User: electrofelon, Location: Cherry Valley NY, Seattle, WA
Asked on: Monday, November 11, 2024 at 10:01 pm EST
Answered on: Thursday, March 6, 2025 at 5:06 am EST
Question: See the attached drawing. They are showing the main electrical panel bonded. I am thinking that is a mistake yes?
Yes, you are correct. Based on standard electrical codes (like the NEC in the US), the drawing likely shows a mistake if the main panel is in a detached structure (like a shed or garage).Here's why: Main Panel (Service Entrance) Bonding
In the main electrical panel, which is typically the first panel after the meter at the service entrance of the house, the neutral conductor is bonded to the panel enclosure and the grounding electrode system. This establishes a single point where the neutral and ground are connected.
Subpanels (Detached Structure) Bonding
In a subpanel located in a detached structure, the neutral conductor MUST NOT be bonded to the panel enclosure. The neutral and ground conductors must be kept separate. The subpanel enclosure is connected to the grounding electrode system, and a separate equipment grounding conductor (EGC) runs back to the main panel to provide the ground fault current path. This is to prevent parallel neutral current and reduce the risk of electric shock.
Therefore, If the drawing is for the subpanel in a detached structure, the neutral should NOT be bonded to the panel enclosure.In summary: The drawing showing bonding in a detached structure's subpanel is likely incorrect and potentially dangerous. It could create a shock hazard and violate electrical codes. Always consult with a qualified electrician for your electrical work. They can properly assess the situation and ensure that the wiring meets all applicable codes and safety standards. Flag for review