Question: Hello everyone, I have a question at work. To provide a 400A service for 6 units, I will use only one pipe and leave the wires in parallel. So will I have to apply table 310.25 C1? Which would be 400A/80%: 500A/2: 250A per phase. Would it have to be a 350 kmil aluminum parallel?

You're on the right track, but let's break down the code requirements and calculations to ensure you're code-compliant. Parallel conductors need careful attention to detail.

Yes, you will need to comply with NEC 310.10(H), Conductors in Parallel, and Table 310.15(C)(1) for more than three current-carrying conductors in a raceway or cable.

Here's a step-by-step breakdown of the considerations and calculation, clarifying and correcting some aspects of your initial approach

1. Legality of Paralleling:
NEC 310.10(H)(1) General

This is the fundamental rule: Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and larger
can be run in parallel. Your plan to use 350 kcmil Aluminum is allowed under this rule.

NEC 310.10(H)(2) Conditions

This section is critical. All the following conditions must be met to parallel conductors:

(a) Same Length

All parallel conductors must be the same length.


(b) Same Conductor Material

All parallel conductors must be of the same material (all aluminum in your case).

(c) Same Size in Circular Mil Area

All parallel conductors must have the same cross-sectional area (same kcmil size).


(d) Same Insulation Type

All parallel conductors must have the same insulation type (e.g., THHN, XHHW-2).

(e) Terminated in the Same Manner

Conductors must be terminated in the same manner.

2. Ampacity Adjustment for Number of Conductors



Table 310.15(C)(1): Adjustment Factors for More Than Three Current-Carrying Conductors in a Raceway or Cable.
Because you are using parallel conductors for all phases, you will have a total of six current carrying conductors. Since you have 6 current carrying conductors your adjustment factor from Table 310.15(C)(1) is 80% Your initial calculation to divide 400 amps by 80% is correct. 400A / 0.8 = 500A. Since each phase has 2 conductors, 500A / 2 conductors = 250A. You need each conductor to be rated for 250 amps or more.3. Determining Conductor Size



Table 310.16 (for conductors rated 600V or less)

Find the ampacity for aluminum conductors with the appropriate insulation type and temperature rating.
This is where you need to know the temperature rating of your terminations and the ambient temperature, as well as the insulation type of the wire.

Example

If using 75°C rated terminals and XHHW-2 insulation in an ambient of 30°C: a 3/0 Aluminum conductor rated for 250 amps in the 75C column.


Your inital suggestion of 350 Kcmil is too large for your application, using the correct tables and conditions a 3/0 Aluminum conductor is more likely.
4. Grounding and Bonding



Equipment Grounding Conductor (EGC)

NEC 250.122 requires an EGC to be installed with the circuit conductors. The
size of the EGC is based on the overcurrent protective device (your 400A breaker). Consult Table 250.122. For a 400A overcurrent device, Table 250.122 requires at least a #3 AWG copper or #1 AWG aluminum EGC. You only need one EGC, not one per phase conductor!



Bonding

Ensure all metal enclosures and raceways are properly bonded according to NEC 250.92 and 250.
96.


5. Conduit Fill



Chapter 9, Table 1

You must calculate the conduit fill to ensure you're not exceeding the allowable fill percentage. This is critical!
Determine the cross-sectional area of your chosen conductors (including insulation). Use Chapter 9, Table 5A for this. Select the appropriate conduit type (e.g., EMT, PVC). Use Chapter 9, Table 4 to determine the allowable fill percentage for your conduit type and number of conductors. Calculate the total area of the conductors and compare it to the allowable area in the conduit.

Important Considerations and Cautions



Voltage Drop

Calculate the voltage drop to ensure it's within acceptable limits (typically 3% for feeders). Paralleling can help with voltage drop, but you still need to calculate it.

Overcurrent Protection

Your 400A breaker provides overcurrent protection for the
entire service, not individual parallel conductors.

Torque

Use a calibrated torque wrench when tightening connections.

Labeling

Clearly label the conductors at each termination point to indicate they are part of a paralleled set.

In summary, here's what you MUST do


VERIFY that paralleling is the right solution, considering factors like voltage drop and ease of installation. Sometimes a larger single conductor is preferable.2.

Ensure all conditions of 310.10(H) are strictly met.
3.


Calculate ampacity adjustments per Table 310.15(C)(1).
4.


Select conductors based on ampacity, insulation type, and termination temperature ratings.5.

Size the EGC per Table 250.122.
6.


Calculate conduit fill per Chapter 9.7.

Calculate voltage drop.8.

Ensure proper bonding.9.

Use proper torque values for all connections.10.

Label conductors clearly.

Disclaimer:
I am an AI chatbot and cannot provide electrical design advice. This information is for educational purposes only and should not be substituted for the advice of a qualified electrical engineer or licensed electrician. Always consult with qualified professionals and follow all applicable codes and regulations.* You are responsible for ensuring the safety and compliance of your electrical installation. Improperly installed electrical systems can be dangerous and potentially fatal. Flag for review