Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Grounding Myers Hub in Service Enclosure

User: lkdiaZ, Location: Virgin Islands

Asked on: Sunday, November 17, 2024 at 2:53 pm EST
Answered on: Thursday, March 6, 2025 at 5:20 am EST

Question: 1000A service has RMC conduits going to a metal pull box before arriving at Main Service Disconnect. RMC conduits are to be terminated at pull box using grounding myers hub similar to STG-10. The conduits contain 500KCM. The bonding jumper for this would have to be 1/0 AWG if I'm not mistaken. Cut sheet for this hub lists a max 4AWG cable. How do I bond the grounding hub with a 1/0AWG cable? I need Nema 3R connection.

You've hit a classic Code quandary! You're right about a few things: 1000A Service = 1/0 AWG Bonding Jumper

Based on Table 250.102(C)(1) in the NEC, for a 1000A service, the minimum size of the equipment bonding jumper
to a service enclosure or to a service raceway is indeed 1/0 AWG copper.

Myers Hub Limitation

You're seeing the common problem of a manufacturer's termination point not being rated for the Code-required conductor size.Here's how to approach this, combining Code compliance with practical solutions:

Understanding the Problem

The purpose of bonding the metallic raceways (RMC) is to ensure a low-impedance fault current path back to the service, facilitating the operation of overcurrent protective devices (breakers or fuses) in the event of a ground fault. You need to make sure the pull box meets the requirements outlined in 250.92.

Solutions


Bushing with Lay-in Lug

This is often the

most practical and Code-compliant solution
. Replace the standard insulating bushing on the end of the conduit inside the pull box with a grounding bushing that has a lay-in lug specifically designed for bonding. These bushings are available with lugs that can accept 1/0 AWG conductors and are specifically listed for grounding purposes. Key

Make sure the lay-in lug is UL listed for the wire size you intend to use.
Connect your 1/0 AWG bonding jumper from the lay-in lug to the grounded metal pull box.2.

Split Bolt Connector

You could theoretically use a split bolt connector (also known as a "bug") outside the Myers hub, attaching the 1/0 AWG to a smaller conductor (e.g., a short piece of #4 AWG) that does fit into the Myers hub's lug.

Important Considerations

The split bolt must be properly insulated and weatherproofed (NEMA 3R-rated if exposed to the elements). The entire connection must be mechanically secure and protected from physical damage. This method requires meticulous installation. A better solution would be using a polaris tap.3.

Larger Hub with Larger Grounding Provision

Explore if there are larger Myers hubs (or hubs from other manufacturers) available that do have grounding provisions listed for 1/0 AWG. This might require a different hub size or style than what you initially planned.4.

Grounding Locknut with External Lug

Some grounding locknuts have an external lug that can accept larger conductors. However, these may not be suitable for use with a Myers hub, as they typically replace the standard locknut on the inside of the enclosure.5.

Exception and AHJ Approval (Proceed with Caution)

In very specific circumstances, you might be able to argue an exception to the AHJ (Authority Having Jurisdiction – the electrical inspector). This is

highly unlikely to be successful
unless you can definitively prove that the smaller conductor (e.g., the #4 AWG allowed by the hub) provides an equivalent or superior fault current path. This would require detailed engineering calculations and justification, and the AHJ is ultimately the final authority. Do not rely on this unless you have pre-approval.Code References



NEC 250.92

Bonding of metallic raceways and enclosures at the service.

NEC 250.102(C)(1)

Sizing of the equipment bonding jumper on the supply side.


NEC 250.8

Methods of grounding and bonding.

NEC 314

Outlet, Device, Pull, and Junction Boxes; Conduit Bodies; Fittings; and Handhole Enclosures.

Important Considerations



UL Listing

Ensure that all components you use (hubs, bushings, lugs, connectors) are UL listed for their intended purpose.

NEMA 3R Rating

If the pull box and raceway system are exposed to the elements, all components must be NEMA 3R rated for weather resistance.


Tightening Torque

Always follow the manufacturer's instructions for proper tightening torque on all connections.*

AHJ Approval

As with any electrical installation, it's best practice to consult with your local electrical inspector (AHJ) to ensure that your proposed method meets their requirements.

In Summary

The

lay-in lug grounding bushing
is typically the cleanest and most Code-compliant solution. It allows you to properly terminate the required 1/0 AWG bonding jumper to the conduit within the pull box while meeting UL listing requirements. Always double-check with the AHJ to confirm their acceptance of your chosen method. Flag for review

Previous Question Next Question