User: solarken, Location: Hudson, OH, USA
Asked on: Friday, November 15, 2024 at 9:08 pm EST
Answered on: Thursday, March 6, 2025 at 5:18 am EST
Question: I am adding SolarEdge batteries and Backup Interface (BUI, a Microgrid Interconnection Device (MID)) to an existing SolarEdge PV System and would like help clarifying a few things. The existing system has a 200A meter-main on the outside of an outbuilding, and the meter-main has a 100A breaker in it that feeds a subpanel inside the outbuilding, and the feed-thru lugs in the meter main feed an underground feeder to the main home about 100ft away, via 4/0 XHHW for L1 and L2 and I believe 2/0 Neutral. There is no EGC with the feeder to the house. There is a 200A loadcenter in the home. The breaker in the meter-main was downsized to 150A and a 60A backfed PV breaker was added in the initial PV installation. The inverter is inside the outbuilding.I am planning on installing the SolarEdge batteries and the BUI inside the outbuilding, removing the house feeder connection from the feed thru lugs, and feeding the main breaker of the BUI from the feed-thru lugs of the meter main. I will run 4/0 AL XHHW from the lugs to the BUI, with a 2/0 AL Neutral and #4 copper EGC. I plan on removing the PV breaker from the meter main and relocating the connection to the PV breaker in the BUI. I plan on pulling the disconnected house feeder into a junction box inside the outbuilding, and extending the conductors to the load terminals on the BUI.My first question concerns the 4/0 aluminum conductors, and whether there is any violation concerning ampacity, and if 310.12 permitting 83% covers the above approach and allows 4/0 AL for the 200A. I would think this is ok, especially since the main braker in the meter main was downsized to 150A.One issue I have with the above is that the outbuilding that will house the batteries would not have power in an outage, since the 100A subpanel is fed upstream from the meter-main, before the BUI. In Ohio, our winters can get cold, so I am thinking it might be better to replace the 100A subpanel in the outbuilding with a 200A subpanel, and feed it from the BUI load terminals, and feed the house from feed-thru terminals in this new subpanel, so everything is backed up. This would permit a small heater to be powered in the battery room during a grid outage if needed.Is there any issue if this 200A subpanel were added, again in regards to ampacity and 310.12? And since the downsizing of the meter-main breaker from 200A to 150A was done to accommodate the PV breaker and that is no longer needed, any issue with putting back in the original 200A main breaker?I am also going to try (finally) to use a generator connected to the generator input on the BUI. Hopefully it will work.Your feedback and suggestions are appreciated.
Okay, let's break down your SolarEdge battery and BUI installation plan, addressing your questions and concerns. This is a complex setup, so accuracy and code compliance are critical. I am an AI and cannot provide official electrical code interpretations; consult with a licensed electrician for code compliance verification.
Understanding the Setup Existing
200A meter-main (outside outbuilding). 100A breaker in meter-main feeds a subpanel inside outbuilding. Feed-thru lugs in meter-main feed a 100ft underground run to a 200A main panel in the house (4/0 Al XHHW L1, L2, 2/0 Al Neutral, no EGC). Previously, the meter-main breaker was downsized to 150A and a 60A PV breaker was added. SolarEdge inverter inside outbuilding.
Proposed
SolarEdge batteries and BUI inside outbuilding. Feed BUI main breaker from meter-main feed-thru lugs (4/0 Al XHHW, 2/0 Al Neutral, #4 Cu EGC). Move PV breaker from meter-main to BUI. Connect house feeder to BUI load terminals.
Question 1: 4/0 Aluminum Conductors for 200A NEC 310.12 (Formerly 310.15(B)(7))
This section (or the equivalent in your local code) allows for reduced ampacity in certain dwelling unit feeder and service calculations. However, it's crucial to understand the specific requirements and limitations.
Ampacity of 4/0 Al XHHW
Typically, 4/0 Al XHHW has an ampacity of around 180A (check your specific wire insulation and temperature rating).
150A Meter-Main Breaker
If your meter-main breaker is 150A, the 4/0 Al conductors are sufficient assuming no other loads contribute to the calculated service demand load.
