Question: What is the reasoning behind having to have a seal in raceways 2” or larger (but not smaller raceways) entering an explosion proof junction box containing no arcing/sparking devices.

The requirement for seals in raceways 2" or larger entering explosion-proof enclosures, even when those enclosures contain no arcing or sparking devices, is primarily based on the principle of pressure piling or pressure piling effect. Here's a breakdown of the reasoning: Preventing Explosion Propagation

Explosion-proof enclosures are designed to contain an explosion within the enclosure, preventing it from propagating to the surrounding hazardous atmosphere.


The Role of Seals

Seals are placed in raceways to limit the passage of gases, vapors, or flames from one area to another. They help maintain the integrity of the explosion-proof system.

Pressure Piling Explained

Imagine an explosion occurring in one part of a raceway system connected to an explosion-proof enclosure. The expanding gases and flame front travel through the raceway. If the raceway is large enough (2" or more), the expanding gases can build up significant pressure in front of the flame front. This is "pressure piling." When this high-pressure mixture reaches the explosion-proof enclosure, it can create a much more severe explosion than the enclosure was originally designed to contain. The increased pressure exceeds the enclosure's design limits. Even without an ignition source inside the enclosure, the sudden introduction of high-pressure, flammable gas and vapor can cause damage or failure of the enclosure.

Why 2" and Larger Raceways

The 2" threshold is based on empirical data and testing. Raceways of this size (or larger) have been shown to be capable of supporting significant pressure piling effects. Smaller raceways restrict gas flow to the point where pressure piling is less of a concern.

No Arcing/Sparking Device Doesn't Mean Safe

The absence of an ignition source
inside the explosion-proof enclosure doesn't eliminate the risk. The high-pressure, flammable mixture entering the enclosure from the raceway can still cause damage or even ignite outside the enclosure if the pressure exceeds the enclosure's design limits and causes it to fail.

Code Requirements (NEC)
The National Electrical Code (NEC) in the United States and similar codes in other countries mandate the use of seals to prevent pressure piling and maintain the integrity of explosion-proof systems. The specific requirements are outlined in articles dealing with hazardous locations.

In summary, the seal serves as a barrier to restrict the build-up of pressure caused by expanding gases in larger raceways. Without the seal, this pressure can exceed the design limits of the explosion-proof enclosure, potentially leading to a hazardous situation even when there is no inherent ignition source within the enclosure itself.

It is important to note that the specific requirements for seals in hazardous locations can be complex and depend on the specific classification of the hazardous area, the equipment being installed, and the applicable electrical codes. Always consult the relevant codes and standards and seek the advice of a qualified professional when designing and installing electrical systems in hazardous locations. Flag for review