Topic: Metallic water piping through out house (plastic supply line)

User: Dsg319, Location: West Virginia

Asked on: Thursday, November 14, 2024 at 7:33 am EST
Answered on: Thursday, March 6, 2025 at 5:11 am EST

Question: In the situation of a dwelling supplied with a plastic water line but the house is plumbed in using copper I know it doesn’t have to be bonded for use of a GESBut still needs to be bonded as likely to become energized? The EGC supplying the hot water tank circuit would achieve this.Or is there more to it and how to size it?Also must there be a jumper between hot/cold lines or is there anything internal to achieve this.Appreciate any answer also if anyone has the appropriate code section to post.Thanks in advance.

Okay, let's break down the bonding requirements for metal water piping systems in a dwelling, especially when you have a mix of plastic and copper.

Understanding the Code Requirements

The key to understanding this lies in why we bond metal water piping. It's

not
primarily for grounding electrical equipment in the house (although it can indirectly contribute). It's mainly about addressing the potential for the piping itself to become energized due to faults elsewhere in the system. NEC 250.104(A) Bonding of Metal Water Piping

"(A) General. Metal water piping system(s) installed in or attached to a building or structure shall be bonded to any of the following:(1) Equipment grounding conductor for the circuit that is likely to energize the piping system.(2) Grounded conductor, where of sufficient size.(3) Grounding electrode conductor, where of sufficient size.(4) One or more of the grounding electrodes used to comply with 250.50."

Your Specific Scenario: Plastic Service, Copper Interior Piping
1. No Requirement to Connect to the Grounding Electrode System (GES)

You're correct. If the water service entrance is plastic, and the piping doesn't extend more than 5' into the building, 250.104(A) doesn't necessarily require you to connect the copper piping to the GES. The absence of a continuous metal path to the earth negates the requirement to ground the copper to a ground rod/plate, etc.
2.


Bonding for Potential Energizing Still Required

This is the crucial point.

The likelihood of the copper piping becoming energized still exists.
This is because: Faults in electrical equipment could energize the piping. A nail through a wire or deterioration of insulation can cause a short. Loose connections or even static electricity build up.Therefore, bonding is still necessary per NEC 250.104(A).3. How is it Bonded? Per 250.104(A)(1), this bonding is typically accomplished through the equipment grounding conductor (EGC) of a circuit likely to energize the piping system. Hot Water Heater Circuit EGC

You're correct that the EGC serving the hot water heater is a prime candidate. The EGC that grounds the water heater is connected to the breaker box and therefore to ground. This is a code compliant way to fulfill the bonding requirement.


Other Circuits

Any other circuit that supplies equipment in close proximity to the copper piping and likely to energize it can also serve as a bonding means. Example, a well pump that supplies the house with water that contains a metal pipe between the pump and the house.

Metal-to-Metal Contact

Incidental contact between the copper water pipes and other grounded metal parts of the building
might provide some bonding, but

this should NOT be relied upon
as the sole means. Rely on the EGC connection.4. Sizing the Bonding Jumper (if separate is used)

If you choose to run a
separate bonding jumper to the piping (instead of relying solely on the hot water heater EGC), the size of the bonding jumper is determined by Table 250.102(C)(1), based on the size of the circuit conductors that are likely to energize the piping. However, in a dwelling, it typically does NOT need to be larger than a #6 AWG copper or #4 AWG aluminum. (See 250.102(C)(1).)

Important

You don't need a separate jumper if the EGC for the hot water heater circuit, for example, is properly sized and connected to the piping. The EGC should originate in the main panel and run with the circuit conductors.5.

Jumper Between Hot and Cold Water Pipes?
Yes, Often Required: NEC 250.104(A)(2) covers this. If the water heater piping system is discontinuous for any reason (such as a dielectric union, plastic fitting or plastic water filter), you must install a bonding jumper to ensure continuity of the water piping system as an effective ground-fault current path. This would bond the hot and cold water pipes, even where plastic is involved. Internal Continuity?

While some water heaters
might have internal paths between the inlet and outlet, you

cannot rely
on this as a substitute for an external bonding jumper if there's a break in the piping system's continuity.

In Summary

1. Plastic water service
doesn't require bonding to the grounding electrode system (GES).2. However, because the interior copper piping can still become energized, it must be bonded.3. This bonding is typically achieved through the EGC of a circuit likely to energize the piping, such as the hot water heater circuit. Verify the EGC of the water heater circuit is properly connected to the metal piping.
4. If there's a break in the metal water piping continuity (like a plastic section), a bonding jumper across the break is required to maintain continuity of the grounding path (250.104(A)(2)).
5. Size the bonding jumper according to Table 250.102(C)(1), but in a dwelling, it usually doesn't need to be larger than #6 AWG copper or #4 AWG aluminum.
6. Ensure all connections are made securely with appropriate fittings (listed for grounding/bonding).


Important Considerations



Local Amendments

Always check with your local electrical inspector for any local amendments to the NEC. Some jurisdictions may have stricter requirements.*

Proper Installation

The key is making sure the connections are tight, corrosion-resistant, and made with fittings listed for grounding and bonding.

Example:


Let's say you have a 20-amp circuit feeding a hot water heater.1. The EGC for that 20-amp circuit will likely be #12 AWG copper (check Table 250.122). This is based on the overcurrent protection device.
2. You install a bonding jumper from the #12 EGC coming from the breaker box at the water heater to the copper cold water pipe near the water heater.3. You verify there is a bonding jumper across any plastic fittings on the hot or cold water pipesBy following these steps, you ensure your copper water piping is properly bonded, minimizing the risk of electrical shock and creating a safe electrical system. Flag for review