Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Class 2 thermocouples

User: Isaiah, Location: Baton Rouge

Asked on: Wednesday, November 13, 2024 at 9:31 am EST
Answered on: Thursday, March 6, 2025 at 5:09 am EST

Question: In the 2020 NEC per 725.121 thermocouples are shown as class 2 circuitsDoes this mean thermocouples are a non shock hazard and therefore do not require the shield or (grounding conductor) to be bonded?

You're focusing on a specific aspect of the NEC and trying to draw a broad conclusion. Here's a breakdown:1. 725.121 and Class 2 Circuits

725.121 in the NEC does indeed address the characteristics of Class 2 and Class 3 circuits. These circuits are defined by having limited voltage and current. This limitation reduces the risk of fire and electric shock, but it does not eliminate them entirely.2.

Thermocouples as Class 2

The NEC allows some thermocouple circuits to be classified as Class 2, provided they meet the voltage and current limitations specified in 725.21 and 725.
41.3.


Non-Shock Hazard - Incorrect Assumption

Class 2 designation does

not
automatically mean a non-shock hazard. While the hazard is significantly reduced, it is not eliminated. Under fault conditions, or if the thermocouple becomes energized by another source, a shock hazard could still exist.4. Bonding/Grounding Conductor (Shield) and Purpose



Shielding

The shield (if present) in a thermocouple cable is primarily for
noise reduction, not necessarily safety grounding. It's designed to minimize electromagnetic interference (EMI) that can affect the accuracy of the thermocouple readings.

Grounding/Bonding

The purpose of grounding or bonding the shield is multi-fold. It's typically done to ensure that the shield provides an effective path for noise currents to return to the source, improving the signal quality. In some situations, it can contribute to safety by providing a low-impedance path for fault currents to return to the source, potentially tripping an overcurrent protective device.

Safety Ground vs. Signal Ground

It's crucial to distinguish between a safety ground (intended to protect against electrical shock) and a signal ground (intended for signal integrity). While they can sometimes be connected, their primary purposes are different. Typically in these low voltage DC applications you want to avoid creating ground loops which will adversely affect the performance of the devices.5.

Necessity of Bonding/Grounding - Depends on Application and Equipment



Manufacturer's Instructions



Always, always, always
follow the manufacturer's instructions for the thermocouple transmitter, any associated equipment, and the thermocouple itself. They will specify if the shield needs to be grounded/bonded and where to do so (e.g., at the transmitter end, at the sensor end, or both). Environment

In electrically noisy environments, grounding the shield is generally recommended to improve signal integrity.


Equipment Requirements

Some equipment may require a grounded shield for proper operation or to meet regulatory compliance.

Intrinsically Safe Systems

If the thermocouple is part of an intrinsically safe (IS) system, specific grounding requirements will apply as dictated by the IS design.

In summary

Class 2 status reduces, but does not eliminate, the shock hazard. The decision to bond/ground a thermocouple shield is not solely based on its Class 2 status.

The primary driver is signal integrity (noise reduction), with safety being a secondary consideration.
You MUST follow the manufacturer's instructions for grounding/bonding. Deviating from those instructions can lead to inaccurate readings, equipment malfunction, or even safety hazards. Consider the specific application, the electrical environment, and the requirements of all associated equipment.

Therefore, the statement that thermocouples, because they are class 2 circuits, do not require the shield or grounding conductor to be bonded is an incorrect generalization. You need to consider the specific application, manufacturer instructions, and environmental factors. If in doubt, consult with a qualified engineer or electrician experienced in instrumentation and control systems. Flag for review

Previous Question Next Question