Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Filler plates in a "dead-front" - derate kaic?

User: grasfulls, Location: Placer County. CA

Asked on: Saturday, November 9, 2024 at 9:28 pm EST
Answered on: Thursday, March 6, 2025 at 5:03 am EST

Question: Using a SQD HOM612L100FCP as an example of a panel manufactured with no door. I have not looked at the specs, but I assume it is rated at 10kaic. I assume this rating means that, with breakers installed or not, and though there is no door, it can contain a surge up to 10kaic, not allowing it to blast outward and potentially cause damage to a person or property. If I break out one more space than I need, does a filler plate now degrade the inrush rating? Should all empty spaces in a panel be filled with unused breakers to maintain the panel's rating? The only thing a filler plate seems to do is protect from exposed live parts.

Let's break down your questions regarding the SQD HOM612L100FCP and its AIC rating, filler plates, and overall safety.

Understanding AIC (Amperes Interrupting Capacity) AIC Rating Explained

The AIC rating (10kAIC in your example) of the panelboard indicates the maximum short-circuit current (measured in kiloamperes, kA) that the
entire assembled panel can safely interrupt without failing catastrophically (e.g., exploding, melting down, causing a fire). It's a crucial safety specification. The interrupting rating of the breakers installed in the panel must be less than or equal to the AIC rating of the panel to be UL or ETL compliant.

Containing the Surge

You are generally correct. The panelboard enclosure, along with its internal design and properly installed breakers, is engineered to contain the energy and byproducts (arcs, heat, pressure) generated during a short-circuit event up to its rated AIC. This prevents the event from blasting outward and causing harm.

Filler Plates and AIC Rating
Impact of Removing a Knockout/Breaking Out an Extra Space

Breaking out an extra knockout (or breaking out more spaces than necessary)
can potentially degrade the overall AIC rating of the enclosure if it creates a significant opening that weakens its structural integrity or compromises its ability to contain the arc and gases produced during a fault.

Filler Plates and AIC Rating

A properly installed, UL-listed filler plate specifically designed for that panel should not degrade the AIC rating. The filler plate is designed to maintain the enclosure's integrity. A good quality filler plate is a key component in this regard.

Importance of Proper Filler Plates

Using the
correct filler plate (matching the panel manufacturer and intended use) is vital. A piece of cardboard or electrical tape won't cut it! The filler plate must be robust enough to withstand the pressure and heat generated during a short circuit.

Why Empty Spaces Shouldn't Be Filled with Unused Breakers
Cost

Unused breakers cost money.

Panel Space

If the panel is already full, this would only waste space.


Unnecessary risk

An unused breaker may be utilized to power something beyond the AIC rating of the panel.

The Role of Filler Plates: More Than Just Live Part Protection


You're right that filler plates protect against accidental contact with live parts. However, they also serve these important functions: Maintaining Enclosure Integrity

As mentioned, they reinforce the enclosure's ability to contain a fault.


Preventing Dust and Moisture Ingress

They help maintain the environmental rating (e.g., NEMA rating) of the panel, protecting the internal components from dust, moisture, and other contaminants.*

Supporting Bus Bar Stability (Potentially)

In some panel designs, filler plates can provide additional support to the bus bars, helping to maintain their alignment and prevent movement during a fault.

Key Takeaways and Best Practices
1. Always Use the Correct Filler Plates

Use only UL-listed filler plates that are specifically designed for your panel model. Don't improvise with other materials. Check the panel manufacturer's documentation for approved filler plate options.2.

Don't Over-Break Knockouts

Be precise when breaking out knockouts. Avoid breaking out more than you need.3.

Maintain Enclosure Integrity

Ensure the enclosure door (if applicable) is properly installed and closed. Damaged or missing parts can compromise the panel's safety.4.

Proper Installation

Always install breakers and other components according to the manufacturer's instructions. Torque connections correctly.5.

Consult the Manufacturer

If you have any doubts about AIC ratings, filler plates, or any other aspect of panelboard safety, consult the panel manufacturer or a qualified electrical engineer.6.

Never Exceed the AIC Rating:
It's a critical safety limit. Ensure your electrical system design and breaker selection keep the potential fault current below the panel's AIC rating.In conclusion, filler plates are a critical safety component in a panelboard. They contribute to maintaining the AIC rating and ensuring that the enclosure can safely contain a fault. Always use the correct filler plates and follow all manufacturer's instructions. Flag for review

Previous Question Next Question