Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Optional Method

User: SonofAdam, Location: Portland Oregon

Asked on: Friday, November 8, 2024 at 8:07 pm EST
Answered on: Thursday, March 6, 2025 at 5:01 am EST

Question: Good evening,What's the rule for doing the optional method for a duplex...? I had notes on it somewhere but i can't seem to find them..I remember something along the line that you treat it as 3? Any tips appreciated, taking my masters soon

Okay, let's break down the Optional Method (sometimes referred to as the Simplified Method or Streamlined Approach) for calculating electrical service load for a duplex dwelling unit. This method is typically found in the National Electrical Code (NEC), specifically in Article 220.80 through 220.87, and sometimes referred to as the "Optional Calculations for Dwellings."Key Principles of the Optional Method for Duplexes


You DO NOT treat it as "3."
That's incorrect. You treat it as TWO dwelling units. The Optional Method simplifies the calculation for each individual dwelling unit, and then you sum the results to get the total service load.2. It's for the Entire Service

The Optional Method is designed to calculate the entire service load for the duplex. This includes both the general loads within each dwelling unit AND any common areas served by the same meter (e.g., hallway lighting, laundry, etc.)3.

Higher Demand Factors

The Optional Method typically uses higher demand factors than the standard calculation method (Article 220 Part III and IV). This is because it's a more simplified approach that assumes a greater degree of simultaneous usage.4.

No Reductions for Non-Coincident Loads

Unlike the standard calculation, you generally don't get to deduct for loads that are unlikely to be used at the same time (e.g., you don't get to say "well, only one water heater will be on at a time").

Steps to Use the Optional Method for a Duplex


Calculate Load for Each Dwelling Unit Separately



General Lighting and Small Appliance Load

3 VA per square foot of living area (NEC 220.14(J) and 220.12(A)).


Appliance Circuits

Add 1500VA for each 20-ampere small appliance branch circuit (NEC 220.16(A)). Typically, you will have at least two small appliance branch circuits for the kitchen.

Laundry Circuit

Add 1500VA for the laundry circuit (NEC 220.16(B)).


Fixed Appliances (Heating, A/C, Water Heaters, Ranges, etc.)

Use the nameplate rating of each appliance. Consider any demand factors permitted by the NEC (e.g., for ranges - see 220.55). Use the largest of either heating OR cooling (but not both at 100%).

Electric Vehicle Supply Equipment (EVSE) and other loads

Ensure to include any other applicable loads, adhering to the correct sections for load calculation per the NEC.2.

Apply the Optional Method Demand Factors (NEC 220.82)



First 10 kVA

100% demand factor.

Remainder above 10 kVA

40% demand factor.3.

Sum the Results of Each Dwelling Unit

Add the calculated load for dwelling unit #1 to the calculated load for dwelling unit #2.4.

Add Common Area Loads

Include any common area loads served by the same meter. These are typically added at 100% demand factor. Common loads may include: Hallway Lighting Outdoor Lighting Common Laundry Facilities (if not metered separately) Water Pumps Anything else not within a single dwelling unit.5.

Calculate the Total Service Load

The sum of the individual dwelling unit loads and the common area loads is your total service load.

Example (Simplified)

Let's say you have a duplex.

Dwelling Unit #1

1200 sq ft Electric Range (8 kW) Electric Water Heater (4.5 kW) Central A/C (3 kW)

Dwelling Unit #2

1200 sq ft Electric Range (8 kW) Electric Water Heater (4.5 kW) Central A/C (3 kW)

Common Area

Hallway Lighting: 200 VA

Calculations (using a simplified approach)



Dwelling Unit #1

General Lighting/Small Appliance: 1200 sq ft 3 VA/sq ft = 3600 VA Appliance Circuits: 2 1500VA = 3000VA Laundry Circuit: 1500VA Range: 8000 VA Water Heater: 4500VA A/C: 3000VA Total VA: 3600 + 3000 + 1500 + 8000 + 4500 + 3000 = 23600 VA Applying Demand Factors: First 10 kVA (10,000 VA): 100% = 10,000 VA Remaining 13,600 VA 40% = 5440 VA Total Dwelling Unit #1 Load: 10000 + 5440 = 15440 VA

Dwelling Unit #2 (identical loads)

Total Dwelling Unit #2 Load: 15440 VA

Common Area

Hallway Lighting: 200 VA (at 100%)

Total Service Load

15440 VA + 15440 VA + 200 VA =

31,080 VA
Important Considerations for Your Exam



Read the Question Carefully

Determine if the question specifically requires the Optional Method. If it doesn't, you should use the standard calculation method.


Know the NEC Article Numbers

Be familiar with where to find the Optional Method in the NEC.

Understand Demand Factors

Know the demand factors that apply to different types of loads.


Remember to include all loads

Don't forget things like water heaters, ranges, air conditioners, and common area lighting.

Ranges

Pay attention to the range calculations. Table 220.55 provides specific demand factors for ranges based on their rating and number.


Largest Motor

If there is a motor load (e.g., for a well pump) be sure to include it.

Why the Optional Method?


The Optional Method provides a quicker way to calculate the service load for dwellings, which can be useful for straightforward installations. It generally results in a slightly larger calculated load than the standard method because of the higher demand factors, which is considered a conservative approach.

Key Differences Between Standard and Optional Methods



Demand Factors

Optional method generally has higher demand factors.


Detail:
Standard method allows for more specific deductions for non-coincident loads. Optional method is less granular.Good luck with your Masters exam! Focus on understanding the NEC and practicing calculations. Flag for review

Previous Question Next Question