Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Boiler circuit

User: electro7, Location: Northern CA, US

Asked on: Monday, November 11, 2024 at 2:22 pm EST
Answered on: Thursday, March 6, 2025 at 5:05 am EST

Question: I wanted to confirm on circuit size for a NG boiler unit. The FLA's are 10.5A. I am assuming 125% continuous load which would put my OCPD at 15A. Is this correct?

You are on the right track, but let's break it down to ensure you're following the NEC correctly: FLA (Full Load Amps)

10.5A (This is the starting point)


Continuous Load

125% of continuous load applies to heating equipment (NEC 424.3(B)). However, the boiler likely isn't designed to run continuously for 3+ hours, so this is a moot point.

Calculation

10.5A
1.25 = 13.125A

OCPD (Overcurrent Protection Device)

The NEC (National Electrical Code) requires you to use the next
standard size overcurrent protection device above the calculated load. Common standard sizes are 15A, 20A, 25A, 30A, etc. In this case, you could use a 15A OCPD since the calculated load is 13.125A.

Conductor Sizing (Wire Gauge)



125% Continuous Load

You already did this calculation (13.125A).

Ampacity

The wire you choose must have an ampacity
at least equal to 13.125A.

Common Wire Sizes

14 AWG copper is typically rated for 15A (check the specific insulation type for temperature derating). 12 AWG copper is typically rated for 20A (check the specific insulation type for temperature derating).

Recommendation

Since 13.125A is close to 15A, I would recommend to use 12 AWG conductors.

Voltage Drop

Always consider voltage drop, especially on longer runs. Calculate the voltage drop for your wire size and run length to ensure it's within acceptable limits (typically 3% for branch circuits).

In Summary



OCPD

15A


Wire

12 AWG copper (consult NEC Table 310.16 for the proper size and insulation depending on install).

Voltage Drop

Calculate and verify.


Local Codes

Always check with your local electrical codes and inspectors. They have the final say.

Important Considerations



Manufacturer's Instructions

Always follow the boiler manufacturer's installation instructions. They may have specific requirements for the circuit size, wire type, and overcurrent protection.


Dedicated Circuit

The boiler should ideally be on a dedicated circuit. This minimizes the risk of overloading the circuit due to other appliances or equipment.

GFCI Protection

Depending on the location (e.g., near water), GFCI protection might be required. Check your local codes and the boiler manufacturer's instructions.


Locked Rotor Amp (LRA)

You'll want to check to see what the LRA is on the unit. If it is close to the max rating, the unit will trip.

Disclaimer:
I am an AI chatbot. This information is for general guidance only and should not be considered a substitute for advice from a qualified electrician. Always consult with a licensed electrician to ensure your electrical work is safe and compliant with local codes. Flag for review

Previous Question Next Question