User: chuggb, Location: Las Vegas
Asked on: Thursday, November 14, 2024 at 6:27 pm EST
Answered on: Thursday, March 6, 2025 at 5:14 am EST
Question: I have a project (in bid) that has four (4) buildings and a single 800A service. The main distribution panel is located in the exterior of building D.Building A has two (2) panels from MDB each 200A. This building is CMU and steel support with a 1"C water pipe (copper).Building B has one (1) panel from MDB also 200A. This building is CMU and steel support with a 1-1/4"C water pipe (copper).Building C has one (1) panel from MDB at 60A. Building C is CMU and steel support.Building D has (1) panel from MDB with 100A. This building is CMU with steel decking.When grounding separate buildings from a single service, 250.32 (A) states, "...shall have a grounding electrode or grounding electrode system installed in accordance with Part III of Article 250." Part III of Article 250 states, "All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system."Please correct me if I'm wrong but, this means I would have my grounding electrode (from the same conduit as my current carrying conductors) and this electrode would be connected to each building's; metal underground water pipe, metal in-ground support structure, and concrete-encased electrode.
You're on the right track, but let's clarify and refine your understanding of 250.32(A) and Part III of Article 250.
Here's a breakdown and corrections
You are correct that 250.32(A) requires each building to have a grounding electrode or system when supplied by a feeder or branch circuit. This applies to your scenario because buildings A, B, and C are considered separate structures supplied by feeders from the main distribution panel (MDB) at building D. Correct Each building must have a grounding electrode system in accordance with Part III of Article 250. This does not apply to building D because the service disconnecting means is located within the building. Not quite correct in application for each building The key is to use the electrodes that are present at each building. You need to evaluate each building individually. If a specific electrode is not present at a building, you don't need to add one just for the sake of having all of them.
Applying the Code to Your Specific Buildings
Here's how you should think about grounding for each building:
Building A
Required
A grounding electrode system.
Assess what is present
Metal Underground Water Pipe (Yes)
You have a 1" copper water pipe. This must be used as a grounding electrode if it meets the requirements of 250.52(A)(1) (10 feet or more in direct contact with the earth). Supplemented by an additional electrode.
Metal In-ground Support Structure (Potentially)
You mentioned "steel support". This qualifies as a grounding electrode only if it meets the requirements of 250.52(A)(2). Contact with earth is required and must be at least 10ft.
Concrete-Encased Electrode (Potentially)
Is there a concrete-encased electrode, commonly called a "Ufer ground" (250.52(A)(3)), in the building foundation or footings? Usually, it is a length of steel rebar encapsulated within the concrete footing.
Connect
Bond together all of the electrodes that are present using a bonding jumper that is sized in accordance with Table 250.66.
Building B
Required
A grounding electrode system.
Assess what is present
Metal Underground Water Pipe (Yes)
You have a 1-1/4" copper water pipe. This must be used as a grounding electrode if it meets the requirements of 250.52(A)(1) (10 feet or more in direct contact with the earth). Supplemented by an additional electrode.
Metal In-ground Support Structure (Potentially)
You mentioned "steel support". This qualifies as a grounding electrode only if it meets the requirements of 250.52(A)(2). Contact with earth is required and must be at least 10ft.
Concrete-Encased Electrode (Potentially)
Is there a concrete-encased electrode, commonly called a "Ufer ground" (250.52(A)(3)), in the building foundation or footings?
Connect
Bond together all of the electrodes that are present using a bonding jumper that is sized in accordance with Table 250.66.
Building C
Required
A grounding electrode system.
Assess what is present
Metal Underground Water Pipe (Likely No)
You don't mention a water pipe, so assume not.
Metal In-ground Support Structure (Potentially)
You mentioned "steel support". This qualifies as a grounding electrode only if it meets the requirements of 250.52(A)(2). Contact with earth is required and must be at least 10ft.
Concrete-Encased Electrode (Potentially)
Is there a concrete-encased electrode, commonly called a "Ufer ground" (250.52(A)(3)), in the building foundation or footings?
If none of those exist, you'll need to install at least one of the grounding electrodes specified in 250.52(A)(4) through (A)(7) – rod, pipe, or plate electrode being the most common choice. Connect
Bond together all of the electrodes that are present using a bonding jumper that is sized in accordance with Table 250.66.
Building D
Not Required
A grounding electrode system.
Reason
The main distribution panel that supplies the other buildings, and contains the service disconnecting means, is located within building D.
Important Considerations
Sizing the Grounding Electrode Conductor (GEC)
The GEC that runs with your feeder conductors to each building needs to be sized according to 250.66, based on the size of the feeder conductors. This GEC will connect to the grounding electrode system at each building.
Grounding Electrode System Bonding Jumper
When you have multiple electrodes at a building (e.g., water pipe and rebar), you need to bond them together to form the grounding electrode system. The bonding jumpers need to be sized according to 250.66. Important: you cannot use 250.66 to size a bonding jumper that is used to connect the grounding electrode conductor.
Supplemental Electrode
It's crucial to understand that 250.53(D)(2) requires that the ground rod, pipe, and plate electrodes are always supplemented by an additional electrode as described in 250.52(A)(1) through (A)(7). If the only electrode you have at a building is a ground rod, you MUST add another electrode from the list.
Water Pipe Electrode
If using a metal water pipe as a grounding electrode, it must be supplemented by an additional electrode as described in 250.52(A)(1) through (A)(7). The supplemental electrode is sized in accordance with Table 250.66 based on the size of the Grounding Electrode Conductor (GEC). The point where the GEC lands on the water pipe must be within 5 feet of the entrance to the building, and it must be electrically continuous. This is to prevent theft of the pipe for scrap metal.
Continuity
Ensure the metal water pipe is electrically continuous. If there are non-conductive sections (like PVC couplings), you'll need to bond around them with a jumper.
Local Codes
Always check for any local amendments to the NEC that may affect grounding requirements.
In summary, your approach is generally correct, but the key is to precisely identify what grounding electrodes are present at each building and ensure you bond them together properly. Don't add electrodes unnecessarily if you already have compliant ones present. Pay close attention to proper sizing of conductors and bonding jumpers based on the relevant tables in the NEC. Flag for review