Question: Hi Folks,I'm about 6 months in with my utility company doing an underground service upgrade. The service has to be moved away from the gas meters and I'm trying to do this changeover as efficiently as possible. FYI I'm a forum verified general contractor and going to hire an electrician, but I like to have a clear plan in place with subs.The current setup is a 200A two meter service with two 100A tenant disconnects that go to two 100A exterior panels.The new service will be 400A with two 200A tenant disconnects 25 ft away.I'm thinking the most efficient and least disruptive way to do this is to upgrade the existing panels to 200A panels prior to the new service trench work. They would remain on the 100A tenant disconnects until the new meters and disconnects are installed. We could run my new 200A feeds from the new panels to the new service and have them ready to go after the new mains are in. The runs would have to come off the bottom of the panels and run through the crawlspace. I guess we would need 3" LB's for those 200A AL SEU cables.-Does this seem like a solid plan? I believe the 200A panels will be allowed to temporarily be on the 100A tenant breaker since the tenant breaker is the current limiting device.-Also not sure if these panels need to be main breaker panels or if they all allowed to be main lug only?Thanks in advance for your expertise!Quincy
Okay, Quincy, let's break down your plan for the underground service upgrade and see if we can refine it for maximum efficiency and compliance.
Assessment of Your Plan
Your approach is definitely well-considered and aims to minimize tenant disruption, which is a huge plus. Pre-installing the 200A panels is a smart move. However, there are some key points to consider and potentially refine: Overall Soundness
The core idea of pre-installing the 200A panels to the existing 100A service, then switching over to the new 400A service is solid, but it will require proper coordination and may involve a temporary power outage while switching over from the existing 100A disconnects to the new 200A disconnects after the utility installs the new meter.
Temporary Over-Paneling (100A Disconnect Feeding 200A Panel)
This is generally acceptable, BUT it's crucial to ensure the existing 100A disconnects are in good condition and properly rated. The 100A breaker will indeed act as the current-limiting device. You're right, the new 200A panels can temporarily operate at a 100A capacity. This avoids service downtime which makes it a very appealing plan.
Panel Selection (Main Breaker vs. Main Lug Only)
This is where the details matter and local utility requirements play a significant role.
Detailed Breakdown and Recommendations
Let's go point by point, expanding on the above and adding more detail:1. Communication with Utility Company (Crucial)
Before you do ANYTHING, have a detailed conversation with your utility company. They are the ultimate authority.
Ask specifically
If they have any specific requirements for service upgrades, particularly with multi-meter installations. If they require specific types of disconnects or panel configurations (main breaker vs. main lug only). What their procedures are for connecting the new service and disconnecting the old service. (Some utilities require YOU to pull the meter on the old service AFTER they disconnect the street side to ensure no one gets electrocuted). Inspect your current meter. Some older meters have special release instructions when pulling the meter. Do they require a full inspection BEFORE they connect the new service?
Get written confirmation of their requirements. This is your protection in case of miscommunication.2. Panel Selection (Main Breaker vs. Main Lug Only)
Utility Rules Override
As mentioned above, the utility company may dictate whether you can use main lug only or main breaker panels. They often have specific rules about service disconnects.
NEC Requirements
The National Electrical Code (NEC) has rules about service disconnects. Generally, you need a service disconnect at each meter location that is readily accessible.
Code References
Look at NEC Article 230, especially sections related to service equipment and disconnects.
Here's a breakdown of the pros and cons of each panel choice
Main Breaker Panels
Pros
Integrated Disconnect:
The main breaker acts as the service disconnect. (Assuming it's located right by the meter.) Simplified Installation
Often easier to install and wire.
Cons
Cost:
Typically more expensive than main lug only panels. Redundancy
The existing 100A breaker in the tenant disconnect becomes redundant because the new service panel will have a breaker.
Main Lug Only Panels
Pros
Cost:
Less expensive. Cons
Separate Disconnect Required:
You must install a separate service disconnect (typically a fused disconnect or a non-fused disconnect switch) adjacent to the meter. This adds cost and complexity. More Wiring
Requires more connections and potentially more conduit.
My Recommendation
Unless the utility specifically mandates main lug only, I would lean towards main breaker panels. It simplifies the installation and provides a clear disconnect means at the meter. However, be sure to research if having two breakers in series is allowed by the code, i.e. the new 200A service breaker in the panel and the tenant breaker outside.3.
Wiring and Conduit
Conduit Sizing
3" conduit for 200A service entrance cable (SEU) is likely correct, but confirm this with your electrician and based on the specific cable you are using. Different manufacturers have slightly different dimensions, and fill percentages in conduit matter.
Aluminum vs. Copper
Aluminum SEU is a common and acceptable choice for service entrance, especially for larger amperages. Copper is more expensive. Be sure to use anti-oxidant paste on all aluminum terminations.
LB Fittings
Using LB fittings to make the bend from the bottom of the panel into the crawlspace is a standard and acceptable practice. Ensure they are appropriately sized for the conduit.
Grounding
Pay close attention to grounding requirements. You'll need a grounding electrode conductor (GEC) to a grounding electrode (ground rod, water pipe, etc.). Size the GEC appropriately based on the service size. The new panels will need to be properly grounded, as will the meter enclosure.4.
Coordination and Staging
Phase 1: Panel Upgrade
Install the new 200A panels and run the new 200A SEU cable through the crawlspace, terminating them temporarily in a junction box near the new meter location. DO NOT CONNECT THEM YET!
Connect the existing 100A feeds to the new 200A panels.
Phase 2: Service Trench and Meter Installation
Excavate the trench. The utility company installs the new meters and disconnects.
Phase 3: Final Connection
Power Shutdown:
Coordinate a brief power shutdown with the tenants. Final Connection
Disconnect the existing 100A feed to the new panels. Connect the new 200A SEU cable to the new 200A disconnects.5.
Inspections
Schedule all necessary inspections with your local electrical inspector. They may want to inspect the panel installation before you energize it, and they will likely want to inspect the completed service upgrade.
Code Considerations
NEC Article 230 (Services)
This is the primary article governing service installations.
NEC Article 250 (Grounding and Bonding)
Critical for safety.
NEC Article 310 (Conductors for General Wiring)
For conductor sizing and ampacity.
Local Amendments
Be aware of any local amendments to the NEC that your jurisdiction has adopted.
Important Cautions
Electricity is Dangerous
This is not a DIY project. Hire a qualified, licensed electrician.
Permits are Required
Obtain all necessary permits before starting any work.
Safety First
Always de-energize circuits before working on them. Use appropriate PPE (personal protective equipment).
In Summary*Your plan is sound, but it requires careful planning, coordination, and adherence to code and utility requirements. By following these guidelines and working closely with your electrician and the utility company, you can ensure a safe and efficient service upgrade.Remember to prioritize communication and documentation throughout the process. Good luck, Quincy! Flag for review