Topic: Generator box

User: hhsting, Location: Glen bunie, md, us

Asked on: Monday, November 18, 2024 at 11:46 am EST
Answered on: Thursday, March 6, 2025 at 5:21 am EST

Question: I have emergency branch which to comply with NEC 2017 Article 700.3(F) has MTS which then feeds portable generator. The portable generator is typically connected with inlet but in this case engineer provided fused disconnect.Where in NEC 2017 Article 700 it says portable generator connected to inlet?

You are right to question the assumption that a portable generator must be connected via an inlet when connected to an Emergency System.The NEC 2017 doesn't require the use of an inlet for connecting a portable generator to an emergency system covered under Article 700. It specifies performance requirements for emergency systems, but the method of connection is more about ensuring a reliable and safe power transfer.Here's a breakdown of why the fused disconnect might be acceptable (or not) and where to look in Article 700: NEC 700.3(F): Portable Generator(s). This section requires you to have one or more portable or temporary generator(s) that is/are available whenever the emergency system is or may be needed. Reliability and Transfer

The core concern for emergency systems is reliability. The connection method (inlet, disconnect, etc.) must facilitate a rapid and reliable transfer of power when the normal source fails. The key is that the system is designed and installed in a way that minimizes human error and ensures quick restoration of power.

Fused Disconnect Considerations

A fused disconnect can be acceptable
if it meets the following criteria related to reliability and safety:

Rapid Connection

The procedure for connecting the portable generator to the fused disconnect must be well-defined and easily executable by trained personnel. There should be clear labeling and instructions.

Proper Overcurrent Protection

The fuses in the disconnect
must be sized appropriately for both the portable generator's output and the emergency load being served. This is crucial for safety and preventing damage.

Lockout/Tagout

The disconnect should be able to be locked out during maintenance and testing to prevent accidental energization.

Listed and Labeled

The fused disconnect itself must be listed and labeled for its intended use.

Where to look in NEC 2017 Article 700



700.1 Scope

This defines what Article 700 covers: emergency systems intended to supply, distribute, and control electricity for illumination and/or power essential for safety to human life.

700.4 Tests and Maintenance

This section requires periodic testing of the emergency system, which includes the generator and transfer equipment. The connection method must allow for easy testing.


700.5 Capacity

The emergency power source must have adequate capacity to carry the intended loads. This is critical for proper sizing of the generator and the disconnect.

700.12 General Requirements

Emergency systems shall meet all requirements for design and installation contained herein.


700.12(B) Separate Equipment

Emergency equipment, including generator sets, shall be installed separate from all other equipment.

700.25 Overcurrent Protection

Where overcurrent protection is provided in accordance with 700.25(A) and 700.25(B), the selective coordination requirements of 700.27 shall apply.


700.27 Coordination

Emergency system(s) overcurrent devices shall be selectively coordinated with all supply-side overcurrent protective devices.

110.3 Examination, Identification, Installation, and Use of Equipment

This general requirement is very important. All equipment, including the fused disconnect, must be installed according to its listing and labeling, and per the manufacturer's instructions.

In summary

The NEC doesn't dictate
how you connect a portable generator to an emergency system, but it emphasizes reliability, speed, and safety. If the fused disconnect arrangement allows for a rapid, reliable, and safe power transfer, complies with all listing/labeling requirements, and meets all other applicable NEC requirements, then it can be an acceptable solution. If the engineer can demonstrate that the fused disconnect provides an equivalent or better level of reliability and safety compared to an inlet system, then it is acceptable. However, it will be up to the AHJ (Authority Having Jurisdiction) to make the final determination on whether the installation meets the intent of the code.

Important Considerations for the Fused Disconnect



Training

Properly train personnel on the correct and safe procedures for connecting the generator to the fused disconnect.

Documentation

Document the entire process, including the steps for connecting the generator, testing procedures, and maintenance schedules.


AHJ Approval

It's always a good idea to discuss the design with the local AHJ (Authority Having Jurisdiction) to ensure they are comfortable with the fused disconnect arrangement before installation.

Therefore, don't focus on finding a specific section that requires an inlet. Instead, focus on whether the chosen method (fused disconnect) meets the overall intent of Article 700: a reliable and safe emergency power system.
Flag for review