Topic: 2 transformers Z

User: chris kennedy, Location: Miami Fla.

Asked on: Monday, November 11, 2024 at 10:27 am EST
Answered on: Thursday, March 6, 2025 at 5:04 am EST

Question: I have 2 100kVa transformers I’m doing available fault current calc for.240V delta systemI know I add the kVa’a together and I also need to add the Z’s together also correct?Thanks

Okay, let's break down how to calculate the available fault current for two transformers in parallel on a 240V delta system. You're on the right track, but there are a couple of crucial points to clarify about impedances.

Understanding the Goal

The goal of a fault current calculation is to determine the maximum current that could flow during a short circuit (fault) condition. This is essential for selecting properly rated overcurrent protection devices (circuit breakers, fuses) to safely interrupt the fault and prevent equipment damage or hazards.

Steps for Calculating Fault Current

Here's a breakdown of the process:1. Determine Transformer Impedance (Z)

You need the impedance of each transformer. This is usually given as a percentage on the transformer's nameplate (%Z). If it's not, you'll need to get it from the transformer's specifications or manufacturer. Let's assume for this example that both transformers have a %Z of 5%.2.

Convert Percentage Impedance to Per-Unit Impedance (pu)

Divide the percentage impedance by 100. So, 5% becomes 0.05 pu.
3.


Calculate the Base Impedance (Zbase)

Use the following formula: Zbase = (kVbase2) / MVAbase Where: kVbase is the voltage of the system in kV (so 240V becomes 0.24 kV) MVAbase is the total kVA of both transformers converted to MVA. You correctly identified to add the kVA. So 100 kVA + 100 kVA = 200 kVA, which is 0.2 MVA. Therefore: Zbase = (0.242) / 0.2 = 0.288 ohms4.

Calculate the per-unit impedance for each transformer.


Zpu = %Z/100In this case 5/100 = 0.05 puThen convert Zpu to ohms by using the base impedance from step 3:Zohms = Zpu
ZbaseSo, Zohms = 0.05 0.288 = 0.0144 ohms5. Combine Transformer Impedances (in parallel)

This is the crucial part about impedances. When transformers are in parallel, you don't simply add their impedances. Instead, you need to calculate the equivalent impedance of parallel impedances. The easiest way to do this is using the reciprocal formula:1/Ztotal = 1/Z1 + 1/Z2Where Z1 and Z2 are the impedances of each transformer (in ohms, calculated above).So:1/Ztotal = 1/0.0144 + 1/0.01441/Ztotal = 69.44 + 69.44 = 138.88Ztotal = 1 / 138.88 = 0.0072 ohms6.

Calculate the Fault Current (Ifault)

Use Ohm's Law:
Ifault = Vsystem / Ztotal Where: Vsystem is the system voltage (240V). Ztotal is the total impedance calculated in step 5 (0.0072 ohms) Ifault = 240 / 0.0072 = 33,333 amps

Important Considerations



Source Impedance (Utility)

This calculation
only considers the transformer impedances. In reality, you must include the impedance of the utility source (the power company's supply). The utility's impedance will limit the fault current. You'll need to get this information from the utility company. Failing to include the source impedance will result in a significantly higher (and inaccurate) fault current calculation. A conservative approach when source impedance isn't available is to assume infinite bus (zero impedance), which leads to the highest possible fault current. This might lead to over-sizing equipment, but ensures safety.

Cable Impedance

The impedance of the conductors between the transformer and the point of the fault will also reduce the fault current. For longer runs, this should be considered.

X/R Ratio

For more accurate calculations, especially for circuit breaker interrupting ratings, consider the X/R ratio (reactance to resistance) of the transformers and the system. Software tools often handle this complexity.


Software Tools

For complex systems, it's highly recommended to use specialized power system analysis software (e.g., SKM PowerTools, ETAP, EasyPower). These tools automate the calculations, account for various factors, and provide comprehensive reports.

Nameplate Data

Always use the actual nameplate data from the transformers. Do not guess.

Code Compliance

Ensure your calculations and equipment selections comply with the National Electrical Code (NEC) or other applicable local codes.

In summary:
1. Get the %Z from the transformer nameplates.
2. Calculate the per-unit impedance based on the total kVA.3. Convert the per-unit impedance to ohms using the base impedance.
4. Combine the impedances of the two transformers
in parallel* using the reciprocal formula.5. Include the utility source impedance (absolutely critical!).
6. Calculate the fault current using Ohm's Law.7. Verify your calculations with a qualified electrical engineer, especially for complex systems.Doing this properly is crucial for safety and reliable power system operation. Don't hesitate to consult with a professional if you have any doubts. Flag for review