Asked on: Friday, November 15, 2024 at 2:19 pm EST
Answered on: Thursday, March 6, 2025 at 5:17 am EST
Question: Hello. Have new construction building with new underground incoming as shown below to a 1200A switchboard.Need to setup a temp service(about 400A) but not sure exactly how it would more than likey be done in field.The one set #500 for 1200A is obviously wrong.1. Would they more than likely install the permanent before hand and only use some of the sets?2. Would temp conductors be run from the utility manhole or property line box?Thanks.
Okay, let's break down the common ways to establish a temporary service for your 1200A service, considering it's a new underground feed. The one set #500 for 1200A is a big red flag; you're right, that's incorrect.
Understanding the Problem and Common Solutions
The key here is minimizing disruption, cost, and safety risks while adhering to electrical codes (NEC). Here's the usual logic flow and common approaches: Utility's Role
The local utility company's policies and procedures are paramount. They dictate how they allow taps and connections to their infrastructure. You must involve them in the planning process early.
Safety First
This is high amperage. All work must be done by qualified electricians adhering to strict safety protocols (lockout/tagout, PPE, etc.).
Minimizing Disruption
The goal is to avoid repeatedly cutting and splicing the permanent service conductors.
Scenario 1: Installing Permanent Service Conductors First (Likely the preferred method if it works) What it involves
This is often the preferred method, particularly if the utility allows it and scheduling aligns.
Permanent Installation
Install the complete permanent underground service conductors from the utility's connection point (manhole or property line box) to the 1200A switchboard, as per your design specifications (including the proper number and size of conductors).
Tap Before Switchboard
Before connecting the permanent service conductors to the 1200A switchboard, install a properly sized tap to a temporary 400A disconnect switch. This requires careful planning and approved tapping methods.
Temporary Disconnect
This temporary disconnect switch will then feed your temporary 400A panel.
Permanent Connection Later
Once the permanent service is needed, the 400A tap is disconnected (with the utility's blessing!), and the permanent conductors are connected to the 1200A switchboard.
Advantages
Less disruption to the permanent service later. Safer - reduces the number of times high-current conductors are cut and spliced. Often more cost-effective in the long run.
Disadvantages
Requires upfront investment in the full permanent service conductors. May need temporary protection of the permanent conductors during construction if exposed.
Important Considerations for this Approach
Tapping Method
You MUST use approved tapping methods for the size of the conductors involved. Common options include:
Insulated Tap Connectors (e.g., Polaris connectors)
These are fully insulated and often preferred for safety.
Split Bolt Connectors (taped)
Acceptable but require careful taping and insulation.
Mechanical Lugs
Properly sized and torqued lugs.
Tap Conductor Sizing
Size the tap conductors appropriately for the 400A temporary service.
Overcurrent Protection
The 400A temporary disconnect MUST have overcurrent protection (fuses or a circuit breaker) sized appropriately for the 400A service.
Working Space
Ensure adequate working space around the tapping point and the temporary disconnect switch.
Scenario 2: Temporary Conductors from Utility (Less Common, but Possible) What it involves
The utility may (less likely) allow you to run a temporary set of conductors directly from their manhole or property line box to a temporary 400A disconnect and panel.
Advantages
Avoids any work on the permanent service conductors initially.
Disadvantages
Requires the utility's explicit permission and likely their involvement in the connection. May be more expensive due to utility fees and labor. Often more complex logistically.
Why it's less common
Utilities generally prefer to only have to connect one service. A separate temporary connection adds complexity and potential for issues.
Scenario 3: Temporary Generator Connection (If applicable to your site) If the temporary power needs are light, a generator connection point may be installed near the switchboard. This point should be connected by a manual transfer switch.
Key Steps and Considerations1. Contact the Utility Immediately
This is the first and most important step. Get their requirements, policies, and fees for temporary services. They will likely have specific connection methods they approve.2.
Consult with a Qualified Electrical Engineer/Designer
You need a professional to: Calculate the correct conductor sizes for the permanent 1200A service (based on the calculated load). Design the tapping method for the 400A temporary service (if using Scenario 1). Ensure all work complies with the NEC and local codes.3.
Hire a Licensed Electrical Contractor
The actual installation must be done by a licensed and experienced electrical contractor familiar with high-amperage services.4.
Permitting and Inspections
Obtain all necessary permits and schedule inspections by the local electrical inspector.5.
Safety Plan
Develop a comprehensive safety plan for the temporary service installation, including lockout/tagout procedures.6.
Documentation
Keep detailed records of all work performed, including conductor sizes, connection methods, and inspection reports.
The #500 kcmil Conductor Issue For a 1200A service, you'll need multiple conductors in parallel per phase. The number and size of the conductors will depend on the conductor material (copper or aluminum), the insulation type, and the allowable ampacity per conductor (based on NEC Table 310.16). Your engineer will determine the exact configuration. #500 kcmil conductors are almost certainly insufficient for a 1200A service.
Example (Illustrative, Not a Design)
Let's say you're using copper conductors with 75°C insulation (a common scenario). From NEC Table 310.16, a #500 kcmil copper conductor has an ampacity of 380 amps. To reach 1200A, you'd need at least four #500 kcmil conductors per phase (1200A / 380A/conductor = 3.16 conductors, round up to 4). This doesn't account for derating factors, which could increase the number of conductors needed. This also doesn't factor neutral requirements.
In summary
Talk to the utility first.2. Engage a qualified engineer.3. Get a licensed contractor.4. Prioritize safety.
Good luck with your project! Flag for review