Topic: Help Ground/ Bond Service and 2 X Pump Controller, 1 X Pivot Disconnect

User: Apprenti, Location: Idaho

Asked on: Sunday, November 17, 2024 at 1:49 pm EST
Answered on: Thursday, March 6, 2025 at 5:20 am EST

Question: I'm trying to keep this post as simple as possible and feel I am failing.At this time, I'm not concerned about sizing bonding jumpers or GEC, or conductors or breakers. I'm only concerned about GEC, Neutral, EGC, where they should land, and methods, execution in a service/ multi pump/ pivot situation. How do I clean this up?Agriculture pump service out in the sticks, trying to make it code compliant to re-energize after several years of being off.Overhead service to a single phase meter base to an (auxiliary???) gutter, then two pump controllers and a pivot disconnect below the gutter. Phase converter, pumps and pivot are hiding behind the equipment in photos. Am hoping everyone can trace neutrals and grounds by pictures alone.My biggest concern is that the service neutral goes from meter base to first pump controller on the left, to a chair lug bolted to the enclosure, then equipment grounds all over the place. Each disconnect does not have its own neutral and GEC.GEC goes from two rods to pump controller on left, chair lug bolted to enclosure. Thats where everything oroginates. GEC doesn't go to each controller/ disconnect individually.I believe some of the issues are:NEC 230.7: service conductors from meter base pass through gutter with conductors other than service conductors, but should be okay because it could be considered an Auxillary Gutter and not a Wireway? But they pass through the same conduit into the left most disconnect, and that's a wireway?NEC 250.92: the meter base and gutter tied to the meter base need a bonding jumper, like a CT can, tied to the neutral somehow. Meter base has a bond jumper tied to the neutral, but the bond jumper for gutter comes from chair lug in left most disconnect on left side of enclosure to a ground bar in gutter.NEC 250.64(D)(2): Each disconnect needs its own tie-in to the grounding electrode system. Currently, only the left most controller has a GEC connection, and it's off a lug bolted to the side of the enclosure. Grounds go from that lug to the other controller/ disconnects.NEC 250.64(E)(1): Bonding bushings with supply side bonding jumpers used throughout. It all comes off the left most controller lug bolted to the enclosure then goes all over the place.Thank you for your time!

Okay, let's break down the issues you're seeing and how to address them in a more streamlined way. You're on the right track with your analysis.

Core Problem

The grounding and bonding are daisy-chained and improperly executed. This means that not only does the grounding of the equipment rely on the integrity of connections that could corrode or loosen, but it can also lead to circulating currents and voltage drops.

Here's a simplified breakdown, focused on fixing the root issues


Grounding Electrode System (GEC)



The Problem

A single GEC connection is inadequate. Each service disconnect
must have its own connection to the GEC. Your current setup uses the disconnect enclosure as part of the GEC, which is not compliant.

Solution



Run a separate GEC (sized appropriately) to each of the three disconnects (two pump controllers and the pivot disconnect).
You can run them individually or you can splice a continuous GEC using irreversible compression connectors to feed all the disconnects. Terminate the GEC inside each disconnect enclosure on a listed grounding bar. Don't rely on bolting to the enclosure.2. Service Neutral and Grounding



The Problem

The neutral is being used as the primary grounding path for equipment. The grounding lug should be bolted to the enclosure, and is not sufficient for any fault current.

Solution



The neutral lands in the first disconnect (left most pump controller). Install appropriate sized Supply Side Bonding Jumper (SSBJ) from neutral terminal bar to an installed grounding terminal bar.
A separate EGC (Equipment Grounding Conductor) must be run with the circuit conductors to every piece of equipment (pumps, pivot motor, phase converter). These EGCs must be connected to the grounding bar in each respective disconnect. Consider using 4-wire circuits (L1, L2, N, EGC) to each piece of equipment. Bond all metallic parts of the auxiliary gutter to the grounding terminal bar in the left most pump controller with a bonding jumper that meets table 250.102(C)(1)3. Auxiliary Gutter Considerations



The Problem

Using the auxiliary gutter as a junction point is fine as long as you follow the rules. Passing service conductors and non-service conductors through the same conduit could be a problem, especially if you have more than six disconnects.

Solution



Verify the gutter fill complies with NEC.
Make sure all connections within the gutter are properly rated and listed. Document that this is an auxiliary gutter for inspection purposes. If possible, try to separate the service and non-service conductors into separate conduits.4. Bonding Bushings



The Problem

You are relying on bonding bushings and jumpers for the entire grounding path.

Solution



Bonding bushings are only supplemental and not a replacement for an EGC. Get rid of them once the EGC is ran from source to load.
Ensure all metal raceways entering and leaving the auxiliary gutter are bonded. Ensure all metal raceways entering and leaving the disconnect enclosures are bonded.5. Overall Execution



The Problem

The current system relies on enclosure bonding, which is prone to failure. There is no isolated neutral, which can allow fault current to travel on the neutral.


Solution



Install Grounding Terminal Bar in all metal enclosures and auxiliary gutter. Use Listed compression or mechanical lugs.
Remove the Lug that is bolted to the side of the left most disconnect. Run properly sized EGC's from all terminal equipment and equipment in between, back to the supply, and to the grounding bar. Utilize a 4-Wire system (L1, L2, N, EGC) from supply disconnects to load equipment.Simplified Steps to Correct the System


Establish a dedicated grounding bar in each disconnect enclosure and left most controller/ auxiliary gutter
2. Run a GEC to each disconnect enclosure and terminate on the dedicated grounding bar. The neutral lands in the first disconnect, then a (SSBJ) to the grounding terminal bar.3. Run EGCs with all circuit conductors to all equipment and connect to the grounding bar in the respective disconnect or auxiliary gutter.4. Bond the metallic parts of the auxiliary gutter and all raceways to the grounding bar in the left most pump controller/ auxilliary gutter5. Remove the Lug bolted to the side of the enclosureImportant Considerations



Code Expertise

You are making great effort, but it's hard to overstate the value of a licensed electrician familiar with agricultural electrical systems.


Inspection:
Engage your local electrical inspector early in the process. This ensures your plan will meet their requirements and avoid rework.This is a simplified approach. You'll need to consult the NEC for specific conductor sizing, bonding jumper sizing, and other details. However, focusing on these core principles will get you on the right track. Flag for review