Question: In a multi-unit dwellin of four stories, romex has been used for branch circuit wiring, SE cable encased in RMC was used for the service and emt runs through return air plenums extends outside to feed outside lights. According to NYC which of the following is true?a. EMT not allowed in plenum ceilingsb. NM allowed in residence over three storiesc. SE in RMCd. Emt allowed outside when treated againstcorrosion with an approved means.
Let's break down each statement according to NYC Electrical Code (which is based on the NEC with NYC amendments): a. EMT not allowed in plenum ceilings This is incorrect. EMT is generally allowed in plenum ceilings in NYC, as long as it meets the requirements of 300.22(C) and other applicable sections of the NYC Electrical Code. The key is that it needs to be suitable for the environmental conditions (e.g., plenum-rated if specifically required by the plenum's listing). b. NM allowed in residence over three stories This is incorrect in NYC. NYC Electrical Code generally prohibits NM cable (Romex) in buildings exceeding three stories. c. SE in RMC This is likely correct as the general rule is to protect service conductors from physical damage. d. Emt allowed outside when treated againstcorrosion with an approved means. This is correct as the NYC electrical code allows for EMT outside but generally requires it to be suitably protected against corrosion, especially in harsh environments.