Asked on: Monday, November 11, 2024 at 11:31 am EST
Answered on: Thursday, March 6, 2025 at 5:04 am EST
Question: We have recently upgraded our crimpers at our facility and have been trying to find the best lugs to use with them.We use mostly #8-373 DLO cable and we use Burndy YAV-FX series lugs rated for use on DLO cable.The issue we are having is that wings are being left on the sides of the lugs after crimping. The dies we are using match Burndy's Die Chart for this lug.Is this normal for this style of Crimper?
The "wings" you're describing after crimping YAV-FX lugs onto DLO cable using the Burndy-recommended die are not inherently normal. Here's a breakdown of what might be happening and what you should check
Possible Causes & Solutions:
1. Die Mismatch (Despite Die Chart)
Double-Check EVERYTHING
Go back to the Burndy die chart and VERY CAREFULLY verify the die number against the exact lug catalog number (YAV-FX and then the specific size for #8 DLO). A slight mismatch can cause this.
Die Wear/Damage
Inspect the dies themselves closely. Look for cracks, gouges, or other damage. Even minor wear can change the crimp profile. If the dies are old or heavily used, replace them.
Incorrect Die Installation
Ensure the dies are properly installed in the crimper, seated correctly, and locked in place. A misaligned die can produce an uneven crimp.
Die Orientation
Some dies have a specific orientation within the crimper (top/bottom, left/right). Refer to the crimper's manual and the die markings to ensure correct positioning.2.
Cable Size/Stranding Issue
Verify Cable Size
Double-check that the #8-373 DLO cable actually measures as a true #8 cable. Manufacturing variations can sometimes occur.
DLO Stranding Consistency
While DLO is generally consistent, there can be subtle differences in the number of strands or the diameter of individual strands from different manufacturers. This can slightly affect the crimp. Consider trying a different batch or manufacturer of DLO cable as a test.
Over-Stripping
Ensure you are not stripping too much insulation off the cable. Too much exposed conductor can lead to bulging during the crimp. Use a wire stripper that provides a consistent strip length, or follow the lug manufacturer's recommended strip length.3.
Crimper Issue
Crimper Calibration
Is your new crimper properly calibrated? Even brand-new tools can be slightly out of spec. Check with the crimper manufacturer for their calibration procedures.
Crimper Power/Force
For hydraulic or powered crimpers, ensure the pressure setting is correct. Too little pressure can lead to incomplete crimps and wings. Too much pressure can over-compress the lug.
Crimper Condition
Inspect the crimper itself for any damage, loose parts, or wear. Worn pins, linkages, or hydraulic seals can affect the crimp.
Crimping Technique
Ensure the lug and cable are properly positioned within the dies before initiating the crimp. The cable should be fully inserted into the lug barrel. Hold the crimper perpendicular to the lug during the crimp.4.
Lug Storage/Condition
Lug Storage
Store lugs in a dry, clean environment. Corrosion or contamination can affect the crimp.
Lug Damage
Inspect lugs for any damage or deformation before use.5.
Burndy Documentation
Consult Burndy directly! They are the experts on their lugs and crimping recommendations. Contact Burndy Technical Support. They may have encountered this issue before and can provide specific guidance based on your equipment.
Troubleshooting Steps
Start with the Basics
Double-check die numbers, cable size, and lug catalog numbers.2.
Visual Inspection
Carefully examine the dies, crimper, and lugs for any signs of damage or wear.3.
Calibration Check
If possible, check the crimper's calibration.4.
Controlled Experiment
Use a new, known-good lug and a piece of new DLO cable. Slowly and carefully perform the crimp, observing the entire process. If wings still appear, carefully inspect the crimp profile.5.
Compare Crimp Profiles
If possible, compare the crimp profile of your crimped lug to a sample crimp from Burndy or a known good crimp.
Why Wings Are a Problem
Reduced Conductivity
Wings can prevent full contact between the lug and the cable strands, reducing current-carrying capacity.
Weakened Connection
Wings can weaken the mechanical strength of the crimp, making it more prone to failure under stress or vibration.
Sharp Edges
Wings can create sharp edges that can damage insulation or pose a safety hazard.
Corrosion Points
Wings can trap moisture and debris, leading to corrosion.
Important Safety Note: A properly crimped connection is critical for electrical safety. If you are unsure about the crimping process or the quality of the connection, consult a qualified electrician. Flag for review