Topic: Yoke and receptacle count for load calc

User: solarken, Location: Hudson, OH, USA

Asked on: Saturday, November 9, 2024 at 11:42 am EST
Answered on: Thursday, March 6, 2025 at 5:02 am EST

Question: 2023 NEC in 220.14(I) has some nomenclature that does not appear to be defined and is confusing to me. Specifies "180VA for each single or multiple receptacle on one yoke". Yoke does not appear to be defined, but appears to refer to the physical piece of equipment that contains a single or duplex receptacle, that is then mounted in a box.The next sentence specifies "A single piece of equipment consisting of a multiple receptacle comprised of four or more receptacles shall be calculated at not less than 90VA per receptacle".From the above two code references, is this true?Add 180VA for a single receptacle in a boxAdd 180VA for a duplex receptacle in a boxAdd 4 x 90VA = 360 VA for two duplex receptacles mounted in a 2-gang boxAlso, to clarify, are both a single or a duplex receptacle considered one outlet?

You are on the right track with your interpretation of 220.14(I) in the 2023 NEC, and your deductions are generally correct. Let's break it down: Yoke

While "yoke" isn't formally defined in the NEC, your understanding is correct. It refers to the mounting strap or frame that supports the receptacle(s) and is attached to the box.


180VA per single or multiple receptacle on one yoke

This means that any single device on a single yoke is 180VA.

Multiple receptacles (4 or more) on one piece of equipment

This refers to a single manufactured unit that contains four or more receptacles. For example, a power strip permanently mounted to the wall or a single large outlet containing 4 or more receptacles. Each receptacle on such a device is calculated at 90VA, but the piece of equipment has to be a single manufactured unit.

Therefore, based on the 2023 NEC 220.14(I), your following statements are TRUE



Add 180VA for a single receptacle in a box

Correct.

Add 180VA for a duplex receptacle in a box

Correct.


Add 4 x 90VA = 360 VA for two duplex receptacles mounted in a 2-gang box

Correct if it's a single piece of equipment. This is not typical and unlikely in most residential and commercial installations. If it is two separate duplex receptacles each would be 180VA.

Clarification on Outlets



Both a single or a duplex receptacle are considered one outlet for the purposes of 220.14(I).
The code is focusing on the physical mounting point (the yoke) rather than the number of individual plug-in points.

In summary

The intent of the code is to simplify load calculations for general-use receptacles. It recognizes that it's often unknown what will be plugged into these receptacles, so it assigns a standard VA value to each outlet based on the number of receptacles on the yoke.

Important Note

This section of the code is for
general-use receptacles. There are other rules for specific appliances or equipment that have known power consumption (e.g., a dedicated circuit for a refrigerator). In those cases, you use the actual nameplate rating of the appliance.

Disclaimer:
I am an AI chatbot and cannot provide definitive electrical code interpretations. Always consult a qualified electrical inspector or engineer for project-specific guidance.* Flag for review