Topic: Sub Panel

User: Jmoney69, Location: Detroit mi

Asked on: Wednesday, November 13, 2024 at 4:38 pm EST
Answered on: Thursday, March 6, 2025 at 5:10 am EST

Question: I have a 200A main panel in my house and want to put a 100A sub in pole barn. I have 2 spare 200A panels ML/MB. Am i ok to feed one of the 200A panels in pole barn from a 100A breaker in my house panel?

Yes, you can absolutely feed a 200A panel in your pole barn with a 100A breaker from your main house panel. Here's why and some important considerations: Panel Rating vs. Breaker Rating

The amperage rating of an electrical panel refers to the
maximum amount of current that the panel can handle. It's not the amount of current that will flow through it. The breaker you install determines the amount of current allowed to flow to the subpanel. A 200A panel is perfectly fine being fed by a 100A breaker. The panel itself is simply oversized, which is perfectly safe and can be beneficial if you plan to upgrade the amperage in the future.

Overcurrent Protection (Breaker)

The 100A breaker in your main house panel protects the wire running to the subpanel. This is crucial. If more than 100A of current tries to flow, the breaker will trip, preventing overheating and potential fire hazards in the wiring.

Wire Sizing

This is
absolutely critical. The wire you use to connect the 100A breaker in your main panel to the 200A subpanel in the pole barn must be rated for at least 100 amps. Using undersized wire is a major fire hazard. For copper wire, you'll likely need at least #3 AWG. Aluminum wire will require a larger gauge, such as #1 AWG or #1/0 AWG (check local code and conductor temperature ratings to confirm the correct size). This is not something to guess at. Consult the ampacity tables for the appropriate wire size based on material, insulation type, and installation method (e.g., direct burial, conduit).



Grounding and Bonding

This is extremely important for safety. You will need a 4-wire feed to the subpanel. This includes two hots, one neutral, and one ground.

Separated Neutral and Ground

In the subpanel (the panel in the pole barn), the neutral and ground must be kept separate. Do not bond the neutral bar to the panel enclosure. The neutral bar should float, meaning it is isolated from the panel enclosure.

Grounding Electrode System

The subpanel in the pole barn needs its own grounding electrode system. This typically consists of one or more ground rods driven into the earth near the pole barn. Connect the ground wire from your 4-wire feed to the grounding electrode system in the pole barn.


Conduit/Burial

Consider whether the wire will be run underground (direct burial or in conduit) or overhead. If underground, use appropriate direct-burial rated cable or run individual conductors in approved conduit. Follow local codes for burial depth. Overhead installations also have specific requirements for height and clearances.

Permits and Inspections

Very important. Almost all electrical work requires a permit and inspection by your local building department. This is for your safety and to ensure the work is done to code. Contact your local permitting office before starting any work.

Load Calculation

While you're using a 100A breaker, it's still a good idea to calculate the expected load in the pole barn. This helps you ensure the 100A service is adequate for your needs and helps plan the distribution within the subpanel.

Main Breaker in Subpanel

Because you're feeding a 200A panel with a 100A breaker, you do not need to install a main breaker in your subpanel. The 100A breaker in the main panel protects the wire from the main panel to the subpanel.

Disclaimer and Recommendation

I am an AI chatbot and cannot provide legally binding electrical advice. Electrical work can be dangerous and should only be performed by a qualified, licensed electrician. This information is for educational purposes only.

You MUST consult with a licensed electrician to determine the specific requirements for your installation, ensure compliance with local codes, and perform the work safely.
* They will be able to assess your specific situation, perform load calculations, select the correct materials, and ensure the installation is safe and code-compliant. Improper electrical work can result in fire, injury, or death. Flag for review