Applying 310.12
To use 310.12 (83% rule), you must correctly calculate the service or feeder load per NEC Article 220 (or equivalent). You can apply the 83% reduction only to the calculated load. If the calculated load is 200A, you can use 4/0 conductors.
Crucial Considerations
Load Calculation
Accurately calculate the total load on the service, including the house, outbuilding, existing PV system, future loads, and potential battery charging/discharging.
Continuous Loads
Be aware of continuous loads (loads that operate for 3 hours or more). These are factored differently in load calculations.
Voltage Drop
Don't forget to calculate voltage drop, especially with the 100ft run to the house. 4/0 AL may be inadequate for voltage drop if the house load is close to 200 amps.
Recommendation
The 4/0 AL is likely sufficient given the 150A breaker, but absolutely verify this with a full load calculation by a qualified electrician. Voltage drop is likely going to be a big issue. If it is found that it might not be sufficient for voltage drop, and the main meter-main breaker is upped back to 200A, then consider using a larger gauge wire such as 250kcmil or 300kcmil.
Question 2: Adding a 200A Subpanel in the Outbuilding Backup for the Outbuilding
This is a good idea to ensure the outbuilding has power during an outage, especially for heating.
Ampacity and 310.12 (if it can be applied)
The same ampacity and 310.12 considerations apply as above. You need to ensure the conductors feeding the 200A subpanel (from the BUI) and the conductors feeding the house (from the subpanel) are sized appropriately based on the calculated loads.
Upping the Meter-Main Breaker Back to 200A
Feeder Size
First determine if the existing feeder to the house can handle a 200A load. Voltage drop calculations are even more critical here.
Main Panel in the House
The 200A main panel in the house must be able to handle the load.
Service Load Calculation
With the PV system, batteries, and potentially higher loads, a proper service load calculation is essential to confirm if the existing service is adequate.
NEC 690.64(B)
This section of the NEC deals with PV system output circuit calculations. Your electrician needs to verify compliance to prevent over-sizing breakers. The 120% rule is especially important.
Considerations with the 200A Subpanel Addition Series Ratings
Ensure that the series rating of your BUI, subpanel, and downstream equipment are sufficient to handle any potential fault currents.
Overcurrent Protection
Each circuit must have proper overcurrent protection (breakers or fuses) sized correctly for the conductor ampacity and connected load.
Neutral and Grounding
Ensure that the neutral and grounding connections are properly made and comply with NEC Article 250. Especially ensure proper grounding of the new subpanel and BUI.
Generator Connection BUI Compatibility
Verify that the generator you intend to use is fully compatible with the SolarEdge BUI. Check the BUI documentation for approved generators and connection requirements.
Generator Sizing
Size the generator appropriately for your backup load requirements.
Transfer Switching
The BUI provides the automatic transfer switching function. Ensure it operates correctly and that the transfer occurs seamlessly.
Bonding and Grounding
Ensure proper bonding and grounding of the generator as per NEC requirements.
Key Takeaways and Recommendations1. Engage a Qualified Electrician
This is a complex project that requires a licensed and experienced electrician familiar with SolarEdge systems, battery storage, and NEC requirements. They can perform the necessary load calculations, conductor sizing, and ensure code compliance.2.
Detailed Load Calculations
Get a comprehensive* load calculation done that considers all existing and future loads, including the house, outbuilding, PV system, batteries (charging and discharging), and the generator.3.
Conductor Sizing
Base conductor sizing on the load calculations, voltage drop requirements, and NEC ampacity tables. Don't solely rely on 310.12 without proper verification.
4.
Grounding
Ensure proper grounding and bonding throughout the system.5.
Permitting and Inspections
Obtain all necessary permits and schedule inspections to ensure the installation meets local code requirements.6.
Documentation
Keep detailed records of the installation, including load calculations, wiring diagrams, and equipment specifications.
In summary, while your plan seems reasonable on the surface, a thorough review and implementation by a qualified electrician are essential to ensure safety, performance, and code compliance. Don't cut corners on safety or proper design! Flag for review