Topic: weathertight bulkhead options with LFMC fitting on one side, EMT (or multi-conductor cable) on the other side?

User: emiller233, Location: pittsburgh, pa

Asked on: Monday, November 18, 2024 at 11:34 am EST
Answered on: Thursday, March 6, 2025 at 5:21 am EST

Question: what is the best way to pass through a metal wall of a sea freight shipping container (keeping it weathertight) and into a junction box with terminals.For the exterior side of the wall, it will be a LFMC 90-degree fitting or possibly a LB fitting.and either EMT with rain-tight fittings or multi-conductor cable with a cord grip on the interior side of the wall.Everything needs to pass an inspection in the US and possibly Canada.The customer wants us to drill holes through the wall and weld conduit couplings onto it as needed for each conduit. I'm guessing this would never fly.cable runs are 480vac 3-phase and 120/240VAC

You're right, welding couplings directly to the container wall is generally a bad idea for several reasons: Structural Integrity

Welding can weaken the container wall, especially around the heat-affected zone. This is a big problem for sea freight, where containers are stacked and subjected to tremendous stress.


Corrosion

Welding removes the original paint and protective coating, leading to rust and potentially compromising the container's weather tightness.

Warranty

Modifying the container by welding can void any warranties.


Inspection

Inspectors in the US and Canada are unlikely to approve this method due to the reasons listed above. It doesn't meet established electrical or structural codes.

The Best Practices Approach

Here's a more reliable, code-compliant, and weather-tight approach:1.

Proper Penetration Fittings (Most Important)



Use Watertight Conduit Hubs/Connectors

This is the key to maintaining weather tightness. These fittings are specifically designed to create a watertight seal when installed through a metal enclosure (like a shipping container). Look for

UL-listed
and CSA-approved hubs/connectors suitable for the conduit and cable you're using. Brands to consider

Crouse-Hinds, Appleton, Ocal, Thomas & Betts, and Hubbell.

Installation

Drill a hole of the correct diameter to fit the conduit hub/connector. Apply sealant (suitable for marine environments) around the hole before inserting the hub. Tighten the hub according to the manufacturer's instructions to compress the gasket and create a watertight seal.

Consider a Flange

For a more robust and professional installation, especially on a container that will see rough handling, consider using a flange. The flange gets bolted or riveted to the container wall, providing a larger, more stable surface for the conduit hub to mount to. Again, seal thoroughly.2.

Exterior (LFMC or LB Fitting)



LFMC (Liquidtight Flexible Metal Conduit)

Connect the LFMC to the conduit hub on the exterior of the container. Use appropriate liquidtight connectors on both ends of the LFMC. The LFMC provides flexibility to accommodate any container movement.

LB Fitting

An LB fitting can be used to transition from the conduit hub to rigid conduit (if desired). Ensure the LB fitting is weatherproof and properly sealed to the container wall using a conduit hub.3.

Interior (EMT or Multi-Conductor Cable)



EMT (Electrical Metallic Tubing)

If using EMT, run it from the interior of the container to the junction box. Use rain-tight EMT fittings (compression or set-screw type) to ensure a weather-tight connection. Although inside, condensation can occur. Secure the EMT to the container wall with appropriate supports (straps or clamps).

Multi-Conductor Cable

Use a suitable cable (e.g., SOOW, Tray Cable) rated for wet locations and the voltages involved (480VAC and 120/240VAC). Use a proper

cord grip
or cable gland where the cable enters the junction box. This provides strain relief and a watertight seal. Choose a cord grip specifically designed for the cable diameter you are using.4. Junction Box

Use a

NEMA 4X
(or higher) rated junction box. This ensures it's watertight and corrosion-resistant, necessary for marine environments. Ground the junction box properly to the container. Terminate the conductors on appropriately sized and rated terminals.5. Important Considerations



Grounding

Establish a good, reliable ground connection. The container itself should be properly grounded. Run a separate grounding conductor within your conduit/cable.

Sealant

Use a high-quality marine-grade sealant (e.g., Sikaflex 291) around all penetrations to ensure a watertight seal.


Drainage

Consider adding a small drain hole (with a screened vent) at the lowest point inside the junction box to allow any condensation to escape.

Materials

Use corrosion-resistant materials for all components (stainless steel, aluminum, or non-metallic).


Documentation

Keep detailed records of all materials used, installation methods, and any testing performed. This will be helpful for inspections.

Code Compliance

Consult the latest versions of the National Electrical Code (NEC) in the US and the Canadian Electrical Code (CEC) to ensure compliance. Specifically, pay attention to articles related to wet locations, grounding, and wiring methods.

Why This Works



Watertight Seals

The conduit hubs/connectors and cord grips are designed to create a reliable, watertight seal.

Mechanical Protection

Conduit protects the wiring from physical damage.


Code Compliance

This approach adheres to standard electrical codes and practices.*

Maintain Container Integrity

No welding or significant weakening of the container walls.

Customer Education

Explain to your customer the risks associated with welding and the benefits of using proper penetration fittings. Emphasize that this approach will result in a more reliable, safer, and code-compliant installation.

Important Note:
Always consult with a licensed electrical inspector or engineer to ensure compliance with local codes and regulations. They can provide specific guidance based on the details of your project and location. Flag for review