Question: I have a 200A main panel in my house and want to put a 100A sub in pole barn. I have 2 spare 200A panels ML/MB. Am i ok to feed the 200A MB panel in pole barn from a 100A breaker in my house panel?Thank you for your response!
Yes, you are generally okay feeding a 200A main breaker panel in your pole barn with a 100A breaker in your house's main panel, provided your wiring is correctly sized and the 100A breaker protects the circuit. Here's why and some important considerations
Why it's generally acceptable:
Panel Rating vs. Load
The 200A rating of the subpanel in the pole barn is the maximum capacity the panel can handle, not necessarily what it will draw. You are putting a 100A limit on the supply to that panel. The subpanel acts like a "highway" that can handle a lot of traffic, but the size of the "pipe" (the 100A feeder) feeding the highway determines the maximum flow.
Overcurrent Protection
The 100A breaker in your main panel is designed to protect the wires running to the subpanel. If the load in the pole barn tries to draw more than 100A, the breaker will trip, preventing damage to the wiring.
Crucial Considerations
Wire Size
This is the most critical factor. You must use wire that is properly sized to carry 100A, and be rated for the wet location, and buried in the correct manner. Using undersized wire is a major fire hazard. Consult a wire ampacity chart (easily found online) and consider the length of the run. Voltage drop can be a significant issue over long distances. Copper wire would likely need to be at least #3 AWG, and Aluminum #1.2.
Grounding
Correct grounding is essential for safety. The subpanel must be properly grounded. You must run a separate grounding conductor (equipment grounding conductor - EGC) along with the hot and neutral wires. Do not bond the neutral and ground in the subpanel. The neutral and ground should only be bonded at the main panel. A four wire feed is required between main and subpanel.3.
Conduit/Burial
The wiring must be run in appropriate conduit (e.g., PVC, rigid metal) and buried to the required depth according to local codes. Direct burial cable needs to be rated for direct burial.4.
Disconnect
You will need a means of disconnecting all conductors at the pole barn. The main breaker in the 200A panel serves as this disconnect.5.
Load Calculation
You must be sure that your main panel has enough capacity to handle the additional 100A load you are adding. It's unlikely you'll actually draw a full 100A continuously in the pole barn, but you need to calculate potential loads.6.
Local Codes and Permits
This is essential. Before doing any electrical work, check with your local building department. You'll likely need a permit and an inspection. They can provide specific requirements for your area and ensure the work is done safely and correctly.7.
Professional Help
If you're not comfortable with electrical work or unsure about any of these steps, hire a qualified electrician. Electrical work can be dangerous, and mistakes can be costly or even life-threatening.
In summary:
Using a 200A panel as a subpanel fed by a 100A breaker is acceptable as long as the wiring is properly sized for 100A, the grounding is correct, and you comply with all local codes and regulations. Do not cut corners on safety. Consult an electrician if you have any doubts. Flag for review