User: Grouch1980, Location: New York, NY
Asked on: Monday, November 11, 2024 at 3:49 pm EST
Answered on: Thursday, March 6, 2025 at 5:05 am EST
Question: I'm pretty sure the answer is no, this is not a tap, but would like feedback:There's an existing installation, with a #1 AWG feeder originating from a 3 pole, 100 amp breaker. The feeder goes to an apartment in a multi-family building. The feeder, inside the apartment, terminates in a splice box. In the splice box, 2 parallel sets of #4 AWG cables splice to the #1 AWG feeder, and go to the electrical panel. All conductors are copper.I do not believe these 2 parallel sets are considered tap conductors, since the total ampacity of the paralleled sets (170 amps, using the 75 deg C column) exceeds the breaker rating of 100 amps. Am I correct? The 10 foot or 25 foot tap rules do not apply.
You are absolutely correct. This is NOT a tap situation. Here's why: Tap Rules Require Ampacity Greater Than or Equal to Overcurrent Device
The fundamental principle of tap rules (like the 10-foot and 25-foot rules) is that the tap conductors must have an ampacity no less than the overcurrent device protecting the feeder they tap. In your scenario, the 100A breaker protects the #1 AWG feeder.
Ampacity of Parallel Conductors
You've correctly identified the ampacity of two #4 AWG conductors in parallel. Using the 75°C column (likely the appropriate temperature rating for most termination equipment), each #4 AWG conductor has an ampacity of 85 amps. Two in parallel gives you 170 amps.
The Problem
170 amps > 100 amps. The two sets of #4 AWG wires connected to the #1 AWG do not satisfy the overcurrent protection requirement to the 10 foot or 25 foot tap rules.
In Summary
Since the combined ampacity of the parallel #4 AWG conductors exceeds the rating of the 100A breaker protecting the #1 AWG feeder, this is not a tap according to the NEC. Instead, it is a case of properly sized conductors for the load.
Important Considerations and Potential Issues
Feeder Size
The only remaining potential issue, is the size of the #1 AWG wire. It must have an ampacity greater or equal to the load, and not less than the overcurrent protection. #1 AWG has an ampacity of 130 amps at 75 degrees, so it is not a code violation.
Workmanship
Ensuring that the splices in the splice box are properly made and rated for the conductor sizes is critical. Poor splices can lead to overheating and failure.
Neutral and Ground: Make sure that neutral and grounding conductors are properly sized and installed throughout the system, including at the splice box and the panel.In conclusion, your assessment is accurate. This is not a tap scenario because the combined ampacity of the downstream conductors exceeds the upstream overcurrent protection. Flag for review