Topic: Arc Flash PPE Category outside of Arc Flash Boundary

User: duck-dude, Location: USA

Asked on: Tuesday, November 12, 2024 at 2:23 pm EST
Answered on: Thursday, March 6, 2025 at 5:07 am EST

Question: From what I understand from NFPA 70E, only the parts of your body within the restricted approach boundary are required to be insulated from shock. Is this also true about working within the Arc Flash boundary?For example;Arc Flash boundary of 9 inchesWorking distance of 18 inchesCategory 1 hazardDo you need full-body AF protection, or just the appropriate gloves and FR shirt?

You're mixing concepts a bit. Let's break it down according to NFPA 70E and address your specific example.

Understanding the Boundaries and PPE Requirements



Restricted Approach Boundary

As you stated, the Restricted Approach Boundary is about
shock protection. If any part of your body crosses this boundary while working on energized equipment, you must have appropriate insulation (usually insulated gloves and sleeves, and possibly insulated tools). This is to prevent accidental contact with energized parts that could result in electric shock.

Arc Flash Boundary

The Arc Flash Boundary is about arc flash protection. This boundary is the distance at which a person could receive a second-degree burn (curable) if an arc flash occurred. If you're within the arc flash boundary, you are exposed to the possibility of an arc flash.

PPE Selection Based on Arc Flash

NFPA 70E doesn't just say "if you're within the Arc Flash Boundary, put on
something". It mandates that you perform an arc flash hazard analysis to determine the incident energy exposure level at the working distance. The result of this analysis determines the appropriate arc-rated PPE you need to wear.

Answering Your Specific Example

Let's analyze your scenario:


Arc Flash boundary of 9 inches
Working distance of 18 inches Category 1 hazard (This is incomplete. You need to know the incident energy (calories/cm^2) of the Category 1 Task)Here's where the important distinction comes in

Just because you are working outside the Arc Flash boundary doesn't mean you don't need any arc flash protection.

What the Standard Says
130.5(C) Arc Flash Risk Assessment

This Section requires that a risk assessment be performed to determine if an arc flash exists.


130.5(G) Arc Flash PPE

Employees shall wear arc flash PPE in accordance with the results of the arc flash risk assessment required by 130.5(C). Arc Flash PPE must cover all ignitable clothing and exposed skin.

130.7(C)(16) Clothing
Clothing worn when exposed to electrical hazards shall be appropriate for the work being done and shall comply with 130.7(C)(16).

Why is this important?1. Even though your working distance (18 inches) is beyond the arc flash boundary (9 inches) calculated to a second-degree burn, you are still inside the arc flash zone and still within an arcing fault.2. You are still exposed to fire. An arc flash will ignite anything flammable. You are still exposed to molten metal in the event of a flash.

Therefore, in your example, you may very well need
more than just gloves and a FR shirt. Here's why: Incident Energy

The actual incident energy at 18 inches could still be high enough to cause injuries beyond a second-degree burn at 9 inches, especially to exposed skin if an arc flash occurs. The farther you are away from the arc source, the lower the incident energy will be, this is true. However, you still have a chance of being injured.

Coverage

Even if the incident energy at 18 inches is low, NFPA 70E requires that all ignitable (non-FR) clothing and exposed skin be protected. A non-FR shirt could ignite if exposed to the arc flash, even if at a low energy level, potentially causing significant burns. A flash hood and eye protection may also be required depending on the level of arc flash.

Therefore, here's what you need to do


Determine the incident energy.
You need to calculate or obtain the calculated incident energy for the task.2. Select PPE

Based on that incident energy, you must select arc-rated PPE that provides adequate protection for the potential exposure. This
could mean a full arc flash suit. It could mean a more limited set of FR clothing, depending on the analysis results. At a minimum, you may only need proper FR clothing to ensure that you do not ignite your regular clothing.

In Summary

You need to perform an arc flash hazard assessment to determine what arc flash PPE is required, and cover all ignitable clothing and exposed skin.