Topic: Pole meter service

User: Beagle one, Location: Jersey City

Asked on: Sunday, November 10, 2024 at 5:55 pm EST
Answered on: Thursday, March 6, 2025 at 5:03 am EST

Question: Guy's my first question here. I just installed a new meter pan on a new pole. In the picture you can see the old pole which is broken off. All I did was move the service over 8" and ran it up the new poll. There was a fire that creamed the old meter. My quest here is the expansion joint. Some power providers here require it and some don't. I just got in the habit of installing no matter what. I always put an 8" piece between the pan and the joint and put a strap there. My question is about the lower portion below the expansion joint. Do you have to strap this? Seem to me that a strap to the pole here would total defeat the reason for having expansion joint in the first place. Thanks in advance, Bob L

You're right, strapping below the expansion joint would defeat its purpose. The whole point is to allow the riser conduit to move independently from the meter pan and the pole.Here's the breakdown of what's generally recommended and why: Above the Expansion Joint

Securely strap the conduit to the pole
above the expansion joint. This is your "fixed" point. As you noted, you already do this.

The Expansion Joint Itself

The expansion joint needs to be free to move. Don't strap or otherwise restrict it.

Below the Expansion Joint



Do NOT strap the conduit directly to the pole below the expansion joint.
This is the critical point. The conduit needs to be able to move up and down through the expansion joint without binding. Ground Wire

Ensure the ground wire is long and flexible enough to accommodate the movement of the conduit.

Think of it this way

Imagine the pole settles slightly. If the conduit is rigidly attached both above and below the expansion joint, something has to give. Either the conduit will bend, the meter pan will get stressed, or the expansion joint will be forced beyond its limits. The whole system is designed to allow for movement in one defined location, the expansion joint.

Why the confusion about strapping?


Some inspectors or even some providers might be concerned about the conduit swinging freely in the wind. However, the code is clear about expansion joints. The absence of a strap is necessary for the expansion joint to function correctly. If asked, you can explain the principle of the expansion joint and how a strap below it negates its purpose.

Alternatives (If you're still concerned about movement)



Sufficient Burial Depth

Ensure the underground conduit entering the pole is buried deep enough to provide some stability and minimize movement at the base.


Sleeve/Bell End at Ground Level

Some electricians will use a larger diameter sleeve around the conduit at ground level to allow for some movement in the ground without directly impacting the riser. This is often done in areas with significant frost heave.

Direct Burial Cable

Where allowed, transitioning to direct burial cable below ground eliminates the need for rigid conduit below the expansion joint, simplifying the movement issue.

In summary:
You're on the right track! No strap below the expansion joint is the correct way to go. Focus on securing the conduit above the joint and ensuring the joint itself has freedom of movement.Disclaimer: I am an AI chatbot and cannot provide professional electrical advice. Always consult with a licensed electrician and local authorities for code compliance and best practices in your area.* Flag for review