Topic: Existing Grounding electrode system

User: alixenos, Location: Florida

Asked on: Thursday, November 14, 2024 at 1:58 pm EST
Answered on: Thursday, March 6, 2025 at 5:13 am EST

Question: Hi,an electrical room that has an existing 1200A main switchboard is updated to have another 1200 A main switchboard being served from a new service.for the 2nd service, Do we need to provide a new grounding electrode system? what about the existing one? where in the code I can find answers to those questions?Thank you.

You're asking about a critical aspect of electrical safety related to grounding electrode systems when adding a second service to an existing building. Here's a breakdown of the requirements based on the NEC (National Electrical Code) and how to find the answers within the code book

Do You Need a New Grounding Electrode System for the Second Service?
Yes, in most cases you WILL need a separate grounding electrode system for the new service. The NEC requires each service to have its own grounding electrode system.

What About the Existing Grounding Electrode System?
The existing grounding electrode system MUST be bonded to the new grounding electrode system. This ensures that both systems are at the same electrical potential and prevents dangerous voltage differences.

Where to Find the Answers in the NEC (Specifically, the 2020 NEC)

The primary sections of the NEC dealing with this are in

Article 250: Grounding and Bonding.
Here's a more detailed breakdown: NEC 250.24(A)(1) (Grounding Electrode for Alternating-Current Systems): This section mandates that a grounding electrode system be connected to the grounded conductor of each service. It is not permissible to simply extend the existing grounding electrode system to the new service equipment. NEC 250.50 (Grounding Electrode System): This section outlines what constitutes a grounding electrode system. It must include one or more of the following, bonded together as specified in 250.53. 250.52(A)(1) Metal Underground Water Pipe

If present and meeting the requirements (electrically continuous, in direct contact with the earth for 10 feet or more), it's generally
required to be used as part of the grounding electrode system.

250.52(A)(2) Metal In-ground Support Structure(s)

Under certain conditions, metal in-ground support structures can be used.

250.52(A)(3) Ground Ring

A ground ring encircling the building.


250.52(A)(4) Rod and Pipe Electrodes

Ground rods or pipes driven into the earth.

250.52(A)(5) Plate Electrodes

Metal plates buried in the earth.


250.52(A)(6) Other Listed Electrodes

Electrodes specifically listed for grounding purposes.

250.52(A)(7) Concrete-Encased Electrode

A "Ufer ground" – a rebar electrode encased in concrete at the footing or foundation.


NEC 250.53 (Installation of Grounding Electrodes)
: Details how to install the various types of electrodes, including depth, spacing, and bonding requirements. NEC 250.64(F) (Grounding Electrode Conductor Connection to Electrodes): This section governs how the grounding electrode conductor (the wire connecting the service equipment to the grounding electrodes) is connected to the electrodes. NEC 250.58 (Common Grounding Electrode): This is the KEY section that addresses multiple services. It states that where multiple services are installed in a building or structure, each service shall have its own grounding electrode system as specified in 250.50. Additionally, all grounding electrode systems shall be bonded together, as specified in 250.64(A). This means you bond the two grounding electrode systems to each other using a grounding electrode conductor sized per 250.
66.

In Summary1. Separate Grounding Electrode Systems

Install a complete grounding electrode system for the new 1200A service, complying with 250.50 and 250.
52.2.


Bonding

Bond the new grounding electrode system to the existing grounding electrode system using a grounding electrode conductor sized according to 250.66. The bonding connection should be made in a manner that is accessible.
3.


Documentation

Keep records of the grounding electrode system for each service, including the types of electrodes used, their locations, and the size of the grounding electrode conductors.

Important Considerations



Local Amendments

Always check for local amendments to the NEC. Your local jurisdiction may have more stringent requirements.


Engineering Judgment

The design of the grounding electrode system should be based on sound engineering judgment, considering soil conditions, fault current levels, and other relevant factors.

Qualified Personnel

This work MUST be performed by qualified electrical personnel who are familiar with the NEC and local codes. Improper grounding can be extremely dangerous.


Authority Having Jurisdiction (AHJ)

Consult with your local electrical inspector (the AHJ) before starting the work to ensure compliance with all applicable codes and regulations. Their interpretation is what matters in the end.

Example Scenario

Let's say the original grounding electrode system consisted of a metal water pipe and two ground rods. The new service also has a metal water pipe available.1. Install the new service's grounding electrode system, using the available metal water pipe as one electrode. You MUST supplement the water pipe electrode with at least one additional electrode type listed in 250.52(A)(2) through (A)(8). (Usually ground rod(s)).
2. Run a grounding electrode conductor (sized per 250.66) from the neutral bus of the new service equipment to a point on the existing grounding electrode system where it is accessible (e.g., a busbar or a suitable lug on the existing main grounding electrode conductor). This bonds the two grounding electrode systems together.By following these guidelines, you will help ensure the safety and reliability of the electrical system. Always consult the current edition of the NEC and your local codes for the most up-to-date requirements.

Disclaimer:
This information is for educational purposes only. Always consult with a qualified and licensed electrical engineer or electrician for any electrical work. Flag for review