Question: I have a project where I need to see what was required at the time of installation, which was 1968-1970.I down loaded the 1968 code book that was posted ( BIG THANX ), but the questions I wonder most about was pvc conduits feeding area lights that have no grounds,Was a ground wire required in pvc conduits in 1968 ?Any help or links to this research would be appreciated...Thanx, dhsvcs
Okay, let's break down the requirements for grounding conductors in PVC conduit systems from 1968 to 1970, focusing on outdoor area lighting and the requirements of the 1968 NEC.
Key Considerations
1968 National Electrical Code (NEC)
This is your primary reference.
Grounding vs. Bonding
It's important to understand the distinction. Grounding connects to the earth. Bonding connects conductive parts together to create a low-impedance path for fault current. In the context of area lighting, we're often concerned with both, but especially bonding.
Equipment Grounding Conductor (EGC)
This is the conductor that provides a low-impedance path back to the source for fault current to facilitate the operation of the overcurrent device (circuit breaker or fuse) protecting the circuit.
PVC Conduit
PVC is non-conductive. Therefore, it cannot serve as the equipment grounding conductor.
Area Lighting
Outdoor installations introduce additional considerations related to moisture and potential for ground faults.
1968 NEC Provisions Relevant to Your Question
The 1968 NEC addressed grounding extensively. While I don't have the text in front of me to quote precisely, here are the key concepts:
General Requirement for Equipment Grounding
The NEC required grounding of electrical equipment. This was not a new concept in 1968.
Grounding Methods
The NEC specified acceptable methods for grounding. These included:
Metal Conduit (Rigid or EMT)
The metal conduit could serve as the equipment grounding conductor, provided the connections were properly made and maintained.
A Separate Equipment Grounding Conductor (EGC)
This was required when using non-metallic conduit like PVC.
Specific Requirements for Non-Metallic Conduit (PVC)
An Equipment Grounding Conductor WAS Required
The 1968 NEC required that an equipment grounding conductor (EGC) be installed within the PVC conduit to ground the metal parts of the lighting fixture(s). PVC, being non-conductive, cannot provide a grounding path.
Size of the EGC
The size of the EGC was specified based on the overcurrent protection (breaker or fuse) protecting the circuit. The NEC had tables specifying the minimum size of the EGC.
Area Lighting and Outdoor Locations
Moisture
Outdoor locations were recognized as being damp or wet, increasing the risk of ground faults. This made proper grounding even more critical.
Exposed Metal Parts
Any exposed metal parts of the lighting fixture(s) that could become energized were required to be grounded.
Therefore, in 1968-1970, an equipment grounding conductor (EGC) WAS required to be installed within PVC conduit feeding area lights that have metal parts. The purpose was to provide a low-impedance path for fault current to return to the source and trip the overcurrent protective device.
Why is this important? Safety
Without a properly installed EGC, a fault could energize the metal parts of the lighting fixture, creating a shock hazard.
Code Compliance
The installation would be in violation of the NEC in force at the time.
Research Tips
Examine the 1968 NEC
Specifically, look for articles on: Grounding (Article 250 or similar – check the table of contents). Wiring Methods (PVC Conduit, etc.). Equipment Grounding Conductors.* Wiring in Damp and Wet Locations.
Disclaimer: I am an AI Chatbot. This information is for guidance only. Consult with a qualified electrical inspector or engineer to verify specific requirements for your project and to ensure compliance with all applicable codes and regulations. Flag for review