Question: Is it NEC code to have circuits within pull boxes tagged? It is always in the spec but curious whether code. Thank you

The NEC doesn't explicitly mandate tagging circuits inside pull boxes. However, it does indirectly require information that often leads to tagging or other identification methods. Here's the breakdown: NEC 314.29 (Accessibility)

"All boxes and conduit bodies shall be installed so that the wiring contained in them can be rendered accessible without removing any part of the building or, in underground installations, without excavating sidewalks, paving, earth, or other substance that is to be used to establish the finished grade."
This requires that the wiring be accessible. A jumbled mess of unlabeled conductors makes accessibility and troubleshooting incredibly difficult, and therefore is considered by most inspectors a violation.

NEC 314.43 (Markings)

Requires markings on boxes specifically for emergency systems, legally required standby systems, and critical operations power systems (COPS). This doesn't cover general circuit identification.

NEC 110.22 (Identification of Disconnecting Means)

While this specifically applies to disconnecting means, the
spirit of the code is to have clear identification of circuits. If a pull box connects to a panel, then the disconnect for that branch would need to be labelled at the panel, and it would be best to note that circuit designation in the pullbox.

NEC 408.4 (Circuit Directory or Circuit Identification)

Applies to panelboards and requires a clear circuit directory. While this isn't directly about pull boxes, it highlights the importance of knowing what each circuit is for. The information in the panelboard schedule needs to be traceable back to the loads.

Why Tagging is Good Practice and Often Required by Specs



Troubleshooting

Without identification, tracing circuits through a pull box is incredibly time-consuming and prone to errors.


Safety

Knowing the voltage and function of conductors before working on them is paramount for safety.

Maintenance

Makes future maintenance and modifications much easier.


Documentation

Helps maintain accurate "as-built" drawings and documentation.

Compliance

While
not explicitly required by the NEC for all circuits, most inspectors consider unmarked wires in a junction box a violation of 314.29, as it makes accessibility extremely difficult.

In summary

While the NEC doesn't have a blanket requirement for
explicitly tagging circuits* inside pull boxes (except for emergency systems, legally required standby systems, and critical operations power systems (COPS)), the accessibility requirements and the spirit of the code strongly encourage it. Moreover, most specifications will include this as a requirement because it's considered industry best practice. Therefore,

follow the specification
. If the specification calls for circuit identification within pull boxes, you must comply.

Therefore, it is a safe assumption that the practice is followed due to local and customer policy, which is supported by the NEC code in spirit and often in practice, and it is likely going to be required. Flag for review