Topic: Next size fuse breaker

User: mannyb, Location: Florida

Asked on: Monday, November 11, 2024 at 3:43 pm EST
Answered on: Thursday, March 6, 2025 at 5:05 am EST

Question: Set of parallel 500mcm aluminum wire rated at 310a is good for 620amps can the next size fuse is 800a. Could this be possible or not?

Okay, let's break down this scenario and see if an 800A fuse is appropriate for a set of parallel 500 kcmil aluminum conductors rated at 310A each.

Understanding the Basics 500 kcmil Aluminum

This refers to the size of the aluminum conductor. "kcmil" means "thousand circular mils," a unit of area.


Ampacity

The ampacity is the current-carrying capacity of a conductor, determined by factors like its material, size, insulation, and installation conditions (temperature, conduit fill, etc.). A single 500 kcmil aluminum conductor is rated at 310A based on standard tables (like NEC Table 310.16).

Parallel Conductors

Running conductors in parallel means connecting multiple conductors of the same size in parallel to increase the overall ampacity.


Overcurrent Protection (Fuses/Circuit Breakers)

These devices are designed to protect conductors and equipment from overloads and short circuits by interrupting the current flow when it exceeds a safe level.

NEC (National Electrical Code)

The NEC is a widely adopted standard for safe electrical installations. It provides rules and guidelines for sizing conductors and overcurrent protection.

Analysis
1. Total Ampacity of Parallel Conductors

You have two 500 kcmil aluminum conductors in parallel, each rated at 310A. Therefore, the combined ampacity is 310A + 310A = 620A.2.

Purpose of Overcurrent Protection

The
primary purpose of the fuse or circuit breaker is to protect the conductors from overheating and potential fire hazards. It needs to trip before the conductors are damaged.3.

NEC Guidelines (Simplified)

The NEC generally requires overcurrent protection to be sized to protect the conductor's ampacity. There are exceptions allowing for the
next higher standard overcurrent device rating in certain cases if the calculated value doesn't match a standard fuse/breaker size. However, there are limits to this "next size up" rule.4.

The Problem with an 800A Fuse



Grossly Oversized

An 800A fuse is significantly larger than the 620A ampacity of your parallel conductors. The fuse wouldn't trip until a current far exceeding the safe capacity of the conductors flows through them. This means the conductors could be seriously damaged (overheated, insulation melted, potential fire hazard) long before the fuse blows.

Violation of NEC

In almost all cases, using an 800A fuse on a circuit with conductors rated at 620A is a violation of the NEC. The exceptions for "next size up" usually only allow a small increase above the calculated ampacity, not such a massive jump.

Why the Misunderstanding Might Exist (Possible Scenarios)
Motor Starting Currents

Some motors draw very high current (inrush current) when starting. Fuses and circuit breakers have time-current characteristics, which allow them to withstand brief overloads (like motor starting) without tripping. However, even with motor loads, the overcurrent protection must still protect the conductors from sustained overloads.

However, this isn't enough to justify such a high value.
Equipment Ratings (Incorrect Assumption)

You
might have equipment downstream that's rated for 800A. However, the overcurrent protection is to protect the conductors leading to that equipment, not necessarily the equipment itself. The equipment should have its own internal overcurrent protection, or be protected by separate devices. You cannot upsize the conductor protection so high to protect only the load.

Voltage Drop Compensation (Incorrect)

Upsizing conductors is sometimes done to reduce voltage drop, but this does not justify using oversized overcurrent protection. The fuse/breaker must still protect the actual ampacity of the conductors installed.

Misunderstanding of "Next Size Up" Rule

The "next size up" rule is often misinterpreted. It's a narrow exception, not a general practice to arbitrarily upsize fuses.


Older Installations (Potentially Incorrect)

Older installations may not meet current NEC standards. Just because something has been done for a long time doesn't make it safe or compliant.

Conclusion


Using an 800A fuse for a set of parallel 500 kcmil aluminum conductors rated at 620A is extremely dangerous and almost certainly a violation of the NEC. The fuse would not provide adequate protection for the conductors. The correct fuse size should be at or below 620A, possibly slightly higher if the NEC allows for the "next size up" in specific circumstances (e.g., motor starting, but only to a reasonable extent), and it must be calculated carefully and documented. You should consult a qualified electrician or electrical engineer to determine the correct fuse size for your application and ensure code compliance.

Recommendation1. Consult an Electrician

Have a licensed electrician review your installation and determine the correct overcurrent protection.2.

Verify Conductor Ampacity

Double-check the ampacity of your conductors based on the specific installation conditions (temperature rating, conduit fill, etc.).3.

Understand the Load

Identify the actual load on the circuit and any specific requirements (e.g., motor starting characteristics).4.

Calculate and Document:
Perform the necessary calculations according to the NEC to determine the appropriate overcurrent protection. Document your calculations for future reference and inspection.Safety should always be the top priority. Don't risk damaging equipment, causing a fire, or endangering lives by using an incorrectly sized fuse. Flag for review