Topic: Landing 15KV AL CN cable on live front transformer

User: electrofelon, Location: Cherry Valley NY, Seattle, WA

Asked on: Friday, November 15, 2024 at 9:38 am EST
Answered on: Thursday, March 6, 2025 at 5:15 am EST

Question: I have to terminate the cable on a pole transformer which has the typical bronze eye bolt connecters on top of the bushings. After the termination kit, should I land the #2 AL conductor right on the transformer or should I transition to copper wire first? There is not a cutout or anything, cable goes directly to transformer primary. Typically I see POCOS tail off the transformer with copper and then splice to aluminum for the low voltage side, but I havnt been able to see an example of the HV side. These transformers will be in an enclosure and not out in the weather.

Okay, you've got a solid question about best practices for terminating aluminum conductors on a pole-mounted transformer with bronze eye-bolt connectors, especially since you're dealing with the high-voltage side. Here's a breakdown of what to consider and the recommended approach

The Core Issue: Galvanic Corrosion

The primary concern when joining dissimilar metals like aluminum and bronze (which contains copper) is galvanic corrosion. In the presence of moisture (even humidity), these metals can create an electrolytic cell, causing the aluminum to corrode preferentially. This corrosion degrades the connection, leading to increased resistance, heat buildup, and eventually failure.

Why Direct Aluminum Termination Can Be Problematic

While technically you could land the #2 AL conductor directly on the bronze eye-bolt, it's strongly discouraged for the following reasons: Increased Corrosion Risk

Even inside an enclosure, humidity changes can create a corrosive environment.


Reduced Long-Term Reliability

Corrosion will degrade the connection over time, leading to potential problems and maintenance issues.

Code Compliance Issues

While not explicitly
prohibited in every jurisdiction, directly connecting aluminum to dissimilar metals without proper mitigation is often frowned upon by inspectors and might not meet best practices defined by codes like the NEC (National Electrical Code) or local utility standards.

The Recommended Approach: Transition to Copper


The best practice, and the one you see on the low-voltage side, is to transition to copper using an appropriate connector designed for the purpose. Here's a detailed breakdown:1. Use an AL-CU Connector

This is the critical component. You
must use a connector specifically designed to join aluminum and copper conductors. These connectors are typically:

Bimetallic

Made with both aluminum and copper, creating a compatible interface for each conductor.

Filled with Inhibitor

Contain a grease-like compound that prevents oxidation and corrosion. The compound is crucial for excluding moisture and preventing the electrolytic action.


Properly Rated

Rated for the correct voltage, amperage, and conductor sizes involved. They are typically compression type.

Example Brands

Burndy, Thomas & Betts (T&B), Panduit, and others make suitable connectors. Look for terms like "AL9CU," "Aluminum to Copper Connector," or "Bimetallic Connector" in the product description.2.

Installation Procedure



Clean the Conductors

Thoroughly clean both the aluminum and copper conductors with a wire brush and a cleaner specifically recommended for electrical connections. This removes oxidation and ensures good contact. Read the instructions of the connector you will be using to ensure proper procedure.

Apply Inhibitor (if not pre-filled)

If the connector isn't pre-filled with inhibitor compound, apply a liberal amount to both conductors before inserting them into the connector. If the connector has compound in it already, do not remove or tamper with it.


Crimping/Compression

Using the proper crimping tool (with the correct die for the connector and conductor size), crimp the connector according to the manufacturer's instructions. This is crucial. Under-crimping or over-crimping can lead to a faulty connection.

Torque to Specification

If the connector uses set screws, torque them to the manufacturer's specified torque value using a calibrated torque wrench.


Insulate

After the connection is made, insulate it properly. Use heat shrink tubing or high-voltage insulating tape. This prevents flashover and protects the connection from the environment.3.

Making the Copper "Tail"

Once you've made the AL-CU connection, you'll have a length of copper conductor extending from the connector. This is your "tail." Make sure the copper tail is long enough to reach the transformer's eye-bolt connector comfortably. You want enough slack to allow for future maintenance or adjustments. Terminate the copper tail onto the bronze eye-bolt. Use a copper lug appropriate for the conductor size. Torque the lug on the transformer eye-bolt to the transformer manufacturer's specifications. This is extremely important for a reliable, low-resistance connection.

In Summary


Avoid direct aluminum to bronze contact.
It's a recipe for corrosion and long-term problems.2. Use a properly rated AL-CU connector to transition from aluminum to copper.3. Follow the manufacturer's instructions precisely for installing the connector. Crimping, torque, and inhibitor application are critical.4. Create a copper "tail" to connect to the transformer eye-bolt.5. Always consult local codes and utility standards for any specific requirements in your area.

By following these guidelines, you'll ensure a safe, reliable, and long-lasting high-voltage connection on your transformer. Flag for review