User: Zee, Location: CA
Asked on: Sunday, November 17, 2024 at 6:39 pm EST
Answered on: Thursday, March 6, 2025 at 5:21 am EST
Question: Can I run the Enphase circuits for 2 ADU's in the same conduit?(Both PV arrays go on the roof of main house because it has the 4-meter bank for all 4 units. 2 detached ADUs are in the back. Each PV system goes to a separate Combiner Box and service.)
It's generally not recommended and often prohibited to run circuits from separate dwelling units (ADUs in your case) in the same conduit for solar PV systems. Here's a breakdown of the reasons why, and what you should consider
Reasons Why It's Problematic:
Code Compliance (NEC)
The National Electrical Code (NEC) specifically addresses this in several articles, focusing on safe and identifiable wiring practices. You will likely run into issues with:
Separation of Systems (NEC 690 and general wiring principles)
The NEC emphasizes separating wiring systems for different units to prevent confusion and ensure proper identification of circuits and overcurrent protection. Sharing a conduit blurs these lines.
Voltage Drop & Conductor Sizing
Calculating voltage drop and proper conductor sizing becomes far more complex and error-prone when circuits for different units are intertwined. You may have to dramatically upsize conductors, making conduit fill and bending difficult, and very expensive.
Fault Isolation
If a fault occurs in one ADU's PV system, it can be difficult to isolate the problem to that specific unit if the wiring is mixed with another. This increases troubleshooting time and potential safety hazards.
Safety
Arc Flash/Shock Hazard
If someone needs to work on one PV system, there's a risk of accidental contact with conductors from the other system within the same conduit, creating a shock or arc flash hazard.
Overheating
Having too many current-carrying conductors in a single conduit can lead to overheating, potentially damaging the insulation and creating a fire risk. This is further compounded when dealing with DC conductors as heat loss is more pronounced.
Inspection Issues
Electrical inspectors are very likely to reject this type of installation due to the potential code violations and safety concerns.
Future Modification/Troubleshooting
Down the line, if you need to modify or troubleshoot one of the PV systems, having the circuits mixed in the same conduit will make the process much more difficult and time-consuming.
Key Considerations and Alternatives
Separate Conduits
The
most reliable and code-compliant solution is to run separate conduits for each ADU's PV system from the combiner boxes to the main house.2. Multiconductor Cables (with limitations)
May Be Permissible, but Check with Local AHJ (Authority Having Jurisdiction): Some jurisdictions might allow the use of listed multiconductor cables rated for outdoor use and sunlight resistance, specifically designed for PV systems, to carry the conductors from both ADUs within the same jacket/cable. This is highly dependent on local codes and the inspector's interpretation. The AHJ would likely want to see each conductor be identifiable, such as being labelled every few feet. Very Limited Practicality: You'd need to ensure that the cable is rated for the combined current of both PV systems, plus any derating factors for conduit fill and ambient temperature. This will mean very large, heavy, and hard-to-manage cables. Not typical or recommended. It is more difficult to pull heavier multi-conductor cable and repair if needed.3.
Multiple Conduits in a Trench
If you are burying the conduits, you can trench them together, but each ADU system must be in its own, completely separate conduit.4.
AC Combiner in ADUs (Potentially)
If space allows and the economics make sense, consider placing the combiner boxes inside the ADUs themselves, then running AC conductors (after the inverters) from each ADU to the main house in separate conduits. AC is generally easier to handle in these situations than DC due to less extreme voltage drop. Again, separate conduits are crucial.
*Before proceeding, contact your local electrical inspector (AHJ) to discuss your proposed setup. They will have the final say on what is permitted in your area. This is the most important step. Give them a clear diagram of your proposed system, including conduit runs, wire sizes, and equipment specifications. Flag for review