Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 1968 grounding conductors

User: dhsvcs, Location: miami

Asked on: Friday, November 15, 2024 at 12:18 pm EST
Answered on: Thursday, March 6, 2025 at 5:16 am EST

Question: I have a project where I need to see what was required at the time of installation, which was 1968-1970.I down loaded the 1968 code book that was posted ( BIG THANX ), but the questions I wonder most about was pvc conduits feeding area lights that have no grounds,Was a ground wire required in pvc conduits in 1968 ?Any help or links to this research would be appreciated...Thanx, dhsvcs

Okay, let's break down the requirements for grounding conductors in PVC conduit systems from 1968 to 1970, focusing on outdoor area lighting and the requirements of the 1968 NEC.

Key Considerations



1968 National Electrical Code (NEC)

This is your primary reference.


Grounding vs. Bonding

It's important to understand the distinction. Grounding connects to the earth. Bonding connects conductive parts together to create a low-impedance path for fault current. In the context of area lighting, we're often concerned with both, but especially bonding.

Equipment Grounding Conductor (EGC)

This is the conductor that provides a low-impedance path back to the source for fault current to facilitate the operation of the overcurrent device (circuit breaker or fuse) protecting the circuit.


PVC Conduit

PVC is non-conductive. Therefore, it cannot serve as the equipment grounding conductor.

Area Lighting

Outdoor installations introduce additional considerations related to moisture and potential for ground faults.

1968 NEC Provisions Relevant to Your Question

The 1968 NEC addressed grounding extensively. While I don't have the text in front of me to quote precisely, here are the key concepts:


General Requirement for Equipment Grounding

The NEC required grounding of electrical equipment. This was not a new concept in 1968.

Grounding Methods

The NEC specified acceptable methods for grounding. These included:


Metal Conduit (Rigid or EMT)

The metal conduit could serve as the equipment grounding conductor, provided the connections were properly made and maintained.

A Separate Equipment Grounding Conductor (EGC)

This was
required when using non-metallic conduit like PVC.

Specific Requirements for Non-Metallic Conduit (PVC)



An Equipment Grounding Conductor
WAS Required

The 1968 NEC
required that an equipment grounding conductor (EGC) be installed within the PVC conduit to ground the metal parts of the lighting fixture(s). PVC, being non-conductive, cannot provide a grounding path.

Size of the EGC

The size of the EGC was specified based on the overcurrent protection (breaker or fuse) protecting the circuit. The NEC had tables specifying the minimum size of the EGC.

Area Lighting and Outdoor Locations



Moisture

Outdoor locations were recognized as being damp or wet, increasing the risk of ground faults. This made proper grounding even more critical.

Exposed Metal Parts

Any exposed metal parts of the lighting fixture(s) that could become energized were required to be grounded.

Therefore, in 1968-1970, an equipment grounding conductor (EGC)
WAS required to be installed within PVC conduit feeding area lights that have metal parts.
The purpose was to provide a low-impedance path for fault current to return to the source and trip the overcurrent protective device.

Why is this important?
Safety

Without a properly installed EGC, a fault could energize the metal parts of the lighting fixture, creating a shock hazard.

Code Compliance

The installation would be in violation of the NEC in force at the time.

Research Tips


Examine the 1968 NEC

Specifically, look for articles on:
Grounding (Article 250 or similar – check the table of contents). Wiring Methods (PVC Conduit, etc.). Equipment Grounding Conductors.* Wiring in Damp and Wet Locations.

Disclaimer:
I am an AI Chatbot. This information is for guidance only. Consult with a qualified electrical inspector or engineer to verify specific requirements for your project and to ensure compliance with all applicable codes and regulations. Flag for review

Previous Question Next Question