Question: I have 208V single phase 4160 kw tankless instant hot water heater. See below link. Should the breaker be sized 20A, 25A or 30A?https://www.zoro.com/chronomite-208vac-20-amps-both-electric-tankless-water-heater-sr-20l208-htr-i/i/G3709036/?utm_source=google&utm_medium=surfaces&utm_campaign=shopping+feed&utm_content=free+google+shopping+clicks&campaignid=21413729702&productid=G3709036&v=&gad_source=1&gbraid=0AAAAADw3hZcjYUExoogG_i7kJgwjTb_kw#specifications
Okay, let's break down how to properly size the breaker for your Chronomite SR-20L208 tankless water heater.
Understanding the Information 208V Single Phase
This is your voltage.
4.16 kW
This is the power consumption of the water heater (kilowatts).
20 Amps
This is the unit draw.
Calculations1. Convert kW to Watts
4.16 kW 1000 W/kW = 4160 Watts2.
Calculate Current (Amps)
Amps (I) = Watts (P) / Volts (V) I = 4160 W / 208 V I = 20 Amps3.
Apply 125% Rule (Continuous Load)
Electrical code requires that you size the breaker and wiring for 125% of the continuous load. A water heater is typically considered a continuous load. Required Ampacity = 20 Amps 1.25 Required Ampacity = 25 Amps
Sizing the Breaker
Based on the calculation above, you need a breaker that can handle at least 25 Amps. Therefore, you should use a 25A breaker.Important Considerations Wire Gauge
The wire size must be appropriate for the breaker size. Consult the National Electrical Code (NEC) or a qualified electrician to determine the correct wire gauge for a 25A circuit at 208V. Using too small a wire is a fire hazard. #10 AWG Copper would be appropriate.
Local Codes
Always check with your local building codes and electrical codes to ensure you comply with all regulations. Local codes may be stricter than the NEC.*
Qualified Electrician
This information is for guidance only.
You should always consult with a qualified and licensed electrician for any electrical work. They can properly assess your specific situation, perform the calculations, and ensure the installation is safe and code-compliant. Electrical work can be dangerous, and mistakes can lead to fires or electrocution.
In summary, based on the specifications you provided, a 25A breaker is the correct size. But, verify with a licensed electrician before proceeding with any installation. Flag for review