing.Attached to it is a garage with an apartment above it (new build)For power and metering they plan on using an existing service approx 50’ away (underground fed service rack) that use to go to a trailer which is now gone.Anything wrong with them utilizing the existing service to feed a new basically apartment and garage attached to an existing structure?

Yes, there are several potential issues and considerations when utilizing an existing service to feed a new apartment and garage attached to an existing dwelling

1. Load Calculation:
The most crucial issue is performing a proper load calculation. The existing service was likely sized for the original single-family dwelling and possibly the trailer. Adding an apartment and garage significantly increases the load. You MUST calculate the new total load, including: Existing dwelling's load (lighting, appliances, HVAC, etc.) Apartment's load (lighting, appliances, HVAC, cooking equipment - especially electric ranges, dryers, water heaters) Garage load (lighting, outlets for tools, garage door opener, electric vehicle charging if planned) Compare the calculated load to the existing service's capacity (ampacity of the service conductors and the main breaker). If the calculated load exceeds the existing service's capacity, the service MUST be upgraded. Overloading the service is a significant fire hazard.2. Code Compliance (NEC and Local)



Separate Metering/Billing

Local codes or the utility company may require separate metering for the apartment, especially if it will be rented out. This allows for individual billing of electrical usage. If required, you'll need to install a new meter socket and possibly a new service disconnect specifically for the apartment. Check with the local AHJ (Authority Having Jurisdiction) and the utility company.

Overcurrent Protection

Each dwelling unit (the existing house and the new apartment) must have its own overcurrent protection (circuit breakers or fuses) at the service entrance or within each unit.


Grounding and Bonding

Ensure the grounding and bonding system is adequate and up to code. Pay particular attention to bonding of metal water pipes, gas pipes, and structural steel.

Arc-Fault Circuit Interrupters (AFCIs) and Ground-Fault Circuit Interrupters (GFCIs)

The NEC has specific requirements for AFCI and GFCI protection in dwellings. The apartment will need to be wired with these devices where required by code.


Permits and Inspections

This project absolutely requires electrical permits and inspections. Do NOT skip this step. The inspector will verify code compliance and the safety of the installation.

3. Service Entrance Equipment



Condition of Existing Equipment

Thoroughly inspect the existing service entrance equipment (meter socket, service disconnect, panelboard). Look for signs of corrosion, damage, or overheating. If the equipment is old or in poor condition, it may need to be replaced regardless of the load calculation.


Accessibility

Ensure the service disconnect is readily accessible to both the homeowner and, if separate metering is used, to the apartment tenant.

Physical Space

Is there enough physical space in the existing service panel to add all the necessary circuit breakers for the apartment and garage? If not, a subpanel will be required.

4. Wiring and Conduit



Conductor Size and Type

Ensure the existing underground service conductors are properly sized for the new load and are of the correct type for underground burial.

Conduit Condition

Inspect the existing underground conduit. If it is damaged or deteriorated, it will need to be repaired or replaced.


Separation of Circuits

Generally, circuits from different dwelling units should not share the same conduit.

5. Ownership and Legal Considerations



Shared Service

If the apartment and house share the same meter, who is responsible for the electricity bill? This should be clearly defined in a lease agreement or other legal document.


Easements and Right-of-Way

Verify that the underground service cable is located within a legally established easement or right-of-way.

In summary:


The plan could be feasible, but only after a thorough investigation and detailed load calculation. It is highly likely that the existing service will need to be upgraded. This is NOT a DIY project. Hire a qualified, licensed electrician to perform the load calculation, assess the existing service, and perform the necessary electrical work to code. Obtain all required permits and inspections. Ignoring these steps could result in a dangerous and illegal installation. Contact your local AHJ (Authority Having Jurisdiction) and utility company for specific requirements. Flag for review